I would probably opt for a 20a rcbo at the house and just mcbs in the shed , just the way I would do it
 
If you are looking at absolute minimum cost then feed the SWA from a RCD protected supply so you can use 2-core cable, then minimum to meet 5% VD and 13A use is 4mm.

If you go for a non-RCD supply your end of cable Zs becomes a factor, though for small SWA the 2C armour R1 is less than the copper R1, but not once above 2.5mm. Here is a crude calculation and assuming TN-S 0.8 ohm Ze and not computing parallel armour + copper R2 in the 3C case:

mm^2 \ length (m)​
60​
V/A drop​
A for 5%​
A for 3%​
R1+R2 2-core​
R1+R2 3-core​
Zs for TN-S 2C​
Zs for TN-S 3C​
1.5​
31​
1.86​
6.2​
3.7​
22.3​
24.2​
2.1​
2.3​
2.5​
19​
1.14​
10.1​
6.1​
16.2​
14.8​
1.8​
1.7​
4​
12​
0.72​
16.0​
9.6​
12.5​
9.2​
1.6​
1.4​
6​
7.9​
0.474​
24.3​
14.6​
10.1​
6.2​
1.4​
1.2​
10​
4.7​
0.282​
40.8​
24.5​
7.8​
3.7​
1.3​
1.0​
So if going for a 13A fuse with max Zs 1.84 ohm and no RCD (very unlikely...) you would be OK for 2.5mm but only 10A max load.

At 4mm you could probably disconnect on OCPD for a 20A B-curve MCB (Zs 1.75 ohm) but if only an out-house I would split tails, put in a small CU with RCD and 20A breaker to feed the cable, and for the out house just have the sockets dropped to 2.5mm as you suggest and a 3A FCU taking off power for some LED lights.

If there is any chance of it being used for office (i.e. PC) or with a TV (wanting Netflix, etc) then I would suggest they put in some armoured CAT-5 or CAT-6 network cable at the same time as there is a trench for the power cable.
 
To keep costs down.... Terminate the 6mm SWA into a 45A (or maybe even 20A) metal-clad double pole switch at the shed end acting as a "main switch," from there to your double sockets and a 3A SFCU acting as a light switch.
 

Reply to 6mm to 2.5mm for sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've had a search, and found an old thread from 2016... but was wondering about modern views on this situation. I've come into possession of...
Replies
5
Views
367
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
295
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
943
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
669
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock