Search the forum,

Discuss Am I missing something here? in the Australia area at ElectriciansForums.net

T

Thenitwentbang

This week, I finally decided to get on with rejuvenating the supply to my garage. This was in place when we moved in and, in all honesty (and on the face of it) is not a bad job. Notwithstanding this, I do probably put more demand on the circuit than the original installer probably intended, so I want to make sure it's all tickety boo and up to the job.

As I say, the existing supply to the outbuilding (which was in place when we moved in) is not actually a bad job - on the face of it. It is a spur from the downstairs ring (lounge - not kitchen) and leaves the house through a 30ma RCD protected FCU. It then makes it's way down the garden in 3 core 2.5 SWA, within black PVC conduit, which has been clipped to fence posts (with additional horizontal supports to stop sagging). There is a reasonable IP 55 CU in the garage already and someone has done a fairly neat job of adding sockets and lighting in the garage. I intend to move the supply from the existing FCU spur to a dedicated RCBO in the CU. Probably worth pointing out at this point that we are TN-S.

One thing does concern me, however, is that the route of the SWA from the spur to the garage makes it's way into my garage through our neighbour's garage (we are the centre garage in a block of three). I can see that it runs through my neighbour's garage within a very old piece of steel conduit - the end of which is just visible as it enters my garage. I don't like the fact that I have not yet seen how this is fixed in the neighbouring garage - or what state it's in. This is one of the key reasons I want to refresh it all.

Before I get on with changing anything, I decided, last night, to start with a few basic tests; to establish the health and integrity of the existing circuits.

An IR test on the external part of the circuit (SWA from the house to the garage) all checked out OK; seeing a reading >1000M Ohms on L-N, L-CPC and N-CPC.

Testing the continuity of the earth on the existing external wiring (disconnected from spur at house, line and CPC linked at garage CU) shows 0.39 Ohms. Naturally, that's not a full R1+R2, but some indication of the health of the existing external line and CPC conductors in the external SWA up to the garage. Notwithstanding this, a full Zs test from the sockets in the garage is more concerning at 3.6 Ohms!!! It's now disconnected and I'm definitely having all the sockets out to find out what's going on there. I'm sure that moving the garage feed onto it's own RCBO will play a part in rectifying this as the fault may well have been down to a poor connection at the FCU.

Given my concerns about the health of the piece of steel conduit in my neighbour's garage (that I have not yet been able to inspect) I also checked to see if there was any difference in potential between this and my own installation. After probing the exposed end that enters my garage with a voltage tester (and getting a reading of 36 volts) I'm glad I did that. What was more worrying was a reading (using my MFT) of 41V between the neutral and CPC in my garage and the exposed end of the conduit in my garage. Naturally, I have now fully disconnected the external circuit at the FCU. Even with this fully disconnected, I still see an indication of voltage at the exposed end of the conduit - and the MFT confirms 50 HZ.

I also see similar readings on the armour of a short length of SWA that comes from the afore-mentioned adaptable box, up the outside garage wall and through the neighbouring garage. I should point out that the armouring has not been used as CPC or bonded; it is terminated into plastic SWA glands at the adaptable box where it leaves the house, at an adaptable box on the external garage wall (junction point of long cable run from house and shorter run through the neighbouring garage into mine) and at the existing garage CU. This would indicate to me that the external insulation on the SWA is damaged as it makes it's way through the steel conduit in the neighbouring garage - so that is very high on the replacement list, also.

As I say, the circuit is now fully disconnected, pending further investigations - and a look at what's going on next door. I suspect that one of two things has happened - either the steel conduit has been bonded to the earth in the neighbouring garage and is becoming live through a fault in that circuit or it's making contact with something in there that is introducing the voltage. Given that I can see voltage present even with the supply disconnected from the spur, I know that this is not coming from the spur wiring - the IR tests would also seem to bear that out. Equally, I'm not blind to the fact that I may be missing something.

My big concern with this is the increased risks posed by the potential for much higher potential differences between line conductors in neighbouring properties, fed from different phases by the DNO.
My personal preference (if I can not find another reasonable route for the new external cable to take) will be to replace the existing metal conduit within the neighbouring garage with some very heavy duty plastic - fully enclosing the SWA from the point of entry to the point of exit. If I can realistically satisfy height requirements, I may actually opt for a catenary wire - rather than the existing route through the neighbouring garage. Additionally, I will be using proper brass SWA glands and bond to the armouring.

Any thoughts or ideas would be greatly appreciated - just conscious that my concerns over the path through the neighbouring garage may be giving me a bit of tunnel vision here!
 
Right, all wiring to my garage removed and the conduit in the neighbour's garage still showing voltage - at 50Hz. Think that confirms what I thought. Conversation with the neighbour will ensue!!!
 
Think you are pretty much answering your own questions in that having part of a circuit run through a neighbour's property is not a good idea. The other thing when you start to re-install the circuit you need to consider voltage drop and whether you should be increasing the cable size.
Also is there a need for main protective bonding in this garage and if so does it make it more economical to
provide it with an earth rod and make it part of a TT system?
 
Everytime there is a garage or shed there has to be the should you. TT it. No he should not TT it. He has good earth in the house with it being a TN-S.
 
Thanks for the replies - as you say, Hawk8, the house is TN-S, so I am satisfied that there is not need to TT the garage (and I certainly never intended to start that debate again!)

Going to upgrade the SWA to 4 MM. The length of run is just about 30 M - so running this in 2.5 would be optimistic!

Going to speak with the neighbour today and see if I can get his agreement to run the cable across the front of his garage externally. Tucked up, close to the guttering, it should not be too unsightly and at least it provides bettert separation from any circuits in his property. I'm sure he'll be happy with that - especially if I offer to make good the unnecessarily big hole someone has punched in his wall to put the previous cable run through his garage!!
 
Go for the external rout if possible. The cable is then open to inspection by you at any time. I’ve a nasty suspicious mind and know it wouldn’t take me long to tap in to your supply J if I were a new neighbour.
As to earthing, this TT issue is wearing a bit thin. (I’ve got my own views and I’ll keep then to myself).
 
Yeah, defo keep your install OUT of your neighbours premises. theres always the no no of having two supplies in the one premises. I think you've pretty much answered all your own questions. One thing you still may want to do (which is also advantagous for your neighbour and for you as he may pay you to put right any faults found :) ) is inspect the installation in his garage and disconnect that conduit from it if possible and thus removing the chance of it become live under fault conditions.
 
Yeah, defo keep your install OUT of your neighbours premises. theres always the no no of having two supplies in the one premises. I think you've pretty much answered all your own questions. One thing you still may want to do (which is also advantagous for your neighbour and for you as he may pay you to put right any faults found :) ) is inspect the installation in his garage and disconnect that conduit from it if possible and thus removing the chance of it become live under fault conditions.

Thanks Wiredspark, thanks Tony.

Yep - external route makes sense and, yes, I do think I'll suggest to him that I have a look at his installation and disconnect this piece of conduit from it.

The installation in his garage has been there pretty much since the houses were built. Previously, he has told me that it's no more than a bit of T & E that exits his house, goes under the garden and re-surfaces somewhere in the garage!!!
 
Everytime there is a garage or shed there has to be the should you. TT it. No he should not TT it. He has good earth in the house with it being a TN-S.

:confused:

Hi Hawk, i certainly was not saying it should be TTed but up until that point there had been no mention of distance and whether or not main protective bonding was needed. An open mind is what is needed. There can certainly come a point where it is more economical not to use the earth at the original CU.
 
Even for economic reasons I still do not believe in ditching a good earth for a non stable earth is good practice.

Neither do I :confused: But if i had to do an awkward run of 50+M of 10mm² for a MPB i might consider knocking in a £2.60 earth rod to see what Ra i was getting. It's usually values of 100-200+ Ω that are considered to be not stable.
 
Even for economic reasons I still do not believe in ditching a good earth for a non stable earth is good practice.

Hawk,

You know my opinions on domestic TT systems, and on extending PME equipotential zones.
In the case of PME and requiring a bonding cable either within your SWA cable, or separate, realistically i think if your sub-main run is going to be over 50 metres or so, it does then start to become uneconomical. We do have to draw the line somewhere... lol!!!
 

Reply to Am I missing something here? in the Australia area at ElectriciansForums.net

Similar Threads

Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
271
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
811
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
768
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
550

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock