Discuss Worcester bosch boiler programmer in the UK Electrical Forum area at ElectriciansForums.net

B

brizospark

I have been asked to add a programmer to a Worcester Bosch boiler. I am more of a commercial industrial spark and don't usually deal with domestic heating switching but want to give it a go. Will any brand of programmer be compatible with a WB boiler and does anyone have a wiring diagram? Also am I correct I assuming I will be requiring 4 core cable?
 
Is it a programmer or timer you need? I assume its a combi boiler so more likely a timer. Are you going to incorprate a room stat? You can use any brand. 4 core cable will be sufficient but i always use 5 core for boilers, one size fits all so to speak.Wiring is pretty straightforward but location of time clock,stat,fcu can create obvious problems.Have you considered using a Worcester Bosch unit that can be intergrated into the boiler ?
 
Whenever i fit an external programmer i usually run a 5 core out to it. Connections in the boiler are L,N,E, LS AND LR. A 4 core can be used if you put a link in the clock between L and 1.

Just check your boiler manual incase external controls are volt free
 
It is a new combi boiler for a flat that is to be rented out multiple occupancy so the timer needs to be in communal area which the boiler isn't can anyone recommend a make model that would suffice?
 
There are 3 rooms in the dwelling. 3 different tenants in house boiler is in one of the tenants room and at present to switch on CH the only way is to do so at boiler landlord wants ability to do this from communal hallway, what do you us recommend a stat and programmer?
 
Might be worth having a chat with the heating engineer. He may be able to incorporate some zone valves into the setup so that each person can control there own area as the people in the other rooms might not want the heating on
 
That has not been specified by the client all he wants is a programmer is this possible and if so what are connections in boiler and programmer?
 
MT10RF will do the trick, I used to fit dozens of these to worcestor bosch boilers.
It is a clock and stat combined, no wiring required, even the batteries are included. Just plug the receiver into the front of the boiler and screw the stat to the wall.
 

Reply to Worcester bosch boiler programmer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just looking at my boiler wiring out of interest, and just wondering if it's wired correctly. So perma lives, neutrals and earths in the right...
Replies
65
Views
5K
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
A question if I may before I dive in. I have an old gravity fed CH system which thanks to members here in the past - works very well. It has a...
Replies
3
Views
3K
As a young man, I was an electrician, but now I'm getting on, I am strictly DIY. I used to have a cheap old 900W petrol generator connected to a...
Replies
8
Views
1K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock