Discuss Can SWA be run in the same metal trunking as singles? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
7
I have checked the regs and can't find anything to say this can't be done. Although I'm worried about cable movement in the case of short circuit damaging singles in the trunking
 
You are fine with that. Of course usual good installation practice needed, but SWA won't move that much unless you are looking at really high energy faults, and more so for sets of AWA singles making up a really high current 3P set.
 
do you mean complete SWA? with the armour? or glanded into the trunking, and the inner cores within trunking?


"Singles" cable has a slightly tougher insulation than something like the inner basic insulation of t&e... Can take a bit of rough treatment no problem.
 
do you mean complete SWA? with the armour? or glanded into the trunking, and the inner cores within trunking?


"Singles" cable has a slightly tougher insulation than something like the inner basic insulation of t&e... Can take a bit of rough treatment no problem.
Yes, complete SWA. We have installed trunking for an installation with 2.5mm, 4mm and 6 mm singles.

We've now been asked to run a 10mm swa for a supply to a new dB and a lot of the trunking is along this route.
 
You are fine with that. Of course usual good installation practice needed, but SWA won't move that much unless you are looking at really high energy faults, and more so for sets of AWA singles making up a really high current 3P set.
Thanks for the reply, the fault current will be 10Ka (theoretical maximum at origin) for the swa as we are right by the site intake.

We have at a maximum 10 single conductors (2.5, 4 and 6mm) at the busiest points in the trunking. All single phase including SWA. I suggested it to the clerk of works and he said absolutely not allowed.

I disagreed and have since been searching high and low for a regulation that prohibits this.
 
Possible future plans require the space in the trunking?

Whats wrong with running the SWA alongside the trunking? Its mechanically protected already. Or, as i said earlier, gland it in and run it through without the armour.
 
Possible future plans require the space in the trunking?

Whats wrong with running the SWA alongside the trunking? Its mechanically protected already. Or, as i said earlier, gland it in and run it through without the armour.
For some reason he doesn't like it clipped direct. Unfortunately it's at the beginning of a 70m run so glanding into trunk is not an option. Clerk also refuses to allow us to clip direct.

I was only really looking for 2nd opinions on this matter as he has highlighted my suggestion to run in the trunking to the client and has questioned my competency
 
Clerk of works will have the final say. I wouldn't waste time arguing with him and would instead ask how he'd like it to be routed - limitations with regard to support might actually result in him having a change of mind. Do whatever he wants and invoice accordingly.
He has refused to make suggestions on how to actually do it as he states 'that's not his job'.

I wanted to triple check that this is in fact acceptable as he has reported my suggestion to his superiors.

Thank you for taking the time to reply!
 
Just one other thought, how would the SWA armour be connected?
I can see both sides of this, whilst I also cannot see a reason why it is Non compliant, it will take up more room in the trunking than the equivalent in singles?!
Personally I would if in trunking be using singles for ease and space saving.
When they ask you back again at a later date to install more circuits you will either be wishing for more space or thinking, glad I left some spare capacity in that trunking!
Just my 2pennies worth.
Sy
 
He has refused to make suggestions on how to actually do it as he states 'that's not his job'.

You've suggested two methods of installation which he has rejected and neither for any regulatory reason and this is something I'd make very clear to him - I'd contend that it's very much his job to decide how the cable is run, unless the client provides a spec.
 
If I had more than one run of SWA I would be tempted to put up cable tray and clip to that. If the tray is vertical (parallel to wall, supported off by short lengths of strut, for example) then you need the occasional metal tie for fire support in addition to regular ties of any other sort.

If the SWA sits on top of a horizontal tray (so it can't fall if clips melt), for example supported on cantilever arms, or suspended from a roof, then standard cable ties are OK. Personally I would always use the black UV-tolerant type even indoors as sometimes it will get sunlight from windows, etc, and it saves me keeping multiple bags.

However, I also get the feeling this person is being difficult for no obvious reason. I would be tempted to present your suggestions for alternatives in writing (e.g. email) and make sure they respond also in writing just to cover yourself.

Incidentally, when you said trunking I was thinking of the metal stuff, 50x50mm upwards, not plastic. Can you confirm the type?
 
If I had more than one run of SWA I would be tempted to put up cable tray and clip to that. If the tray is vertical (parallel to wall, supported off by short lengths of strut, for example) then you need the occasional metal tie for fire support in addition to regular ties of any other sort.

If the SWA sits on top of a horizontal tray (so it can't fall if clips melt), for example supported on cantilever arms, or suspended from a roof, then standard cable ties are OK. Personally I would always use the black UV-tolerant type even indoors as sometimes it will get sunlight from windows, etc, and it saves me keeping multiple bags.

However, I also get the feeling this person is being difficult for no obvious reason. I would be tempted to present your suggestions for alternatives in writing (e.g. email) and make sure they respond also in writing just to cover yourself.

Incidentally, when you said trunking I was thinking of the metal stuff, 50x50mm upwards, not plastic. Can you confirm the type?
100x100 metal trunking, only 1 SWA to run. After SWA goes in with the other circuits.we are at approx 10% capacity
 
You’re still going to have to gland the swa into the trunking somehow, even leaving armour on.

I have to agree that there is no valid reason that it can’t be clipped surface. It’s perfectly ok in every other building.
 
You’re still going to have to gland the swa into the trunking somehow, even leaving armour on.

I have to agree that there is no valid reason that it can’t be clipped surface. It’s perfectly ok in every other building.
The beginning of the swa run is internal (where the trunking is), then runs externally to an outbuilding to upgrade a feed there.

There seems to be no logical reason to a lot of his requests
 
Just one other thought, how would the SWA armour be connected?
I can see both sides of this, whilst I also cannot see a reason why it is Non compliant, it will take up more room in the trunking than the equivalent in singles?!
Personally I would if in trunking be using singles for ease and space saving.
When they ask you back again at a later date to install more circuits you will either be wishing for more space or thinking, glad I left some spare capacity in that trunking!
Just my 2pennies worth.
Sy
Entry and exit to trunking will be 32mm metal compression gland, there is then a 30m run beyond trunking to the next dB that the swa continues to.

100x100 trunking with, at a maximum, 10 singles conductors (2.5, 4 and 6mm) so trunking will be approx 10% capacity with SWA installed
 
Ensure when you ask the question which regulation if does not comply with you have a copy available to ask them to point it out, too easy to say I just know it does not comply.
 
You keep saying its only going to be 10% full with the swa in.... like its a reasoning to do it the way he's suggesting....but if that's the case, there should be some paperwork with the design saying something like... "have oversized the trunking to accommodate the SWA cable"
A conscious decision to not do it the way its done everywhere else.
100mm square does seem oversized for what you say is going in.... which does suggest they think there will be more added in the future.


OK, it will save some time, not having to separately clip the swa along the route, and maybe its an aesthetic decision... One square metal trunking might look neat against the wall, but not a black cable with tray, or cleats alongside.


"doesn't comply" is an absolute cop out, but one that is easily debunked if you've got the book there.
 
You keep saying its only going to be 10% full with the swa in.... like its a reasoning to do it the way he's suggesting....but if that's the case, there should be some paperwork with the design saying something like... "have oversized the trunking to accommodate the SWA cable"
A conscious decision to not do it the way its done everywhere else.
100mm square does seem oversized for what you say is going in.... which does suggest they think there will be more added in the future.


OK, it will save some time, not having to separately clip the swa along the route, and maybe its an aesthetic decision... One square metal trunking might look neat against the wall, but not a black cable with tray, or cleats alongside.


"doesn't comply" is an absolute cop out, but one that is easily debunked if you've got the book there.
He hasn't suggested a way at all, says that's our job. Drawings only specify location of accessories and what circuit.

He has said no to clipped direct because 'it will look ---- ' his words. Also a no to SWA in the trunking with singles. Time to email a superior imo
 
Yes, complete SWA. We have installed trunking for an installation with 2.5mm, 4mm and 6 mm singles.

We've now been asked to run a 10mm swa for a supply to a new dB and a lot of the trunking is along this route.
Reading the second sentence it would tend to indicate this is a change to the specification, do you have a COW Site Instruction to carry out this extra works, if so get them to specify how they wish it to be done, just don't do it until they instruct you, perfectly legitimate not to carry out the work until you are satisfied with the instruction as it's an extra, have you priced it or is it on day works at your enhanced rate?
 
Aesthetics for clipped direct, and just says swa can't be run in the same trunking as singles so I can only assume he means that regs prohibit it.
If it is aesthetics they are complaining about then it is unlikely cable tray will pass muster. However, I have often seen tray near the ceiling in places and most folks just don't notice it.

The only regulation or instruction that I can think of that might make SWA in 100x100 trunking an issue is bend radius if it has to enter/exit through the side. 10mm 4C SWA is about 20mm or so diameter, so the bend radius would normally be about 8 times that (check manufacturer's specifications here) and so you are looking at 160mm radius, so a 90 deg bend won't fit in 100mm trunking.

Taking it out end caps so practically no bend, etc, is perfectly fine, and as you suggested compression glands would serve well to keep things in place and preserve a decent IP rating where a 25mm grommet might not.

Stripping a long length of SWA to have the inner cores (probably kept in the inner insulating sheath) in the trunking is just not sane or practical to do. You could use a SWA gland through the trunking to an adaptable box inside, and there use some crimps or similar to connect the 10mm to some 10mm singles for the run, etc, plus a copper CPC from the banjos or earthing nuts just to be sure of armour earth integrity, but it means added joints which usually you want to avoid. Would it only be needed at one end, if this trunking goes direct to some main DB?

Imo this is something for the mep to deal with and is above my role
Indeed, but put down you ideas and suggestions to your superior in an email or so so they have a solid case to take up with the COW to get a decision.
 
I've been following the wrong thing here...



You say the COW doesn't want it clipped direct, but he also doesn't want it run in the trunking??


How the hell does he want you to get it from A to B then? Some of that magic wireless power?

A second, empty trunking, just to hide the swa in?

A different route so its not seen?
 
Reading the second sentence it would tend to indicate this is a change to the specification, do you have a COW Site Instruction to carry out this extra works, if so get them to specify how they wish it to be done, just don't do it until they instruct you, perfectly legitimate not to carry out the work until you are satisfied with the instruction as it's an extra, have you priced it or is it on day works at your enhanced rate?

I've been following the wrong thing here...



You say the COW doesn't want it clipped direct, but he also doesn't want it run in the trunking??


How the hell does he want you to get it from A to B then? Some of that magic wireless power?

A second, empty trunking, just to hide the swa in?

A different route so its not seen?
I honestly don't know, the area it's run in is a welders workshops and a carpenters workshop, with 4 meter tall ceilings with trunking at 3.7m and the ability to clip direct above or below trunking. These aren't aesthetically pleasing rooms as you can imagine.



Very tempted to walk away right now it's absolutely ridiculous
 
Just give him in writing an estimate of how much it will cost to hide all the SWA to his satisfaction and copy it to the client, I think there would be some very embarrassed face's at the next project meeting.

Thinking further, 4M ceiling with the trunking at 3.7M which means working off MWEP or ladders, has the Health and Safety Co-ordinator been involved in this? their main function after all is the Safety of the workforce, easier to do if they do not have to leave the ground, is it possible to run the trunking around the walls?
 
Just give him in writing an estimate of how much it will cost to hide all the SWA to his satisfaction and copy it to the client, I think there would be some very embarrassed face's at the next project meeting.

Thinking further, 4M ceiling with the trunking at 3.7M which means working off MWEP or ladders, has the Health and Safety Co-ordinator been involved in this? their main function after all is the Safety of the workforce, easier to do if they do not have to leave the ground, is it possible to run the trunking around the walls?
We have a mobile tower which is plenty safe enough. It's been decided that we run 50mm tray below the trunking which is fine. Leave the bosses to sort out variations from scope
 
Just a vagary to throw into the pot when they are being awkward.

The most common accidents on site's are falls from height, if the work can be done at low level that is preferable than working off a tower that you have to access probably without a harness and up a ladder, unless it's a professional tower with internal access, kick boards at all levels and double rails, getting your tools and equipment to the top level also has to have consideration, not in a bucket pulled up on a rope, or worse carried up by you whilst climbing the ladder, who supplies the access equipment, if it's the site these things if relevant should be brought to the attention of the COW for them to sort out.
 
I would add that with 50mm trunking you need to be aware of bend radius of the SWA if the run is not straight. You might need to use a pair of 45 deg bends, etc, to get something sane. Also some suppliers have a very "square" 90 deg bend and others (like Unitrunk) have a bit more curve allowed.
 
I would add that with 50mm trunking you need to be aware of bend radius of the SWA if the run is not straight. You might need to use a pair of 45 deg bends, etc, to get something sane. Also some suppliers have a very "square" 90 deg bend and others (like Unitrunk) have a bit more curve allowed.
We're fabricating ourselves due to lack of access to materials. I believe 4 core 10mm has a ten fold diameter for bend radius so definitely need to be careful we.dont fall foul of that
 
We're fabricating ourselves due to lack of access to materials.
WTF???
I believe 4 core 10mm has a ten fold diameter for bend radius so definitely need to be careful we.dont fall foul of that
If you have some cable tray you ought to be able to make a gradual 90-deg bend by cutting V-shaped sections out and bending it in the a fan-shape. You will need some short links to join up the inner edges that you cut away to give it some strength though.
 
WTF???

If you have some cable tray you ought to be able to make a gradual 90-deg bend by cutting V-shaped sections out and bending it in the a fan-shape. You will need some short links to join up the inner edges that you cut away to give it some strength though.
We're abroad and it takes a couple of weeks and a lot of money to get anything here, materials were ordered by the office.
 
We're abroad and it takes a couple of weeks and a lot of money to get anything here
That's something that strikes me watching some of those North American series (Ice Road Truckers, Wikd Akaska, and the like. We're so used to just popping to the wholesalers to get common stuff from stock, or next day, or withing a few days if it's a special order. And planning on the basis that if we forget something, it's no big problem. Not just electrical, but for other stuff - e.g. I know I can pop round and pick up a bag of cement if I run out.
The idea that we have to accurately work out our materials a year in advance, have them delivered during a short window, and if we get it wrong then we're screwed is ... quite a mindset shift.
 
It's all to do with land area, if you look at any house in rural France, which is vast in comparison to the UK, you will see that nearly every house has a trailer sitting somewhere in the property, this is due to obviously to pick up supplies, but also due to the vast amount that companies charge for delivery.
 
It's all to do with land area, if you look at any house in rural France, which is vast in comparison to the UK, you will see that nearly every house has a trailer sitting somewhere in the property, this is due to obviously to pick up supplies, but also due to the vast amount that companies charge for delivery.

Same applied here in NI and probably much of the UK.

Prior to online shopping ushering in the era of home delivery everything had to be collected. A builder's supplier may have delivered, but only if the order was sizeable and if you weren't near to them a not inconsiderable sum may have been involved.

Growing up I don't remember anything being delivered other than heating oil, with all other goods being collected by car or trailer. All seems a bit mad now considering the tiny scale of NI.
 
Wicks in the UK have deliver free for anything on orders over £100.00 in Kent, that is not a lot a large order now days.

Most places now offer delivery at reasonable cost, with modest minimum order for free delivery.

This only became available in recent years as a response to online options that had eaten into margins.

I know a guy who lives on a Welsh mountainside and doesn't drive. His life was revolutionised in a short space of time around 10 years ago. Previously everything involved planning, favours and effort, whereas now even his groceries arrive from 30 miles away with his only effort being to lug them the last couple of miles up a rough track. Not sure how he'd feel about carrying drums of armoured cable up there 😁
 

Reply to Can SWA be run in the same metal trunking as singles? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Is anyone aware of any galv trunking that is smaller than 50x50. I'm drawing a blank online. I've taken over a job that's used 16mm twin and earth...
Replies
12
Views
857
Hi, Posted here as I'm not an electrician, not because it relates to anything I'm considering "Doing Myself". My late parent's house is supplied...
Replies
5
Views
378
I was working with some odd singles today from Batt Cables, they seemed to have a plastic like braid between the insulation and the copper, almost...
Replies
11
Views
584
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
604
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
802

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock