Why is it that recently people seem to find using the SWA armour as bad practice or unacceptable. Seems to be serveral posts each week asking if its ok to do.
If running a cable outside, then IMO it is bad practice to use steel armouring as CPC. I have seen numerous times what happens to the armour when the sheath of the cable is damaged, and water starts to ingress. The amouring rots away.
However if you believe that there is no chance of the cable being damaged, or of water ingressing then go for it.
Lenny that is brilliant. I've been looking for something like this for ages, where did you get it.
Check out www.earthingnuts.co.uk
Lenny that is brilliant. I've been looking for something like this for ages, where did you get it.
In reply to Amp David, I think people who don't really know how to make glans off are the ones against it. Yes it's good practice to run a seperate earth but it's not always practical.
cheers, Ron
I think it's poor practice not to use the armour as the cpc when it is adequate to be used as such.
i've been trying to clear this up(for myself)
there is no reason not to parallel the armour and separate cpc is there?-for SP and 3P SWA on PME
thanks
The separate cpc must be sized as if it alone were to take the earth fault current, it is not permissible to add the CSA's of the two conductors together