Discuss Can we use the armour of an SWA as the CPC??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Hello again sparkies, here is a snippet of my project submitted for 2391-20 qualification regarding minimum size of S= √(1966²×0.1)/46=13.5mm²

Using the table provided by AEI I can see that a 70mm² four core cable has a 131mm² armour CSA, therefore this is perfectly acceptable.
[/I]

This shows that the armouring can handle 10x the amount of fault current that is required....!! no need for seperate CPC ;-)

Please note: values for armour and conductor resistance are from AEI cables, vvv useful!!! as you dont find them in the regs book, OSG etc. (OSG up to 50mm and doesnt show armour resistance.... there is a way of calculating conductor resistance but i cant remember how.....

Was going to post link to AEI site but you need to be a member to view the datasheets.... if anyone wants to see them and needs assistance then let me know ;)

hope this helps AMP DAVID!!!

The AEI table suggest that the 'effective csa of armouring' is 16.38 sq.mm. Which seems closer to the mark and still good enough but not 10 times as good.

I am not criticising the findings but trying to get this to sink into my bald/grey head and have found this thread very useful.

Thank You.
 
It would depend on what it is you wish to achive.
If for instance you wish to determine whether the armour of an SWA cable is suficient to be used as a CPC, then I would either use the cable manufacturer's data or perhaps a chart that you feel is reliable, and then apply the adiabatic equation.
If however you wished to determine, whether the armour was suitable to be used as a bonding conductor, I probablly wouldn't bother making the attempt other than as an exercise to prove to someone that the armour is not sufficient.

Got it now.Thanks.
 
Just throwing this in because i'm sick of reading these threads about very basic electrical practise. If you have to ask questions like this then you shouldn't be touching any electrical installation above a 13amp plug!!!
 
Just throwing this in because i'm sick of reading these threads about very basic electrical practise. If you have to ask questions like this then you shouldn't be touching any electrical installation above a 13amp plug!!!

I don't agree at all, this has been a good thread, especially the points relating to the adiabatic and copper-steel conductivity ratios.
 
Just throwing this in because i'm sick of reading these threads about very basic electrical practise. If you have to ask questions like this then you shouldn't be touching any electrical installation above a 13amp plug!!!

I look forward to your future input with interest. :cool:

Try your spell checker on the more taxing issues. :rolleyes:
 
@Amp David: Thanks for that eloquent input into the discussion. After all, who knows? maybe i am a "nugget", or maybe i'm just some daft spark that's looking after his and his fellow electricians jobs! Now for the reality check........If guys on here think they are doing some sort of noble gesture by educating the ill-informed fast track sparks out there by giving away our trade secrets and experience, then don't complain when the next job you've priced for at competitive rates is blown out of the water by a fast tracked fake spark, undercutting everyone and saying a big thanks for this oppertunity!!! Just think about it for a second and you'll see who the real nuggets are and pray that you'll always have a secure and non threatened workplace. Oh and TAFF4, i don't need to be great at spelling on a site like this as it's not dangerous......unlike some of the question and answers i've had the misfortune to gaze on here!!!
 
@Amp David: Thanks for that eloquent input into the discussion. After all, who knows? maybe i am a "nugget", or maybe i'm just some daft spark that's looking after his and his fellow electricians jobs! Now for the reality check........If guys on here think they are doing some sort of noble gesture by educating the ill-informed fast track sparks out there by giving away our trade secrets and experience, then don't complain when the next job you've priced for at competitive rates is blown out of the water by a fast tracked fake spark, undercutting everyone and saying a big thanks for this oppertunity!!! Just think about it for a second and you'll see who the real nuggets are and pray that you'll always have a secure and non threatened workplace. Oh and TAFF4, i don't need to be great at spelling on a site like this as it's not dangerous......unlike some of the question and answers i've had the misfortune to gaze on here!!!

madmac, I think you're missing the spirit of the forum, who are we to 'restrict' certain items of information?

The sizing of SWA for use as a CPC certainly doesn't slot into the 'trade secret' category, it's been the subject of many reports and studies by the IET and ECA!

Then the adiabatic equation, how many blank looks I get when I mention the adiabatic to 'time served' approved electricians, not because they are 'fast tracked fake sparks' but because they never have occasion to use it on a regular basis!

Of course we can all lose contracts to lesser qualified electricians but restricting forum information won't have a drastic effect on that....
 
New posts

Reply to Can we use the armour of an SWA as the CPC??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
603
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K
Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...
Replies
7
Views
1K
Armoured cable or equivalent to go around garden border for on the ground flood lights everyone using any alternative to swa, will H07RN be OK or...
Replies
5
Views
736
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock