Discuss Basic Testing Procedures in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Sintra

Staff member
Esteemed
Supporter
Reaction score
5,316
Safe isolation

The procedure for proving dead should be by use of a test lamp or two pole voltage detector as recommended in HSE Guidance Note GS38.
Non-contact voltage indicators (voltage sticks) and multi-meters should not be used. The test instrument should be proved to be working on a known live source or proprietary proving unit before and after use. All phases of the supply and the neutral should be tested and proved dead.


Test sequence and descriptions

The following tests are carried out with the Consumers main switch isolated


1. Extenal earth fault loop impedance
Reason: To establish that a good earth exists at the installation in order for the remaining tests to go ahead.

Method: Disconnect the main earthing conductor from the main earthing terminal. An earth fault loop impedance tester is connected at line and earth (main earthing conductor) at the supply side of the installation and a test performed. Reconnect the main earthing conductor. The result is Ze and recorded on the sheet. The prospective fault current is measured at the same time after the reconnection of the main earthing conductor.


2. Continuity of protective and bonding conductors
Reason: To check that all circuit protective conductors (green and yellow cables) are continuous and are present at every electrical accessory on the circuit. Also to check that the main earthing conductor and main bonding conductors are continuous and correctly connected.

Method 1: The line conductor is connected to the circuit protective conductor of the same circuit at the consumer unit and a measurement taken at ALL accesories on that circuit between line and c.p.c. The highest measurement obtained is recorded on the test report.
Test result is R1 + R2. The line conductor and neutral conductor are then connected and the above repeated to obtain R1 + Rn


Method 2 (used for main earth and main bonding conductors): A wandering lead is connected to one end of the conductor to be tested and a measurement taken between the other end of this lead and the other end of the conductor.
Test result is R2.
During this test polarity can be checked as well. The continuity of the neutral conductor can also be checked.


3. Continuity of ring final circuit conductors
Reason: This test ensures that all ring final circuits (sockets usually) are indeed a continuous ring with no interconnects or breaks within it.

Method: The line, neutral and earth conductors of the circuit are identified and a measurement from one end to the other end of each is taken. These results are r1, r2 and rn.
The incoming line conductor is then connected to the outgoing earth conductor and the outgoing line conductor is connected to the incoming earth conductor. A measurement is then taken at ALL socket outlets on the ring. The highest of which is recorded on the report.
This result is R1+R2 for that circuit. The above is then repeated using the neutral conductor instead of the earth conductor. This test provides R1+Rn which does not need to be recorded on the report but is essential to check the circuit correctly.


4. Insulation Resisitance
Reason: This test checks whether the insulation around a cable is still intact and has not broken down over time. It is a good indicator of the age of an installation.

Method: An insulation resistance tester is connected across line and neutral tails at the origin of the supply. 500V are then pumped down the conductors to see if any voltage leaks across from one conductor to the other. The same is then done for the line and earth and the earth and neutral conductors.

5. Polarity
Reason: To check that all accesories are correctly connected to line, neutral and earth and that all switches and circuit breakers are connected in the line conductor only.

Method: The method for this is the same as for continuity and is usually done at the same time by operating switches etc whilst conducting the test.


6. Earth electrode resistance
Reason: To make sure that any earth electrode used is of a sufficiently low impedance to allow the timely operation of the RCD protecting the installation.

Method: An earth fault loop impedance tester is connected between line and earth at the origin of the supply and a test performed. The result of which is considered the resistance of the electrode (Ra).


The following tests are carried out with the Consumers main switch energised

7. Live polarity test
Reason: To verify polarity of supply authorities system.

Method: An approved voltage indicator shall be used or test lamp to GS38. Using the approved voltage indicator, one probe shall be placed on the incoming neutral, and the other on the incoming line conductor, on the main breaker. The indicator should show it is live. One probe shall now be placed on the CPC and the other on the incoming line conductor. The indicator should show it is live. A test shall be preformed between CPC & incoming neutral. The indicator should show that it is not live.

8. Earth fault loop impedance
Reason: This test is done at the furthest point on a circuit in order to make sure the impedance of the earth path is not too high even at the furthest point so that sufficient current will flow under fault conditions to take out the circuit breaker protecting the circuit.


Method: An earth fault loop impedance tester is connected to line and earth at the furthest point on the circuit and the test performed.

9. RCD test
Reason: To make sure RCD's trip within the correct time


Method: An RCD tester is connected and a test at 1/2 times, 1 times and 5 times the trip current is performed on each side of the cycle and a time of trip obtained. Usually milli-seconds with the highest being recorded. The manual test button is then pressed.

10. Functional testing
Reason: To make sure all switches, isolators, MCB's etc. work as they should.


Method. Self explanatory.
 
Good post - Cheers

My only comments are that you have missed out live polarity using an approved voltage indicator. Strictly, live polarity should be the first test you carry out with the supply switched on.

Also, a reference to safe isolation should be on there.

I know, I'm a picky little b*****d !! :)
 
Last edited by a moderator:
Excellent post mate we should have a lot more of these as a refresher for the old boys and a great help to those just starting out.


Chris
 
Last edited by a moderator:
Hi,

Should also have mentioned that the earthing conductor is disconnected from the MET for the Ze measurement and subsequently re-connected to measure PFC.
 
Good post - Cheers

My only comments are that you have missed out live polarity using an approved voltage indicator. Strictly, live polarity should be the first test you carry out with the supply switched on.

Also, a reference to safe isolation should be on there.

I know, I'm a picky little b*****d !! :)

Thanks Steve good points all modified now.

Excellent post mate we should have a lot more of these as a refresher for the old boys and a great help to those just starting out.


Chris

Thanks acat

Hi,

Should also have mentioned that the earthing conductor is disconnected from the MET for the Ze measurement and subsequently re-connected to measure PFC.

Thanks for that Wayne now included.


If anyone else has a comment please feel free to add.
 
some good stuff on there. it would have made my course a lot easier with a site like this to look trough and saved a small fortune on books :( mind i would have only spent it on tools :)
 
Sintra some useful info there for people like myself currently studying the 2391, however i believe the first part could be mis-informative to people who may have interpretated it as i have. Ze (external earth fault loop impedance taken at the origin) is not a dead test as described. Granted all outgoing sides of the DB main breaker should be open (in OFF position). However it is a live test and therefore will not be done after you perform a safe isolation.
 
Sintra some useful info there for people like myself currently studying the 2391, however i believe the first part could be mis-informative to people who may have interpretated it as i have. Ze (external earth fault loop impedance taken at the origin) is not a dead test as described. Granted all outgoing sides of the DB main breaker should be open (in OFF position). However it is a live test and therefore will not be done after you perform a safe isolation.

Beg to differ here IMO the safe isolation must be done prior to the Ze test as you are removing the main earthing conductor to the installation. I stated that the Ze test had to be done with the supply switched off not that it was a dead test
 
Last edited:
The actual supply is not switched off, the installation past the main breaker is switched off granted but not the supply. Anyone just about to take the 2391 practical may be confused as books including GN3 and OSG use the CRIPLER method and this is the way i've been taught to test within my 2391 course;

Dead tests:

Continuity of circuit protective conductors
Ring final circuit conductor continuity
Insulation resistance testing
Polarity

Live Tests:

Loop impedance test external (Ze)
Earth fault loop impedances (Zs)
RCD testing
 
Have changed some of the terminology to try and make it clearer.
Thanks for your input.
 
No probs Sintra i knew what you meant but i think the way it is now is more clearer for the likes of myself who are new(ish) to the testing game and studying 2391. Wa hey my first receieved thanks! Well thank you Sintra! :) Cool bike btw...lol!
 
Last edited by a moderator:
The actual supply is not switched off, the installation past the main breaker is switched off granted but not the supply. Anyone just about to take the 2391 practical may be confused as books including GN3 and OSG use the CRIPLER method and this is the way i've been taught to test within my 2391 course;

Dead tests:

Continuity of circuit protective conductors
Ring final circuit conductor continuity
Insulation resistance testing
Polarity

Live Tests:

Loop impedance test external (Ze)
Earth fault loop impedances (Zs)
RCD testing

Hi Safetyfirst,

You are right to a degree.

The sequence you stated above applies to 'Initial Verification' only.

On a PIR, as you will do on your 2391 practical, there is no set sequence of testing, you can do them in any order that you like:)
 
Yes but i personally believe thats the most logical way the cripler method anyhow, each to there own but i personally would carry testing out that way the majority of the time, PIR or no PIR.
 
That's all very well, but on the 2391 time is short - and in the real world, time is money.

Consider this:

Whilst performing safe isolation of the installation you have your voltage tester in your hand -

so you might as well perform the same tests on the incomming side of the main switch and confirm

supply polarity.

Then, as you have the cover off the board anyway, disconnect the earthing conductor and measure

Ze

Re-connect the earthing conductor and measure your PFC

These three tests have took you 5 minutes and you haven't moved.

Then onto your sequence of tests - continuity, ring final, IR, Polarity

Now, really speaking, you should put the cover back on the board before re-energising. (HSE and all

that) - but that's okay, because your finished in there and shouldn't have to take it off again:D

On with the remaining live tests - Zs, RCD and the functionals.

Job done.

Your not doing anything wrong - it's just more efficient:)
 
In the 2391 the 1st thing you do is safe isolation anyhow so you can't do a live test first as an isolator feeds your board (at least mine did) but generally at an occupied building of course the way you said is the choice a lot of sparks would command to. Though i believe however you do them you still take the same amount of time doing the individual tests any which way as you don't go quicker with individual tests doing them in different orders.
Anyways its each to there own, we all have our own way of doing things. My main worry was for anyone reading this article as it was before being edited that are about to sit there 2391 practical, not for those who test day in day out, they are confident and can do it however they feel at ease to.
 
In the 2391 the 1st thing you do is safe isolation anyhow so you can't do a live test first as an isolator feeds your board (at least mine did) but generally at an occupied building of course the way you said is the choice a lot of sparks would command to. Though i believe however you do them you still take the same amount of time doing the individual tests any which way as you don't go quicker with individual tests doing them in different orders.
Anyways its each to there own, we all have our own way of doing things. My main worry was for anyone reading this article as it was before being edited that are about to sit there 2391 practical, not for those who test day in day out, they are confident and can do it however they feel at ease to.

The correct way (as you are supposed to be isolating a live supply) is for the isolator feeding your board to be closed.

You isolate the installation by opening the three phase main switch then proving dead.
This doesn't have the same effect if the 'main isolator' to the 2391 board is already open.:)

My examiner actually told me to go across the incommers with the same 'ten-point' test that I performed for safe isolation - this, of course, proved supply polarity.

He then closed the 'main isolator' and locked it off.

The time saved is in the efficiency of testing - for instance: no point in having to take the cover off the board again to do tests you could have done earlier.
 
The correct way (as you are supposed to be isolating a live supply) is for the isolator feeding your board to be closed.

You isolate the installation by opening the three phase main switch then proving dead.
This doesn't have the same effect if the 'main isolator' to the 2391 board is already open.:)

My examiner actually told me to go across the incommers with the same 'ten-point' test that I performed for safe isolation - this, of course, proved supply polarity.

He then closed the 'main isolator' and locked it off.

The time saved is in the efficiency of testing - for instance: no point in having to take the cover off the board again to do tests you could have done earlier.

I've just read my post and realised the stupidity in what I have said:eek: - So ignore me and do what you think is best.

Either way is fine.:)
 
No bother at all Wayne its good that we share all our own ways of doing things it can only be of benefit. I am currently on a 2391 course so i can only speak of how i've been learning and having done the practical already my expirience so far.
 
Thank you for explaning that helps alot. is there any chance of explaning what the readings mean eg. greater than 1M ohm, also the reading for insulation resistance. as this confuses me and dont understand a good reading from a bad one. cheers
 
Hi Safety First,

I think I saw the CRIPPLER way of remebering the tests from either Chris Kitcher or Dave Potter. There is a second P which reminds polarity Live test as well as the polarity dead test.
Great way of remembering, thanks,

Best wishes,

Rex
 
Safe isolation



The procedure for proving dead should be by use of a test lamp or two pole voltage detector as recommended in HSE Guidance Note GS38.
Non-contact voltage indicators (voltage sticks) and multi-meters should not be used. The test instrument should be proved to be working on a known live source or proprietary proving unit before and after use. All phases of the supply and the neutral should be tested and proved dead.




Test sequence and descriptions



The following tests are carried out with the Consumers main switch isolated



1. Extenal earth fault loop impedance


Reason: To establish that a good earth exists at the installation in order for the remaining tests to go ahead.


Method: Disconnect the main earthing conductor from the main earthing terminal. An earth fault loop impedance tester is connected at line and earth (main earthing conductor) at the supply side of the installation and a test performed. Reconnect the main earthing conductor. The result is Ze and recorded on the sheet. The prospective fault current is measured at the same time after the reconnection of the main earthing conductor.


2. Continuity of protective and bonding conductors


Reason: To check that all circuit protective conductors (green and yellow cables) are continuous and are present at every electrical accessory on the circuit. Also to check that the main earthing conductor and main bonding conductors are continuous and correctly connected.


Method 1: The line conductor is connected to the circuit protective conductor of the same circuit at the consumer unit and a measurement taken at ALL accesories on that circuit between line and c.p.c. The highest measurement obtained is recorded on the test report.
Test result is R1 + R2. The line conductor and neutral conductor are then connected and the above repeated to obtain R1 + Rn


Method 2 (used for main earth and main bonding conductors): A wandering lead is connected to one end of the conductor to be tested and a measurement taken between the other end of this lead and the other end of the conductor.
Test result is R2.
During this test polarity can be checked as well. The continuity of the neutral conductor can also be checked.


3. Continuity of ring final circuit conductors


Reason: This test ensures that all ring final circuits (sockets usually) are indeed a continuous ring with no interconnects or breaks within it.

Method: The line, neutral and earth conductors of the circuit are identified and a measurement from one end to the other end of each is taken. These results are r1, r2 and rn.
The incoming line conductor is then connected to the outgoing earth conductor and the outgoing line conductor is connected to the incoming earth conductor. A measurement is then taken at ALL socket outlets on the ring. The highest of which is recorded on the report.
This result is R1+R2 for that circuit. The above is then repeated using the neutral conductor instead of the earth conductor. This test provides R1+Rn which does not need to be recorded on the report but is essential to check the circuit correctly.


4. Insulation Resisitance


Reason: This test checks whether the insulation around a cable is still intact and has not broken down over time. It is a good indicator of the age of an installation.

Method: An insulation resistance tester is connected across line and neutral tails at the origin of the supply. 500V are then pumped down the conductors to see if any voltage leaks across from one conductor to the other. The same is then done for the line and earth and the earth and neutral conductors.


5. Polarity


Reason: To check that all accesories are correctly connected to line, neutral and earth and that all switches and circuit breakers are connected in the line conductor only.

Method: The method for this is the same as for continuity and is usually done at the same time by operating switches etc whilst conducting the test.


6. Earth electrode resistance


Reason: To make sure that any earth electrode used is of a sufficiently low impedance to allow the timely operation of the RCD protecting the installation.

Method: An earth fault loop impedance tester is connected between line and earth at the origin of the supply and a test performed. The result of which is considered the resistance of the electrode (Ra).



The following tests are carried out with the Consumers main switch energised




7. Live polarity test


Reason: To verify polarity of supply authorities system.


Method: An approved voltage indicator shall be used or test lamp to GS38. Using the approved voltage indicator, one probe shall be placed on the incoming neutral, and the other on the incoming line conductor, on the main breaker. The indicator should show it is live. One probe shall now be placed on the CPC and the other on the incoming line conductor. The indicator should show it is live. A test shall be preformed between CPC & incoming neutral. The indicator should show that it is not live.


8. Earth fault loop impedance


Reason: This test is done at the furthest point on a circuit in order to make sure the impedance of the earth path is not too high even at the furthest point so that sufficient current will flow under fault conditions to take out the circuit breaker protecting the circuit.

Method: An earth fault loop impedance tester is connected to line and earth at the furthest point on the circuit and the test performed.


9. RCD test


Reason: To make sure RCD's trip within the correct time

Method: An RCD tester is connected and a test at 1/2 times, 1 times and 5 times the trip current is performed and a time of trip obtained. Usually milli-seconds. The test button is then pressed.


10. Functional testing

Reason: To make sure all switches, isolators, MCB's etc. work as they should.

Method. Self explanatory.
i have just started to test and I would like you to tell me if you could how to fill in the test sheets that I have to fill in Q.1.In the circuit details for the installation, there is a column 'Reference Method', what is this?
 
i have just started to test and I would like you to tell me if you could how to fill in the test sheets that I have to fill in Q.1.In the circuit details for the installation, there is a column 'Reference Method', what is this?


It refers to the installation method of the cable/wiring system and it's associated reference method.

You'll find them on P261 in BS 7671.
 
PSCC Prospective short circuit current measured between L & N

PEFC Prospective earth fault current measured between L & E

PFC Prospective fault current the highest reading from the 2 tests above.

The results of this test allow you to calculate the size of the main earthing conductor and to select the type of overcurrent device to be used.
 
Thanks for that mate,this is all good info,when I am out on site I dont get the chance to ask these kind of questions all everybody wants todo is get the results down on the sheets and fill the rest of them out at home. I have another,we are working in a large factory,we can not get to the main dis board that supplys all the sub boards but on the sheet that I was given there is a section for parameters of supply with Zs one of the box to be filled in do I take this reading at all my sub boards as well as the main board.
 
Hi Safety First,

I think I saw the CRIPPLER way of remebering the tests from either Chris Kitcher or Dave Potter. There is a second P which reminds polarity Live test as well as the polarity dead test.
Great way of remembering, thanks,

Best wishes,

Rex

Your right, the second P is Live polarity which is done on the supply side of the isolator before turning it ON!!
Regards D.P
 
Thanks for that mate,this is all good info,when I am out on site I dont get the chance to ask these kind of questions all everybody wants todo is get the results down on the sheets and fill the rest of them out at home. I have another,we are working in a large factory,we can not get to the main dis board that supplys all the sub boards but on the sheet that I was given there is a section for parameters of supply with Zs one of the box to be filled in do I take this reading at all my sub boards as well as the main board.


I think you mean Ze and there is only one Ze on any installation and that is where the suppliers cables end and the installation cables begin
 
PSCC Prospective short circuit current measured between L & N

PEFC Prospective earth fault current measured between L & E

PFC Prospective fault current the highest reading from the 2 tests above.

The results of this test allow you to calculate the size of the main earthing conductor and to select the type of overcurrent device to be used.
at this stage would the earth and protective device be in place
 
at this stage would the earth and protective device be in place

Yes at this stage the main earthing conductor will have been reconnected back into the MET the main switch will be in the open (off) position. Test carried out at incoming side of main switch.
 
so Ze is at the main incomer and Zs can be measured at every other fitting,and what does this tell you,the Zs that is?

The Zs figure obtained will let you know whether a protective device will operate in the required time under fault conditions.
 
Ze is the test done at the main incomer, with the main earth dis-connected from MAIN EARTH TERMINAL with the mains still on is that right.My other question is , is it right saying that I can measure Zs at every fitting
 
Ze is the test done at the main incomer, with the main earth dis-connected from MAIN EARTH TERMINAL with the mains still on is that right.My other question is , is it right saying that I can measure Zs at every fitting

Zs only needs to be tested at the last point on every circuit as you will have previously tested R1+R2 at every accessory prior to energising.
 
Yes at this stage the main earthing conductor will have been reconnected back into the MET the main switch will be in the open (off) position. Test carried out at incoming side of main switch.
what do I do if I can not turn off the power to carry out this test and what happens if I do the test with the power on in the building.
 
so there must be a table of numbers that the result must be under to be ok

Yes there is a table in bs7671

Thanks ,so the test is for the circuit and not for every fitting

Correct

what do I do if I can not turn off the power to carry out this test and what happens if I do the test with the power on in the building.


The installation NEEDS to be isolated for Ze as main earthing conductor is disconnected. If you can not isolate then this needs to be noted as a limitation but only on a PIR.

As for PFC this could be done with the installation live as all earthing and bonding will be in place.
 
Get yourself a copy of Guidance Note 3, and have a good read.;)
I like talking to you guys about these things ,its much more fun than reading a book;) but I will have to get myself guidance note 3 as the one I have is out of date I think, it is yellow in colour .Do you know any where I can get GN3 and BS7671 a bit cheaper :confused:
 
Yes there is a table in bs7671



Correct




The installation NEEDS to be isolated for Ze as main earthing conductor is disconnected. If you can not isolate then this needs to be noted as a limitation but only on a PIR.

As for PFC this could be done with the installation live as all earthing and bonding will be in place.
I ll tell you what I'm doing, I am installing new circuits and breaking into exsisting rings ,when I install a new circuit I issue a New installation cert and when I tamper with a ring I issue a Minor works cert,but the thing is I am doing this in a very large store and the power can not be turned off so I can not do my Ze so I think I put this down as a limatation and just do PFC or if I can get my hands on previous test sheets issued can I use them?
 
Beg to differ here IMO the safe isolation must be done prior to the Ze test as you are removing the main earthing conductor to the installation. I stated that the Ze test had to be done with the supply switched off not that it was a dead test
The actual supply is not switched off, the installation past the main breaker is switched off granted but not the supply. Anyone just about to take the 2391 practical may be confused as books including GN3 and OSG use the CRIPLER method and this is the way i've been taught to test within my 2391 course;

Dead tests:

Continuity of circuit protective conductors
Ring final circuit conductor continuity
Insulation resistance testing
Polarity
 
The actual supply is not switched off, the installation past the main breaker is switched off granted but not the supply. Anyone just about to take the 2391 practical may be confused as books including GN3 and OSG use the CRIPLER method and this is the way i've been taught to test within my 2391 course;

Dead tests:

Continuity of circuit protective conductors
Ring final circuit conductor continuity
Insulation resistance testing
Polarity

Except that you don't have to follow any particular order in the 2391, as it's a PIR that you are completing, not an Initial Verification.

You can basically test in the order that suits you best.:)
 
Dead tests:

C
ontinuity of circuit protective conductors
Ring final circuit conductor continuity
Insulation resistance testing
Polarity

Live Tests:

Loop impedance test external (Ze)
Earth fault loop impedances (Zs)
RCD testing

Just a note I was shown this and it really helped. It's vey similar.

C.R.I.P.P.E.L.D (main point to notice E & L are the wrong way round)

Continuity of C.P.C's inc main and supplementary bonding conductors

Ring final continuity

Insulation resistance

Polarity (dead)
>Earth electrode test if a TT system
Polarity (Live) inc phase rotation at origin of the installation

Externals Ze inc PFC at origin

Loop impedance Zs inc phase rotation and PFC both taken at the load

Devices inc RCD/RCBO and fuctional testing of both On-load and Off-load switching devices
 
Hi BillyBoBob,

Thats a great comment probably originating from Chris Kitchen or a guy called Dave Potter.

Good stuff, good info.

Best wishes,

Rex
 
Hi BillyBoBob,

Thats a great comment probably originating from Chris Kitchen or a guy called Dave Potter.
Good stuff, good info.
Best wishes,
Rex

The Dave Potter way is:

Continuity of protective conductors including bonding.
Ring continuity test
Insulation resistance tests
Polarity dead (normally already confirmed with C & R)
Polarity live (confirmation of supply polarity at live side of main switch before turning on)
Loop impedance tests, Ze or earth electrode followed by Zs readings.
Earth fault current and short circuit fault current (PFC)
Rcd and other functional tests.

The greens are dead tests and the reds are live.
 
Last edited by a moderator:
good stuff mate its handy havin it online instead ov rummaging through books could u put the range on the tester like megaohms or that used for each sequence of tests up as well?
 

Reply to Basic Testing Procedures in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
721
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
936
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
716
Hi There is a lighting circuit fault in a property with the downstairs lighting circuit. I have tested the voltage and there is 230v on both...
Replies
10
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
383

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock