I’ve got a job coming soon to replace an old Fusebox with an all rcbo unit.
The box at the moment is mounted behind an access door in the wall.
It may be the new CU is wider than the existing door, but that’s not really the problem.

The distance between the front of the new CU and the access door may mean that any access lid on the cover might not open fully.

Could I remove the hinged lid from the CU?
There’s no chance the breakers could be accidentally turned off as they’re still behind the access door in the wall.
 
The lid is supposed to help contain an exploding/burning MCB/ RCBO/RCD
Ok. Makes sense. Never thought of it as a safety feature, just aesthetics.

much better than the old plastic hinges that either broke, or would open but not shut again.
Or the covers on fuse boards with the thumb turn. Always find them laying on top of the fuseboard, not back where they should be.
 

Reply to Altering consumer unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a doorbell I want to install. The issue is the 16v transformer is designed to sit on a DIN rail. I have a 10 way 17th edition BG Nexus...
Replies
4
Views
908
Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Replies
2
Views
851
Hi All, looking for some assistance on this as finding different information wherever i look. We have a garage external to the house, which we...
Replies
22
Views
4K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
4K
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock