Hello again sparkies, here is a snippet of my project submitted for 2391-20 qualification regarding minimum size of S= √(1966²×0.1)/46=13.5mm²
Using the table provided by AEI I can see that a 70mm² four core cable has a 131mm² armour CSA, therefore this is perfectly acceptable.
[/I]
This shows that the armouring can handle 10x the amount of fault current that is required....!! no need for seperate CPC ;-)
Please note: values for armour and conductor resistance are from AEI cables, vvv useful!!! as you dont find them in the regs book, OSG etc. (OSG up to 50mm and doesnt show armour resistance.... there is a way of calculating conductor resistance but i cant remember how.....
Was going to post link to AEI site but you need to be a member to view the datasheets.... if anyone wants to see them and needs assistance then let me know
hope this helps AMP DAVID!!!
The AEI table suggest that the 'effective csa of armouring' is 16.38 sq.mm. Which seems closer to the mark and still good enough but not 10 times as good.
I am not criticising the findings but trying to get this to sink into my bald/grey head and have found this thread very useful.