Discuss Combined L&N IR test on all RCBO board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

M

maguire

Hi
Carrying out a whole board insulation resistance test , very large house and LOTS of vulnerable equipment so wish to do a L&N combined [ link busbar to neutral bar] on whole board. Each circuit is on a RCBO , how would i test this, do the neutral and earth fly leads of each RCBO need to be disconnected?
Thanks in advance
 
Hi
Carrying out a whole board insulation resistance test , very large house and LOTS of vulnerable equipment so wish to do a L&N combined [ link busbar to neutral bar] on whole board. Each circuit is on a RCBO , how would i test this, do the neutral and earth fly leads of each RCBO need to be disconnected?
Thanks in advance

When you say Vulnerable equipment, i hope you have accounted for any dimmer switches, and removed them. Dimmers are (or should be) in the line conductor only, and no matter which test method you use, if they are in circuit, you WILL kill them.

Cheers...........Howard
 
Hi
Carrying out a whole board insulation resistance test , very large house and LOTS of vulnerable equipment so wish to do a L&N combined [ link busbar to neutral bar] on whole board. Each circuit is on a RCBO , how would i test this, do the neutral and earth fly leads of each RCBO need to be disconnected?
Thanks in advance


Disconnect L & N from each RCBO, link and then test to earth.
 
Dimmers are (or should be) in the line conductor only, and no matter which test method you use, if they are in circuit, you WILL kill them.

No, you won't kill them if you're testing L+N to E. I never have. If they have the same potential on input and output, which they will if L and N are connected together, then no problem.
 
They can only have the same potential on either side if you've bridged across the lamp?
Laurie


No, you won't kill them if you're testing L+N to E. I never have. If they have the same potential on input and output, which they will if L and N are connected together, then no problem.
 
Last edited by a moderator:
They can only have the same potential on either side if you've bridged across the lamp?
Laurie

If you leave the lamps in (no reason to remove them if testing L+N to E) then, since there's no significant current through the lamp when doing an IR test, the voltage on either side of the dimmer will be the same. This will apply in the case of standard GLS and halogen lamps, but may not be true for other types.
 
Which ever way you want to test is fine but with RCBO's and RCDSO you are far better removing the L & N from the units and then test.

The electronic internals are not compatible with IR testing even if it is fitted with a fly lead.

Post 4 answered the question IMO !
 
Which ever way you want to test is fine but with RCBO's and RCDSO you are far better removing the L & N from the units and then test.

The electronic internals are not compatible with IR testing even if it is fitted with a fly lead.

Post 4 answered the question IMO !
I Agree !
 
Going with post 4 too. Test each ct individually, it might take longer but at least you don't risk damaging the RCBO and having to replace it (pricey). Same goes for dimmers, if you ain't confident that they can withstand test take then out of circuit. I always IR at 250v on existing circuits & them ramp it up to 500v providing I don't get any unusually low readings.
 

Reply to Combined L&N IR test on all RCBO board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
689
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
775
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
646
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
709
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock