Hello,
I own a 1971 Mobile Home with Aluminum Wiring. Recently I had trouble with corrosion causing arcing at the metal clip area of my old breaker. I decided to buy two new breakers. I installed two new original equipment 15 Amp Breaker (aftermarket as original company is no longer in business)...
Hi there. I'm dealing with a difficult to locate problem with our 120V landscape lights. My first thought was there was a short somewhere in the run, but there seems to be something additional going on at the circuit breaker or closer to it. The circuit (one bundle of white, black, green)...
This is hypothetical, I am just curious. Please give this some thought.
I have a 600V, 5HP motor (3728.5 Watts) and a 600V panel I want to supply it from.
If I use a 20A, 600V breaker - the breaker will see ~6A on motor run. (P/V=I , 3728.5/600 = ~6A)
If I use a 20A, 240V breaker - the...
Hello everyone!
I’m a new homeowner and a new dad! I recently just built myself an office on my property and I wanted to run electricity to it.
I currently have the dreaded challenger panel and I wanted to know what breakers I can use with this panel?
I plan to run some lights and several...
I have a Square D panel for my apartment with following breakers: 1 double 40,2 double 30's and 4 single 20. One of the 20's controls a convection cooking panel, a small toaster, an 11 watt microwave, living room lights, n HDTV and my Internet. When all the above are on, during the past few...
As per title, what code do you think is applicable when a 63A RCD has a 40, 32, 6 & 20A breakers?
And gas not bonded but was required at time of building (2012) although not now?
Hi all, I'm hoping to tap into the wealth of advice on here to help me solve my LED light issue.
Background:
Brought an expensive dimmerable LED light from a UK company in August – Light fitting made and shipped from Hong Kong.
Light was installed by replacing the old standard wiring with ease...
I found that the circuit breaker had tripped on the downstairs lighting circuit after a light didn’t turn on. I don’t know what caused it but I found the the water heater breaker had also tripped (I assume is the water tank heater in the airing cupboard). I could reset the water heater but the...
Greetings, everyone!
I am trying to do a small, simple job: replacing an outlet in one of the bathrooms on 2nd floor of our house.
To do this, I am trying to shut off the power to that outlet. The breaker box was labeled by someone else (probably the previous owner). Alright...
So I tried all...
I have a 30amp breaker that feeds a circuit that goes through a double gang junction box and continues on to the final outlet for my electric clothes dryer. Since the junction box is accessible to potentially use, I was wondering if I can add a 20amp circuit breaker in that junction box to...
Hi guys, why might a fault on a final circuit in an apartment trip the dp c63 submain circuit breaker in the plantroom but not any mcbs on the consumer unit in the apartment?
Hello,
I have a 7.5kw 3 phase motor 400/690v 50hz. Can anyone advise what size and type mcb is needed for this please? It’s currently being fed via a c16 which is tripping now and then.
many Thanks
In my kitchen, I have 1 circuit with a total of 5 outlets (backsplash), and it appears to have a dedicated neutral which is connected to a Square D Homeline issue AE-70 20A combo AFCI/GFCI breaker in my panel.
I have a Miele espresso maker on this circuit. Occasionally but not always (maybe...
Hi, I try to install FSTWIFI on my towel rail heater, I think I connected everything correctly but when I switch it on it tripps breaker.
I would appreciate any help.
Thx, Rob
Below picture of connections.
https://www.dropbox.com/s/ttxxlxlvyu4idpc/20201013_202705.jpg?dl=0
I am in need of the 200 amp main breaker for a QOC-20M200 Series 1 breaker box. I have attached a picture for reference. I was told it is obsolete and have looked online but none of the reference pictures have the lower bolt-on as I have? Any help would be greatly appreciated!
Been asked to provide a 4 pole 16A socket with RCD protection with a C20 protecting the circuit specified by the manufacture of the machine, should I not use a 32A socket?