We use Amtech software and have never had the swa armour fail as a suitable earth conductor.
We specialise in domestic and heavy industrial installation work.
 
We use Amtech software and have never had the swa armour fail as a suitable earth conductor.
We specialise in domestic and heavy industrial installation work.


That would depend on size and core number, it would also depend if your program automatically undertakes adiabatic equations in it's calculations. But it's not always the case where the SWA will meet the cables requirements of being the CPC...

Where figures work out, that are right on the knuckle so to speak, you may have to look at the length of that cables run....
 
Last edited by a moderator:
Hi folks very interesting post which provokes a lot of thought and reading / interpretation . I was once installing cabling for a large banking organisation for some UPS feeds , at that time we had our NICEIC assessment . Particularly he picked up on the fact that we had ran seperate CPC for the majority of the cabling installed , we stated that as a matter of belt and braces we installed these seperate CPC . At the time he informed us that anything less than 10mm2 (SWA) requires seperate CPC , so theoretically the seperate CPC installed by us was not required , but possible good practice .
 
Then the NICEIC inspector was clearly WRONG!! The Steel wire armour of the smaller SWA cables are more than adequate to be used as the circuits CPC. It's only after 95mm that you need to check for compliance!!

Things are a bit different if your intending to use the SWA for bonding purposes. As the SWA then needs to meet the copper equivalent of the required minimal bonding conductor size related to that installation...
 
As a respected member i will bow to your superior knowledge , as it happens our qualifying supervisor at the time then held the nic mans words to be good and all installs from then were done with compliance with his argument . i was not trying to say that this was wrong or wright , but just passing comment on my personal experience . As it happens i very rarely install a seperate CPC until as you say we get to the larger cables in which my AMTECH program works it all out quite nicely for me .
 
My appreciation for the quote of regs , however for at least the last 5 years on most of the large coporate installs i have been attached to the majority of SWA have had external seperate CPC's ran with them , so i assume not many people either do not read or understand the regs with or without new ammendments . not complaining just commenting
 
My appreciation for the quote of regs , however for at least the last 5 years on most of the large coporate installs i have been attached to the majority of SWA have had external seperate CPC's ran with them , so i assume not many people either do not read or understand the regs with or without new ammendments . not complaining just commenting

Don't doubt it, as it was the only way to provide a CPC for a SWA when the wire armouring couldn't comply as the CPC!! lol!!

But it just shows you how the NICEIC likes to make-up it's own regulations, and often getting things totally wrong in the process!! lol!!
 
Hi Hawk81

yes I come across that quite a lot myself & whats the betting that they have used Bw glands instead of weatherproof cw type
 

Reply to Can we use the armour of an SWA as the CPC??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
603
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K
Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...
Replies
7
Views
1K
Armoured cable or equivalent to go around garden border for on the ground flood lights everyone using any alternative to swa, will H07RN be OK or...
Replies
5
Views
737
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock