I have just completed an EICR.

All the earths have been chopped off in the ceiling roses and switches on the lighting circuit. There are no class 2 fittings.

Usually if there are no earths on the lights and no class 2 fittings then it will be a C3. However, the lighting circuit does have CPC's they have just not been connected anywhere. Would this be a C2 as Zs will be greater than the maximum? Also, how does this relate to RCD protection? There is RCD protection on everything but with the Zs on the lights being non existent the RCD will not trip with an earth fault (especially in relation to the bathroom).

Cheers guys.
 
Contra Spin, C2. RCD will operate, but not until someone or something with a path to earth touches the live metal part to create a circuit. Great that an RCD (theoretically) shuts off the circuit quick enough that the shock won't interrupt the fibrillations of your heart, better though when it shuts the circuit off without a human conductor.
 
Wait, so we can apply a code C3 for lighting circuits that have no CPC at all, but it’s C2 if the unused CPCs have been cut off, rather than terminated in a parking terminal?
Questions that should be asked:
It’s not dangerous, there’s no live parts that can be touched, and it’s not potentially dangerous because there are no exposed-conductive-parts that could become live under fault conditions.
Yes improvement is required in order to comply with BS7671 which requires a CPC, in case someone decides to install class 1 fittings or accessories.
 
I have seen brand spanking new builds where the sparks have simply bent back and cut the cpc extremely short where class II fittings are fitted , just taking the lives and N into the light

I tend to sleeve the cpc and coil it up like a snake leaving it long incase the home owner changes the light
 
Yes but in the original post if I understood correctly by cutting the earths they were then not taking an earth round the circuit to each point, compared to what you are saying where the earth is there but just not connected
 
OP have you checked to see if the cpc is connected at the fuse box ? Or has that been cut short as well ?
 

Reply to What code for all CPC's chopped off on lights? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
605
EICR picked up no continuity on cpc on 3 pendants fittings in a grd Floor Flat. Zs measured @ other pendants & complies. Different opinions on the...
Replies
8
Views
429
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
632
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock