Hi guys,

I would just like to ask if any one could look at my test procedure off the top of my head and give any advice or pointers or whether its too long winded or short. got an exam in 2 weeks so trying to drill it in to this thick skull :)
Many thanks

Safe Isolation has been carried out:



  • Seek permision , Inform client and relevant persons that test is about to be carried out
  • Make area safe by putting up barriers and warning notices
  • Disconnect lamps and link out or disconnect other sensitive devices that may be vulnerable to test voltages
  • Select an insulation resistance tester, Check tester is calibrated, leads show no sign of damage, and that tester is functioning.
  • Select the Megaohm range set at 500V DC
  • Identify circuit to be tested, and test between Live - Neutral and record result. Do the same test between Live - Cpc and Neutral - Cpc record results.
  • Expected result a minimum of 2 M/ohm.
  • Reinstate circuit
 
you have not mentioned safe isolation and lock off. that should be your 2nd bullet point. ... prove volage tester, isolate, prove dead... before you connect IR tester.
 
Megohms not megaohms, your terminology is very important mate. Everything you need to know is in GN3 so stick your head in that and only come up for air.
 

Reply to Advice on insulation resistance test procedure :) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
707
Evening chaps, I've been asked to do a visual inspection, and an insulation resistance test on a fishing boat, which is working off 24v, this is...
Replies
3
Views
2K
I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch...
Replies
9
Views
2K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock