Still confused with order
Ring Final returned

0 and 5.5 and-- 5 MegOhms ...
L-E, ..L-N and N-E...?
If N-E have not been isolated L&N swapped ..
(or is it just LE,LN&NE sequence off)
 
Zero was the reading for Ring Final between Line/Earth. 5.5MOhms was the reading for Line/Neutral. 5 MOhms N-E. c.350 MOhms or thereabouts for the other circuits. This was a soft test (250V) - and yes I know what 7671 says...but disconnecting all loads was not practical at the time. I knew the CU would have to be replaced and that the circuitry was shot due to the burnt N bar so I hoped a soft test would suffice knowing a new CU would then have to be fully tested with 500V DC.
 
If you haven't disconnected all loads how have you got a L/N reading and differing L/E and N/E readings. You should have used 500v it would have done no harm.
 
But the zero ohm reading shows that there is either a fault or something is still plugged in. Without unplugging everything how will you know which it is? The test result is meaningless.
 
But the zero ohm reading shows that there is either a fault or something is still plugged in. Without unplugging everything how will you know which it is? The test result is meaningless.
Not entirely meaningless. Just not the value you would have hoped for. If you can get an acceptable IR value with appliances connected, you know it's going to be OK without them. Obviously, if the IR's too low then further investigation required.
 
Not entirely meaningless. Just not the value you would have hoped for. If you can get an acceptable IR value with appliances connected, you know it's going to be OK without them. Obviously, if the IR's too low then further investigation required.

But he hasn't got acceptable values.
 
The burnt neutral looks to me to be on the lighting circuit..must have been loose.
I would agree that all would need to be unplugged for IR test and the imm htrs would need to be switched off if double pole switch or disconnected if only single pole kit eg some spurs maybe for washing machine?

Wonder what live to earth on ohm scale showed?
 

Reply to Burnt Main Downstream Neutral in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
634
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K
I'm having an extension built and the builder leading the project has said that the electrician will be over in about 4-6 weeks to start his works...
Replies
4
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock