Search the forum,

Discuss AFDD in 18th 2nd Amendment in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Status
Not open for further replies.
Reaction score
115
18th 2nd amendment comes in, in Sept.
AFDDs are in it. To be fitted on socket circuits of 32A and above.
To be fitted in residential blocks of 6 floors and above, care homes and the likes.

Are these mandatory for everyone? If say you have a 17th edition CU, do you have to update to AFDD?

AFDDs integrated with an RCBO which appear the perfect fit and fix, but £150 each.


1649710309815.png

https://www.NoLinkingToThis/p/wylex-nxs-25a-30ma-sp-n-type-b-afdd-rcbo/706jk
 
There are two aspects to this.
1) Inspection and Testing
The installation will be inspected according to the latest regs, and the safety of the system decided according to the judgement of the person inspecting it. There is no obligation to upgrade installations for inspection purposes unless there are safety concerns.

Eventually most inspectors decide that enough time has passed since a reg change was bought in that it moves from an suggested improvement to a potential safety issue requiring action. For example TT earthing via a metal water pipe was allowed once. We wouldn't hesitate to C2 it now. Many people decide lack of RCD for sockets outside is now a C2. To my thinking it will be a good while before lack of an AFDD become a C2 items.

2) Modifications or Extensions
This is more complicated but in general if modifying a circuit or providing a new circuit, that circuit will comply with latest regulations. The overall installation shall be in a safe condition to modify or extend. (BTW any AFDD fitted should be the same manufacturer as the enclosure.)
I think we're all still working out exactly how these ideals play out in practise. There's a discussion on another thread about this at the moment.
 
On your note 2, Tim, if you’re going to add an afdd because you are adding a new circuit to an existing installation, then you would need to change a plastic CU to metal for the same reason.

They are still cost- prohibitive for adding as we would change an mcb to RCBO

It will encourage Have-a-go Henry’s avoiding paying for a professional when a simple job becomes too costly
 
On your note 2, Tim, if you’re going to add an afdd because you are adding a new circuit to an existing installation, then you would need to change a plastic CU to metal for the same reason.
This is where it gets interesting. I don't actually see it like that. I'm also not saying I'm definitely right, and am very interested how others approach this.

How I'm thinking -
If I was adding a lighting circuit in a dwelling, I'd need the lighting circuit to be RCD protected to meet 18th edition.
Everything about my work concerning the new circuit has to be to latest regs.
I don't currently include the enclosure it's going into in that thinking. I'm not modifying the CU, so I feel no responsibility to change it to metal or add an SPD for that matter. My only responsibility is that the installation as a whole is safe to extend, so the CU needs to be safe, no holes in it, no thermal damage, it has a cover etc.
(The exception would be if the only way to provide RCD protection was to change the CU, in which case the CU would have to meet latest regs and yes then we're into metal box and probably SPD.)
I'd better say that I would include earthing, bonding, and tail sizes in the thinking though, and would upgrade these if found wanting.

I think the same applies to AFDD's, if I was adding a sockets circuit in a building which needed one, applying the same logic as above then it should really have one. If there's no upgrade path for the CU then it's new metal CU, SPD, and all the =32A sockets circuits need AFDDs.

At least that's how I see things. Very happy to observe more discussion and think more about it though!
 
I don't ever recall the regs saying must be metal

non-combustible, then....

Try asbestos
As written, only ferrous metal is acceptable. As we well know, the reg is a pile of poo and it's hard to understand how a supposedly professional committee could have passed it - and harder still to understand how they failed to fix it in the ltest amendment.
As written, no material complies - simply because there is no material which can be said to be non-combustible without adding some qualifications. An oxygen lance can usually cut through many things we consider non-combustible. It is only the note added that says ferrous metal is deemed to comply which makes steel enclosures "compliant".
And all it needed was for them to say something along the lines of "meets text X in BS EB YYYYY" - then I reckon a fair number of non-metallic enclosures would be acceptable (like the old Wylex fuse boards)
 
As written, only ferrous metal is acceptable


421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:

(i) have their enclosure manufactured from non-combustible material, or

(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.

NOTE 1: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.


What are non-combustible materials?

• Non-combustible means that the material will not ignite, burn or release flammable vapors. when exposed to fire or heat. Examples of non-combustible materials include steel, masonry, ceramics and certain insulating materials (such as fiberglass or mineral wool insulation).
 
Last edited:
What are non-combustible materials?

• Non-combustible means that the material will not ignite, burn or release flammable vapors. when exposed to fire or heat. Examples of non-combustible materials include steel, masonry, ceramics and certain insulating materials (such as fiberglass or mineral wool insulation).
Definitely not plastic.

I’d like to see a consumer unit made of ceramic or brick… 🤣
 
  • Like
Reactions: DPG
Eventually most inspectors decide that enough time has passed since a reg change was bought in that it moves from an suggested improvement to a potential safety issue requiring action.

No, time isn't relevant to whether it becomes an issue. Some things will never become a safety issue and other things are straight away.


For example TT earthing via a metal water pipe was allowed once. We wouldn't hesitate to C2 it now.

I would certainly hesitate, the use of a metal water pipe as an earth electrode is still allowed.

If it is no longer providing an adequate connection to earth then it would be a C2, but if the connection to earth is adequate then it may be a C3 or no code depending on who owns the pipe.
 
No, time isn't relevant to whether it becomes an issue. Some things will never become a safety issue and other things are straight away.
Thanks - I can see it wasn't obvious but I was talking about what a lot of inspectors do, not intending to say it was right.
The emphasis was supposed to be the preceding bit "The installation will be inspected according to the latest regs, and the safety of the system decided according to the judgement of the person inspecting it. There is no obligation to upgrade installations for inspection purposes unless there are safety concerns."
I was trying to say that in spite of this, many people seem to decide "it's about time that was a C2". We see it time and time again on EICR's posted here.

I would certainly hesitate, the use of a metal water pipe as an earth electrode is still allowed.
Only in very specific circumstances though! I'm sure the default position is they shall not be used unless privately owned and other caveats that I'm not looking up tonight! Maybe VOELCBs would have been a better example.
 
421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:
(i) have their enclosure manufactured from non-combustible material, or
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.
On that there is no debate.
NOTE 1: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.
Which makes ferrous metals (i.e. steel) acceptable.
What are non-combustible materials?

• Non-combustible means that the material will not ignite, burn or release flammable vapors. when exposed to fire or heat. Examples of non-combustible materials include steel, masonry, ceramics and certain insulating materials (such as fiberglass or mineral wool insulation).
And here is the problem. You cannot use that definition, or any standards for combustibility ratings, as BS7671 does not reference them. As has already been said several times, all they had to do was specify it in terms of "non-combustible according to <some standard for such things>". Had they done that, then there'd be no problem - if a material meets the referenced standard then it's OK, if it doesn't then it isn't.
As I've pointed out, steel is not "non-combustible" as you can certainly get it to combust under the right conditions. I suspect at least some of the rest can also be made to combust if you try - OK, I suspect concrete and rock melt and flow rather than oxidise when an oxygen lance is aimed at them.

And that is the problem, because BS7671 does not specify what the standard for non-combustible is, there really aren't any practical materials that can be said to comply - steel doesn't. It is only the presence of note 1 that makes steel acceptable.
 
On that there is no debate.

Which makes ferrous metals (i.e. steel) acceptable.

And here is the problem. You cannot use that definition, or any standards for combustibility ratings, as BS7671 does not reference them. As has already been said several times, all they had to do was specify it in terms of "non-combustible according to <some standard for such things>". Had they done that, then there'd be no problem - if a material meets the referenced standard then it's OK, if it doesn't then it isn't.
As I've pointed out, steel is not "non-combustible" as you can certainly get it to combust under the right conditions. I suspect at least some of the rest can also be made to combust if you try - OK, I suspect concrete and rock melt and flow rather than oxidise when an oxygen lance is aimed at them.

And that is the problem, because BS7671 does not specify what the standard for non-combustible is, there really aren't any practical materials that can be said to comply - steel doesn't. It is only the presence of note 1 that makes steel acceptable.
There is no published definition for the term ‘non combustible’ that aligns with the intent of Regulation 421.1.201. However, as stated in Note 1 to the regulation, ferrous metal, such as steel, is deemed to be an example of a non-combustible material.


Steel will no doubt be the material usually employed in the manufacture of the enclosure or cabinet. Nevertheless, it will be open to manufacturers to offer enclosures or cabinets made from other types of material that they claim to be non-combustible within the intent of Regulation 421.1.201. In this case, however, the manufacturer would have to provide suitable evidence to support the claim of non-combustibility, and it is not presently clear what criteria would be used to judge the non-combustibility of a material other than non-ferrous metal.

Non-combustible materials include: Any material which when tested to BS 476-11:1982 (2007) does not flame nor cause any rise in temperature on either the centre (specimen) or furnace thermocouples. Products classified as non-combustible in tests following the procedures in BS 476-4:1970 (2007).
 
But BS7671 does not reference BS476 either. So because something can pass a test defined in BS476 doesn't mean it meets the requirements of BS7671.
We all know what the intent of the reg is - but as currently worded, steel is effectively the only permissible material.
 
We all know what the intent of the reg is - but as currently worded, steel is effectively the only permissible material.

The fact that some manufacturers are offering die-cast CUs suggests that they view metals other than steel as suitable.
 
18th 2nd amendment comes in, in Sept.
AFDDs are in it. To be fitted on socket circuits of 32A and above.
To be fitted in residential blocks of 6 floors and above, care homes and the likes.

Are these mandatory for everyone? If say you have a 17th edition CU, do you have to update to AFDD?

AFDDs integrated with an RCBO which appear the perfect fit and fix, but £150 each.


View attachment 96764

https://www.NoLinkingToThis/p/wylex-nxs-25a-30ma-sp-n-type-b-afdd-rcbo/706jk
Socket circuits not exceding 32a John.
 
The fact that some manufacturers are offering die-cast CUs suggests that they view metals other than steel as suitable.
Die cast in what ? OK, sloppy use of words, but "steel" is shorter to write than "ferrous metal" - I'm assuming you mean die cast iron - plastic CU cases are die cast, as are many aluminium boxes (obviously excluding ones that are folded from flat sheet), ...
Look up chlorine trifluoride.
No I hadn't heard of that, and no I don't intend to experiment with it 😱 So that demonstrates that without a definition of "non combustible", not even concrete or rock (which would traditionally be classed as non-combustible) can't truly be said to comply. And the answer to "is it combustible" remains the counter question "under what conditions ?"
 
Die cast in what ? OK, sloppy use of words, but "steel" is shorter to write than "ferrous metal" - I'm assuming you mean die cast iron - plastic CU cases are die cast, as are many aluminium boxes (obviously excluding ones that are folded from flat sheet), ...

I don't know what metal they are specifically but the have the feel of, and drill like, the kind of metal boxes that are often sold as just 'die cast project boxes'. I think they are usualy some aluminium/zinc/magnesium based alloy but don't know for sure.
 
Aluminium is "interesting".
Having looked it up, it's classed as non-combustible as a solid - but I think we're all aware that if you do get it going, which is a lot easier in powder form, then it takes off big time (c.f. Thermite). But again, because BS7671 doesn't specify how "non-combustible" is determined (e.g. by reference to existing standards), there's no objective way of saying aluminium complies with the regulation.

But having said that, die-cast aluminium CUs would be quite nice to work with.
 
  • Like
Reactions: DPG
Diecast aluminium can be nice to work with, but it can also easily crack if mistreated trying to put in a big hole, etc.

Realistically pressed steel sheet is the cheapest and easiest solution to making a CU fire-containing, though some plastics would also be an option (but probably more expensive).
 
Aluminium is "interesting".
Having looked it up, it's classed as non-combustible as a solid - but I think we're all aware that if you do get it going, which is a lot easier in powder form, then it takes off big time (c.f. Thermite). But again, because BS7671 doesn't specify how "non-combustible" is determined (e.g. by reference to existing standards), there's no objective way of saying aluminium complies with the regulation.

But having said that, die-cast aluminium CUs would be quite nice to work with.
NOTE 1: Ferrous metal, e.g. steel, is deemed to be an example

Aluminium is a non-ferrous metal


The regs point is that the enclosure be non-combustible, if a manufacture produces a consumer unit and specify that it's non-combustible then I can't see any reason for not using it.
 
Last edited:
If they specify that it's non-combustible to the standard specified by BS7671, no problem. Now which standard does BS7671 reference 🙄
 
If they specify that it's non-combustible to the standard specified by BS7671, no problem. Now which standard does BS7671 reference 🙄

They also don't specify a standard for steel ones either.
 
No, but they specified that its deemed to comply - therefore using steel (or any other ferrous metal) complies with the regs.
 
No, but they specified that its deemed to comply - therefore using steel (or any other ferrous metal) complies with the regs.

They only deem it to be an example of a non-combustible material, they don't say “steel complies”.
 
The practical effect of the wording is that they say exactly that. Is there any other interpretation of "You must use X, ferrous metal is deemed to be X" other than "using ferrous metal complies with the requirement to use X" ? Since steel is a ferrous metal, then using it is deemed to comply because the note says it does - there is no scope for doubt since ferrous metal is by definition one based on iron, and steel is an alloy composed mainly of iron.

Though I suppose you could go down the rabbit hole of pointing out that they don't define what ferrous metal is ...
 
NOTE 1: Ferrous metal, e.g. steel, is deemed to be an example

Aluminium is a non-ferrous metal


The regs point is that the enclosure be non-combustible, if a manufacture produces a consumer unit and specify that it's non-combustible then I can't see any reason for not using it.
Cast Aluminium, available from screwstation.

Are these compliant?

Screenshot_20220820-122649_Samsung Internet.jpg
 
I would say yes as long as it's deemed to be non-combustible, but that’s listed as a garage consumer unit.

According to Luceco Technical Team,
This board is fully compliant with all of the manufacturing requirements in the 18th edition of the wiring regulations.
 
Last edited:
Realistically all of the metals used for electrical work are going to be acceptable, steel is cheapest and easy to work with. Aluminium is easier to mould in to odd shapes and has some theoretical advantages (e.g. higher strength to weight ratio, non-magnetic, higher conductivity) but cost is likely to go against it. Same for copper and brass, but knobs on the price tag.

There are some metals that would not be acceptable, most obvious is magnesium alloys as they will burn spectacularly in air if heated to even normal temperatures. Less obvious are alloys with large amounts of beryllium in them as they result in toxic dust if worked, as well as being expensive.
 
Trying to get my head round this. Chlorine trifluoride? Crikey, i don't want to meet that any time soon! However, that and an oxygen lance are unlikely bedfellows for a domestic CU. I'm presuming that what the regs are intending, though not saying, is that the material used should be non-combustible "in the normally envisaged environment in which it is installed"...I'm simply thinking that, eg in a normal house, you are unlikely to encounter a situation where conditions can exist which would cause a normally non-combustible material to go on fire, and the purpose of the enclosure is to contain any fire that may occur within the enclosure, or prevent any fire externally from gaining access to the interior of the enclosure. I can see that steel is probably the easiest and cheapest solution for many reasons. Would carbon fibre be an option as i believe it has a very high temperature melting point and doesn't actually combust? It would look really "cool" too!
 
I checked the specs on them and it actually says its cast steel.

You checked the wrong one.

Put 1926g in.

https://www.NoLinkingToThis/p/briti...d=337165#product_additional_details_container
 
I'm presuming that what the regs are intending, though not saying, is that the material used should be non-combustible "in the normally envisaged environment in which it is installed"
Yes, I think we all assume that. But in terms of signing a certificate to say "this installation complies with BS7671 ed foo amd bar" then I don't think "we all assume" is sufficient. I'd agree that an oxygen lance or ClF3 is highly unlikely to be involved, but I'm sure some interesting cases have come up in the past - hence the adage that nothing is foolproof as fools are so inventive.
All they (the committee behind BS7671) had to do was reference an existing standard, or simply state "when heated to X˚C in a normal atmosphere" if they didn't want to use an existing standard. Had they done that then there'd be an objective test allowing the use of any material that met the specific requirements. I.e. it would be really easy - "does the material meet the laid down objective test ?", if yes then it can be used.
 
Yes, I think we all assume that. But in terms of signing a certificate to say "this installation complies with BS7671 ed foo amd bar" then I don't think "we all assume" is sufficient. I'd agree that an oxygen lance or ClF3 is highly unlikely to be involved, but I'm sure some interesting cases have come up in the past - hence the adage that nothing is foolproof as fools are so inventive.
All they (the committee behind BS7671) had to do was reference an existing standard, or simply state "when heated to X˚C in a normal atmosphere" if they didn't want to use an existing standard. Had they done that then there'd be an objective test allowing the use of any material that met the specific requirements. I.e. it would be really easy - "does the material meet the laid down objective test ?", if yes then it can be used.
Wouldn't that be BS EN 61439-3.
 
Last edited:
But I suspect this thread has descended in to an electrician's equivalent of "How many angles can dance on the head of a pin?"
 
angles??? angels??

Id take the manufacturers data sheets over Screwfix's description any time.
Yes, looks like screw fix messed up, i'll shop at tool station from now on :)
 
is that for the 1926g
I looked a bit more and indeed you're right, not that i would use BG anyway as the last time i used one 3 of the mcbs were faulty.
 
Screwfix info says for the 1926g


Specification
BrandBritish General
Cable Entry PointsTop, Bottom, Side & Rear
Construction Material (Electrical)Aluminium
Consumer Unit TypeGarage
CSU Populated/UnpopulatedPopulated
Current Rating40 A
Fixings SuppliedFixings Not Supplied
IntegrityNon High Integrity
IP RatingIP65
You don't believe all that the Screwfix website says do you
 
You don't believe all that the Screwfix website says do you
I'll just quote Pete, “How many angels can dance on the head of a pin”
 
I have fitted one of those BG units and I could have sworn it was a cast ally/lightweight alloy from the weight and the way it drilled.
 
I have fitted one of those BG units and I could have sworn it was a cast ally/lightweight alloy from the weight and the way it drilled.

Just did a bit of digging as I know there have been changes to these boards over the years, but can not find anything which confirms if aluminium was ever used for the enclosure. I know they used to be (probably still are) cast, rather than pressed, which might account for the odd feel it had when drilling.
 
Status
Not open for further replies.

Reply to AFDD in 18th 2nd Amendment in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Locked
So, a flat 6 floors and above needs an AFDD on each socket circuit. At up to £150 each it is going to be an expensive undertaking if there are...
Replies
21
Views
3K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
78K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock