Hi Guys

I wonder if someone with more experience of PV might be able to give me some advise.

Was called out today to a domestic building with a remote barn on which a 4kW PV array is sited. The Inverter is in the barn and a long (50m) 2.5mm twin and earth in pipe (historic) feed back to the house.

The problem I have is that there is a full short (L-E) on the cable between the house and the barn. So far no problem.

Just to prove the diagnosis I disconnected the earth at both ends of the cable between the house and the barn and re-energised the system

However I was then getting an Off Grid notification on the inverter and more worryingly 240V present when testing between N-E on from the PV inverter.

Is this energised CPC normal? And would the lack of an earth be picked up by the PV system and cause the OFF GRID notification.

The supply cable I can sort, just need to know if I need to call in a PV company to sort the PV Array out.

Thanks for any help
 
What kind of earthing set up do you have? Is there an earth rod at the barn?

Incidentally, if the cable to the barn needs replacing then it needs to be upgraded to a larger cable.
 
Do your calcs on the cable for sizing, as Solarcity said it needs upgrading.
You need to work on a 1% loss not the normal 3% or the inverter will go overvoltage.

Why not diconnect the cable altogether then do your tests, live to earth, neutral to earth etc on the cable.
I had a fault once on an outside light but only when it was wet, so one rainy day, coat on pinpointed the fault, vermin had chewed the wire...
 
that's not normal. I'd be wanting to rule out the potential for the earth being live through a fault elsewhere in the AC circuit before considering that it might be the inverter... though they do have capacitors etc inside them so it's possible these are discharging through the earth or something.

eta - ie is the pipe itself that the t&e is running through bonded at both ends, so the system is still actually connected to the MET through that?

eta 2 - hmm, actually in some countries I believe they sometimes bond the negative pole of the panels to the negative pole of the inverter for some reasons that I forget (we don't do it here), I wonder if the installers maybe done that here for some reason, as well as bonding the actual frame to an earth spike (as was the guidance for transformerless inverters), then if the pipe is bonded in any way it will also be in the ground, so forming a bit of a very low power DC circuit, which just happens to be at 240V. It'd be a bit unusual, but not impossible, as you can get a slight leakage current flowing through the frames... do you know what current is flowing?
 
Last edited:
Not my cable, first time I`ve set foot in the place. The supply cable looks like it was put in at least a decade ago by a DIYer as its standard 2.5mm T/E in an alcathene pipe.

I have isolated it completely as suggested above so there is no earth path at all. However there is a voltage running through the cpc from the inverter when it is powered up.
 
Do your calcs on the cable for sizing, as Solarcity said it needs upgrading.
You need to work on a 1% loss not the normal 3% or the inverter will go overvoltage.

Why not diconnect the cable altogether then do your tests, live to earth, neutral to earth etc on the cable.
I had a fault once on an outside light but only when it was wet, so one rainy day, coat on pinpointed the fault, vermin had chewed the wire...

Yeah did all that before I posted on here. I know the supply cable has a fault, that can be fixed, its this odd energised cpc and the question about OFF GRID above.
 
If there is a live to earth fault on the cable then by disconnecting the earth from both ends you are effectively making the earth cable live. This would explain the reading between neutral and (live) cpc.

Edit:

Actually, I may have misunderstood what you were saying. Are you testing neutral to earth AT the inverter? If so, is there any cable connected to the earth connection of the inverter?
 
Last edited by a moderator:
well, I'm confused, so I think I'll just have to wish you luck with this. Though I'd definitely double check for the negative DC > neutral bonding on the inverter as I have heard of installers getting confused by the bonding point on the inverter and asking if they're meant to bond to it (not many mind, but it's possible). If it's a TL inverter could be that there's a patch back through the inverter somehow.

Maybe try it with the DC isolator switched off as well, which will tell you if it's panel related or capacitor related.

erm right, I'm out, keep us posted though please, as it's always good to know how quirks like this occur for future reference.
 
With the cpc from the inverter disconnected from CU in the barn and the cpc on the supply cable disconnected and L+N connected there is no earth connection to the inverter at all. The disconnected cpc from the inverter shows 240V when tested between the cpc and Neutral. . Glad I avoided these things when so many others were getting involved.
 
PV fault.png.........the cpc is live
 

Reply to Voltage on CPC from PV Array. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
780
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
447
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
969
Hello All, Currently building an extension to my barn/workshop and before i pour the foundations i want to run some new cables from my ground...
Replies
3
Views
2K
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock