Discuss 3 phase surge on reenergising panel board in the UK Electrical Forum area at ElectriciansForums.net

bigspark17

-
Arms
Reaction score
718
Hi all..
Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin gerin panel board) over the next 30 mins customers on park are reporting loud bangs inside some of there vans, boilers and electric fireplaces (with pcbs) exploding..

Wondering if any1 else experienced similar or shed some light on this..
Seems to me like it could be a temporary loss on Neutral somewhere be it a downstream fault in cable, loose neutral or dodgy main switch (was 4 pole) if the neutral lost on 3 phase with then single phase circuit voltage rising to 400v+ would have caused this pcb problems..

Appreciate and info :)
 
i think you are right on the cause, loss of neutral whilst 2 or more phases are connected.

If it was the IR testing that damaged things, i would expect delicate electronics to fail but not in a loud bang type of way.

map out the damage by phase and distribution board, the fault must be upstream of them all and probably downstream of everything that has had no faults on attached circuits.
 
Typical result of neutral loss, the remaining phases use anything that was connected to neutral as a alternative path yet much higher voltage, the main neutral bar becomes a star point of the phases and loads connected allow the voltage rise often destroying delicate circuitry.
 
Yup, definately sounds like more than one phase energised and no neutral. Did you do any tests after the event or did you just run away before the pitchforks came out?

I'd start by testing the 4-pole isolator you used to isolate the power. Also check it's actually a 3pole and neutral isolator where the neutral is late break / early make, I've seen it where some nimrod has used 2x single pole isolaters/MCB's and fitted a rail between the individual levers to make it operate like an SP+N breaker so I wouldn't put it past someone to do something similar with a 4-pole MCB or isolator...
 
It's going to be a right kerfuffle with all the insurance claims. Especially when people claim for the brand new ipad which they had on charge at the time (honest guv)
 

Reply to 3 phase surge on reenergising panel board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A bit of an embarrassing question. I have a regular customer who I enjoy working for. He has asked me to install an EV rapid charger for his...
Replies
64
Views
10K
Quick question, have a small caravan site to wire up. Have 3 phase supply and TT earthing, 30ma RCD in each individual pods. Was planning on...
Replies
38
Views
12K
I have my AM2 exam and the question I have is how would you confirm supply polarity? Would you do the following tests:- L1-L2 L1-L3 L2-L3 L1-N...
Replies
12
Views
5K
Hi all, Been a few years since i've posted but here goes! At the factory I work in we have an old Spanish line from the mid-eighties that is fed...
Replies
6
Views
5K
Hi does anyone know what if any type of MCBs/rcbos are compatable with merlin gerin 3 phase boards.
Replies
25
Views
5K
baldsparkies
B

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock