Search for tools and product advice,

Discuss 2 wire sounder question in the UK Electrical Forum area at ElectriciansForums.net

P

Patrick Griffin

In a 2 wire fire alarm system (non conventional) the sounder polarity is reversed to initiate the decive. Is L at the panel actually N in a non alarm state so? And in alarm state it reverses so current can flow through the diode initiating the decive.
 
On most conventional, but not all...the bell circuit polarity is reversed on alarm activation. Hence the diode on sounders and bell units. On a 2 wire conventional system, like Kentec Sigma T series or Haes Excel, the Zone is also reversed polarity on alarm activation.
 
Thanks tazz.

In a non conventional 2 wire system which has as you know only one circuit for initiating devices and alarm devices, the alarm devices also swap polarity to activate i beleieve, how does this happen if everything is on the same circuit? Is the entire circuit reversed polarity including initiating devices?
 
All manufactures detection will work reverse polarity without a problem, but the diode bases block the path. so most manufactures request Sav bases to over come this. All sounders/bells are then wired reverse polarity, on the same zone circuit, so when activated, the polarity is reversed, and sounders active.
2 Wire.jpg
 
Sav bases are used on all detection, smokes, heat etc. They allow the circuit to be monitored for head removal, and activation. Call points are standard 470 ohm types. You can place call points anywhere on the circuit, they do not have to be wired first. Sounders are standard, wired in reverse.
 
Its wired basically the same, but allows you to add sounders on the same zone wiring. Unlike the now obsolete Twinflex, the sav bases offer the use of good quality detection such as Apollo S65, and hochiki. Attached is kentec sigma manual, may help to explain better.
View attachment Sigma Manual.pdf
 

Reply to 2 wire sounder question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
638
Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
Replies
38
Views
4K
Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
786
Hi, I'm completely rewiring a 9 bed 3 storey HMO in Jan, The fire detection required is just some linked lithium detectors in the...
Replies
7
Views
754
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
361

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock