Discuss Confirmation on testing procedure in the UK Electrical Forum area at ElectriciansForums.net

APE37

-
Reaction score
56
Hi guys another q I would like to clear up,
when testing to confirm a pipe is extraneous in an existing install I use the equation 230/0.01 =23000ohms - 1000ohms= 22000ohms.
when carrying out the test I test from the earth block to the pipe in question.
just looking to confirm as I have just read on another post and site that you should pull the main earth out from supply cable and test from that ( obviously isolating the install first) so not to have any parallel paths
just wondering now weather I am right or wrong as in the G N 8 it states to test from MET so just looking for opinions as I have now got confused.
Cheers
 
Hi guys another q I would like to clear up,
when testing to confirm a pipe is extraneous in an existing install I use the equation 230/0.01 =23000ohms - 1000ohms= 22000ohms.
when carrying out the test I test from the earth block to the pipe in question.
just looking to confirm as I have just read on another post and site that you should pull the main earth out from supply cable and test from that ( obviously isolating the install first) so not to have any parallel paths
just wondering now weather I am right or wrong as in the G N 8 it states to test from MET so just looking for opinions as I have now got confused.
Cheers
https://www.youtube.com/watch?v=v38PfIVy2rI hope this helps
 
Pete you linked me that video some time ago, thanks again.

I've summarised it because he doesn't get to the point until the last minute.

IR tester - measure between a known earth and the metal.
A value of equal to; or less 0.02 M ohm it’s a extraneous conductive part.
> 0.02 M ohms it’s just a piece of metal.

Would you, or anyone else, agree with my summary ?
 
Pete you linked me that video some time ago, thanks again.

I've summarised it because he doesn't get to the point until the last minute.

IR tester - measure between a known earth and the metal.
A value of equal to; or less 0.02 M ohm it’s a extraneous conductive part.
> 0.02 M ohms it’s just a piece of metal.

Would you, or anyone else, agree with my summary ?
But when does the piece of extraneous pipe need bonding?
 
There's a reg in section 7 outling the 3 requirements to be met
so you don't need supplementary bonding
one is rcd protection, main water bonding and something else, I'd have to look it up. :D
 
I will watch it again, and will do research all around the topic.
Take advice from experienced people, such as yourself.
And will look out for it in any situation I come across it.
That's how I roll, and that's why I'm here. :D
 
I will watch it again, and will do research all around the topic.
Take advice from experienced people, such as yourself.
And will look out for it in any situation I come across it.
That's how I roll, and that's why I'm here. :D
Trust me, I need to watch videos like this to understand it!. To assist, I think your referring to re 701.415.2. Which go's on to say that all supplementary bonding may be omitted if items iv) to vi) apply. iv) says all extraneous conductive parts are effectively connected to protective equp' bonding. For that, 'Note' at the bottom refers to reg 415.2.2. Have a butchers at John Wards vid, goes into that in better detail than I can explain. Quite long vid, but worth watching to understand the reg. :)
 
Trust me, I need to watch videos like this to understand it!. To assist, I think your referring to re 701.415.2. Which go's on to say that all supplementary bonding may be omitted if items iv) to vi) apply. iv) says all extraneous conductive parts are effectively connected to protective equp' bonding. For that, 'Note' at the bottom refers to reg 415.2.2. Have a butchers at John Wards vid, goes into that in better detail than I can explain. Quite long vid, but worth watching to understand the reg. :)
Thanks I'll check out the JW video, a lot of the time I have to look at dozens of sources explaining the exact same thing to find the one that makes the coin drop for me. When I understand I go back to the expalanations I couldn't understand before, to see what extra I can gain. Thanks again !
 
Is the metal extraneous? If in doubt then a test will confirm this.

Test between the metal in question and the earthing conductor of the installation. The installation should be isolated from the supply before the test is carried out for obvious reasons.
IR @ 500V, A reading greater than 22Kohms will indicate that it is not extraneous. Below this value and Bonding is required.

Ohms Law. GN8 goes more in depth on the subject in regards to calculations and shock currents. The designer is the person who takes account for what is acceptable etc.

Happy to be corrected and learn something myself. Is it not just ohms law at the end of the day and a basic understanding of how to apply principles and science to ensure safety?
 
Reg. 415.2.2 gives an equation or formulae to calculate resistance R (max) between simultaneously accessible exposed-conductive parts & extraneous conductive parts. Below that figure it is effectively connected. Above that figure & below 22000 ohms, it requires bonding. Above 22000 ohms, as Mr Kitcher explains, its just a piece of metal.
 
The way it was explained to us, was each arm of your overalls was clamped in a bench vice by ya fellow apprentices, and another zapped you across each hand with a megger. Shocking.
 
What reading/value of ohms does it require bonding? For circuits protected by RCD e.g.?

Look at the first bit of the video and take note of where Chris derives the formula from, hint RCD operating current.
 
Look at the first bit of the video and take note of where Chris derives the formula from, hint RCD operating current.
Preaching to the converted Pete. I was trying to get the others guys to find out themselves without spoon feeding them. Also useful to note the reg applies to over current devices.
 

Reply to Confirmation on testing procedure in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
884
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
754
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
Replies
2
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock