Discuss Voltage in shower waste! in the UK Electrical Forum area at ElectriciansForums.net

OK....was wondering if there might be any electric fence energisers in the vicinity??

My thinking is that you actually need quite a fair old voltage to push through that much pipe, and if it's all three stacks then it's clearly communal to something downstream of the join, hence way after the conventional 'bounds' of the place.

Or - what's the sewerage system? Is there a septic tank with a lift pump or a Klargester system or......

If it's a shared lateral sewer, might be worth seeing what's going on at the neighbours, too.
 
No volts at the drain outside I believe? Gotta be an IR fault in the house somewhere. Been happening for long or just started ?

That's just implausible if considering water/pipe as the conductor - it's all gotta go somewhere!
 
What voltage do you get from a live in the house to the flowing water?
Thinking a voltage coming in from a neibour's fault (different phase).
Therefor if you have 240v available do you get more than that testing to the water?

Boydy
 
What voltage do you get from a live in the house to the flowing water?
Thinking a voltage coming in from a neibour's fault (different phase).
Therefor if you have 240v available do you get more than that testing to the water?

Boydy

Definately have not tried this...voltage is only present within the house waste. Nothing present in drain outside where 3 stack pipes meet in pit.

Somewhere the water is carrying a voltage. How much voltage at origin is anyones guess as I could be reduced by the time I'm reading it. It seems more load/more voltage. In fact it was even more voltage every time I added the next room onto the circuit today. All I was doing in this little experiment was adding the feed back into the ceiling rose without switch wires etc. More resistance meant more voltage, about 3-4v each time I added a leg back on.

I cant see why im getting the voltage on all three wastes when it seems they are not connected until outside.....where there is no voltage.....
 
Have you had a chance to take readings, under the same conditions with water flowing, of the following set of three voltages:
a) External test spike to MET
b) External test spike to energised water stream
c) MET to energised water stream
If the conditions are identical and the spike outside the resistance area of the fault, then it should prove conclusively which point is being elevated above true earth.

The above checks have been carried out and as you say they are all the same.

I didn't mean to imply the voltages should be the same, only that the conditions should be the same for all three readings. For example, 2V spike-MET, 12V spike-water and 14V MET-water would suggest that the MET is where it should be and the water was 'live' which is what we believe is occurring but as yet have no proof. Whereas 13.5V spike-MET, 0.5V Spike-water and 14V MET-water would show that the fault is on the supply. I was just looking to see if that could definitely be ruled out once and for all.

Exhaustive IR tests would be my preferred next move but I figured you might already have noted those voltages in earlier tests.
 
What's puzzling me is even if there IS an IR fault internally, how is that interacting with a waste pipe and how is one part of the waste system not conducting through to another when it's the water inside it that has to be acting as the conductor as effectively flows everywhere.

Has anyone thought to remove the waste traps and see what measurement is the other side of the water trap? My guess is none.

There's something about this whole thing that doesn't quite ring true.
 

Reply to Voltage in shower waste! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
263
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
506
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
467

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock