Discuss calculating csa of earthing conductor with BS1361 fuse in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

K

knasher

Maybe I'm overlooking the obvious but how would you calculate the min. csa of an earthing conductor of say a tn-s system when there is no time/current graph for a 1361 fuse in the BGB? Do you just obtain If from Uo/Ze and then use this in the adiabetic equation. Ta
 
Look in a copy of the BRB, or obtain the information from the fuse manufacturer.
You would not be able to conduct the adiabatic equation without this information, as you require a value for 't'.
 
From the BGB -1361 spec for cartridge fuses for ac in domestic or similar premises replace by BS 88-3: and withdrawn 1/3/2010.
 
Last edited:
Hi rushton, are you saying BS88-3 is now the replacement for the 1361 fuse? or that BS88-3 replaced the BS1361 fuse but now not deemed as a suitable replacement? Just trying to get this clear in my head please
 
So, to satisfy an old man's confusion, if the installation has a BS1361 fuse and it's now been turned into a BS88 type 3 by the magic of the BGB, do you use the info for BS88 fuses in the tables?
 
Yes as understand it the spec for BS 1361 has been removed and replaced by BS88 -3: 2010 . It's on page 277 of the green book. and the book will only list the current standards. Appendix 1 on the top of the page gives the criteria.
 
So, to satisfy an old man's confusion, if the installation has a BS1361 fuse and it's now been turned into a BS88 type 3 by the magic of the BGB, do you use the info for BS88 fuses in the tables?

I would still use the old specs its as clear as mud.
 

Reply to calculating csa of earthing conductor with BS1361 fuse in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
821
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
481
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hi all, After months of waiting, the fused neutral cut-out at my parents house has been replaced but I am concerned about the main earth. I...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock