Discuss Wiring inside a kitchen island - conduit required? in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
We are installing a new kitchen and the electrician has supplied the electricity under the base units, there is a spur for a socket that will be installed at the end of the island.

The conduit from the floor is not long enough to reach the socket and so I have run the wire as-is in between the space behind the base units - the question is - do I need to put conduit all the way up to the socket? Or is it enough that the wire is inaccessible?IMG_0096.jpg
 
Last edited by a moderator:
The conduit doesn’t need to fully reach the socket, if the cable is standard grey twin and earth (6242Y)

The conduit is there so that the cable can be easily replaced if need be… not completely stuck in a concrete floor.

I did this not so long ago in a customers kitchen with a 25mm conduit for a 6mm cable for hob, and a 20mm conduit for a 2.5mm spur to a double socket for a little wine cooler and a pop-up socket tower.
 
The conduit doesn’t need to fully reach the socket, if the cable is standard grey twin and earth (6242Y)

The conduit is there so that the cable can be easily replaced if need be… not completely stuck in a concrete floor.

I did this not so long ago in a customers kitchen with a 25mm conduit for a 6mm cable for hob, and a 20mm conduit for a 2.5mm spur to a double socket for a little wine cooler and a pop-up socket tower.
Out of curiosity, any reason why you run two separate conduits? Thanks
 
Out of curiosity, any reason why you run two separate conduits? Thanks
The space available in the conduit and the size of the cables used is the reason for 2 conduits

In the past when I have installed island units I have used 40mm or 50mm waste pipe and swept bends rather than elbows for cables and water pipes or 63/50 twinwall ducting is good if it is a new slab and it is installed before the concrete is poured
 
Last edited:
Existing concrete floor.
Builder had to cut a chase to the island, and was making his job easier.

It’s also easier if a cable does need replaced, it’s not dragging against another cable.
 

Reply to Wiring inside a kitchen island - conduit required? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi everyone, please advice and comment on the attached wiring diagram for a kitchen. There are mixed opinions on the need for FSU-s and number of...
Replies
52
Views
4K
Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Replies
1
Views
348
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
899
Hello guys, It’s my first post here so please be gentle :) I’m having a kitchen extension done and will have the hob and few powerpoints...
Replies
4
Views
1K
After 24 years my septic lift station pump and high water alarm needs to be replaced. It was tripping the breaker and the alarm was no longer...
Replies
5
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock