Evening all, apologies if this is in the wrong forum or has been asked before.

I have ordered a new oven thinking I could just plug it in to 13amp socket same as my old one. However I checked today and the oven is 16amp and therefore should have its own dedicated circuit.
I checked the instructions for the old oven and turns out that is also 16amp, however it has been connected to 13amp socket.

I understand that using 3 core flex to connect the new oven to a 3 pin socket does not conform to regulations, and I do not intend on doing so.
But if the plug was fitted with 13amp fuse, would this not adequately protect the cable from over current? Assuming the oven was at full load and drawing 16amps, would the plug top fuse simply blow causing a minor annoyance at dinner parties?

I must stress again that I have no intention on doing it this way, I just have a keen interest in electrical theory and want to know for my own satisfaction

Thanks in advance
Beeg
 
it may well work just fine, 16A will be the current draw whilst every element is on at the same time. however I WOULD NOT RECCOMEND doing so.
note, the time the fuse will blow is in the middle of cooking x-mass dinner, when the fuse is warm from being under load for a long time and you turn everything up to finish it off.

sods law and physics working in harmony.

Dedicated circuit is the way forwards.
 
But are they implying that a 13A switched spur is ok

16A is the key,
standard 13A plug is a no
13A spur is a no
16A socket could be done
16A isolator is ok.
simple, supply has to be greater than manufacturer's instructions.
No If's, No buts. if you want it to comply and be safe, follow the manufacturers instructions.
 
Last edited:
Hi - as above, use manufacturer’s installation instructions as your guide. No plug and socket for a 16A oven please. By the by, a 13A fuse won’t melt at 13A as that’s it’s rated working current. What we perhaps can’t be sure of is what size flex is used. So the fuse will protect against a short circuit, but maybe not a small (but long term) overload. There are fuse current vs time graphs around if you’d like to dig further :) .
 
Thanks everybody.

I suspected it wasn’t right, even though the existing one is 16amp connected to a wall socket.

I haven’t had chance to look but did wonder if it was possible that the socket was on a dedicated 16A radial circuit , but as I understand it the socket would only be rated to 13A? And even then the safety of the cable is relying on the fuse blowing in time?

Apologies if that’s a load of bo****ks ^^
 
Hi - as above, use manufacturer’s installation instructions as your guide. No plug and socket for a 16A oven please. By the by, a 13A fuse won’t melt at 13A as that’s it’s rated working current. What we perhaps can’t be sure of is what size flex is used. So the fuse will protect against a short circuit, but maybe not a small (but long term) overload. There are fuse current vs time graphs around if you’d like to dig further :) .

Just had a quick look at the current v time graphs and apparently a 13A fuse can have 20A through it and not blow :eek:
 
Well .... the mi says 16a

So a dedicated circuit required ...
I agree, as I said before I had no intention of doing it any other way, I just wanted to satisfy my own curiosity about the potential consequences of connecting to a standard 3 pin plug / socket. Thanks for your help :)
 
It is not something you can say “it’s only a little over”
The limit is 13A, not 13.2A not 13.05A
13A IS THE MAXIMUM.
End of discussion.
 
I agree, as I said before I had no intention of doing it any other way, I just wanted to satisfy my own curiosity about the potential consequences of connecting to a standard 3 pin plug / socket. Thanks for your help :)

Rule of thumb .... if it comes with a 13a plug on it, plug it in, if it doesn’t you need to hard wire it.
 
It is not something you can say “it’s only a little over”
The limit is 13A, not 13.2A not 13.05A
13A IS THE MAXIMUM.
End of discussion.
I completely agree with you, as I said in my original post I had no intention of connecting to a 3 pin plug. I fully appreciate that the regs and max current ratings are there purely for safety and under no circumstances should they be exceeded.
I was merely asking to satisfy my own curiosity and I apologise for any confusion this has caused.
 
Could be way off the mark here.... if the existing socket was off a RFC then the MCB would be rated at 32A.
Would it be possible / acceptable for an electrician to remove the existing socket and fit a cooker control unit, providing the cable to the oven is suitably sized, say 6mm?
 
Yes, you are way off the mark. It is not permitted to connect loads greater than 13A to a ring final.
All connections to ring final circuits must have a fuse of no more than 13A (usually a fused BS1361 plug or an FCU).

In fact, the guidance is that fixed loads of more that 2KW should be on their own dedicated circuit.
 
Yes, you are way off the mark. It is not permitted to connect loads greater than 13A to a ring final.
All connections to ring final circuits must have a fuse of no more than 13A (usually a fused BS1361 plug or an FCU).

In fact, the guidance is that fixed loads of more that 2KW should be on their own dedicated circuit.
I didn’t think it would be as simple as that somehow :sweatsmile: so I either need to buy an oven under 2.9kW that has a plug fitted or get a sparky to run a new cable from the CU with a 16Amp MCB?
 
I didn’t think it would be as simple as that somehow :sweatsmile: so I either need to buy an oven under 2.9kW that has a plug fitted or get a sparky to run a new cable from the CU with a 16Amp MCB?
Hi - the common approach for providing power to electric cooking appliances is by their own circuit. While the design can vary, its often a 6mm cable with a 32A overload protective device. The actual appliance connection method used is then varied to suit the appliance.
Are you saying you have no cooker circuit?
 
Could be way off the mark here.... if the existing socket was off a RFC then the MCB would be rated at 32A.
Would it be possible / acceptable for an electrician to remove the existing socket and fit a cooker control unit, providing the cable to the oven is suitably sized, say 6mm?
NO
 
Hi - the common approach for providing power to electric cooking appliances is by their own circuit. While the design can vary, its often a 6mm cable with a 32A overload protective device. The actual appliance connection method used is then varied to suit the appliance.
Are you saying you have no cooker circuit?
I do have a cooker circuit but as far as know that’s for the electric hob on the other side of the room.
So it could be that the socket isn’t part of the RFC but is actually fed from its own 32A MCB?

If that was the case would it be acceptable /conforming to remove the socket and fit a JB/cooker connection unit with some 6mm T&E to the oven?
 
Last edited:

Reply to Wiring for new 16 Amp oven in the Electrical Appliances Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock