- Reaction score
- 2,089
As long as you can guarantee that it is TN-S and isn’t taken from a TN-C network.Sorry, I forgot to mention is a TN-S earthing system.
Discuss Bonding RSJ question. in the Commercial Electrical Advice area at ElectriciansForums.net
As long as you can guarantee that it is TN-S and isn’t taken from a TN-C network.Sorry, I forgot to mention is a TN-S earthing system.
Yeah definitely TN-S. We have two separate private LV transformers, as the site is spilt into two substations.As long as you can guarantee that it is TN-S and isn’t taken from a TN-C network.
Could I bond the nearest RSJ of the storage building to the metal container which is 40 metres away, as the RSJ structure is bonded near the sub main? This would save 70 metres of cable.
My apologies, I was not really thinking of what the OP actually asked about.Correct.I always bond the metalwork to the CPC .I understood from the OP that he wondered about running a separate bonding cable to the metallic structure.
Very unlikey to introduce an outside potential into the system.Is the metal container itself not an extraneous conductive part ?
Not neccessarily. Bonding it may mean you are actually introducing a fault-path. We test to ascertain whether it is extraneous and whether it is likely to introduce an outside potential into the system. If the test proves otherwise, we do not bond.But if the metalwork is not bonded to the CPC system they risk being at differing potentials, say should the CPC be on a faulted-PEN segment of the supply network.
So while all structural metal work might be at the same potential, any class I equipment may be at another. So bonding is still needed.