Discuss 6mm to 2.5mm for sockets in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
20
Hi

I've got a job that i've been asked to quote for and i'm struggling with how to do it the best way.

It's a summerhouse and the customer only wants a couple of double sockets and a light in it. My issue is that it's a fair distance from the house where the supply will be taken from. I've done the volt drop calcs and 6mm will be fine upto 20A max load. The existing consumer unit is full so I've got 2 options, spur from one of the socket mcb's (32A) to a fuse spur, then run to summerhouse giving 13A and enabling me to have both sockets without it being a spur off a spur (if I went straight from the MCB) or split supply at house to small RCD main switch DB at house end and use a 20A mcb to feed summerhouse. She mentioned using a kettle in the summerhouse so would like to give her more than 13A really. Ultimately I'm trying to keep costs down as best I can.

Also if I'm using 6mm to solve the volt drop issue can I take that to an adaptable box at the summerhouse then connect 2.5mm onto it to go to the sockets as the 6mm will be too big for the socket terminals.

Cheers Tom
 
can I take that to an adaptable box at the summerhouse then connect 2.5mm onto it to go to the sockets as the 6mm will be too big for the socket terminals.
Yes. But what about lighting? You'll need another switched FCU with 5A fuse in it for lights.

In the house,13A FCU will be fine, providing she doesnt have kettle plus heater!
take a look at the current required to actually BLOW a 13A fuse.

PS, I'm surprised that 6mm is necessary. How far are we talking about?
 
Yes. But what about lighting? You'll need another switched FCU with 5A fuse in it for lights.

In the house,13A FCU will be fine, providing she doesnt have kettle plus heater!
take a look at the current required to actually BLOW a 13A fuse.

PS, I'm surprised that 6mm is necessary. How far are we talking about?
Yes I was going to put a spur in for the lights in the summerhouse. It's about 60 metres. You never know what people will plug in so was trying to give as much power but keep costs down
 
Can you not get back to the consumer unit , split the tails in a henley and pop a new small board in to feed the outhouse submain
 
To be honest, my first choice would be neither!
or split supply at house to small RCD main switch DB at house end and use a 20A mcb to feed summerhouse
My thinking would be to split the supply at house with overcurrent protection but not RCD, and have small CU with RCD in the summerhouse . This assumes the house is not TT and the 6mm cable is mechanically protected or in ducting.

Then a future inevitable fault outside (e.g. light fitting filling with water) won't turn off half the house.
Your method still achieves that but is a longer walk to turn it back on again!
 
To be honest, my first choice would be neither!

My thinking would be to split the supply at house with overcurrent protection but not RCD, and have small CU with RCD in the summerhouse . This assumes the house is not TT and the 6mm cable is mechanically protected or in ducting.

Then a future inevitable fault outside (e.g. light fitting filling with water) won't turn off half the house.
Your method still achieves that but is a longer walk to turn it back on again!
Yeah I know what your saying. Did one like that recently. Just trying to keep costs down. There isn't any outside lights etc so hopefully not much that can fill with water at the summerhouse.
 

Reply to 6mm to 2.5mm for sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've had a search, and found an old thread from 2016... but was wondering about modern views on this situation. I've come into possession of...
Replies
5
Views
367
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
295
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
940
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
669
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock