Hi guys , I have to break a ring circuit through a contactor with an emergency stop button .. just want to double check my wiring in the diagram is correct .. haven’t done much of this sort of work so any feedback is appreciated.
A29BE5DC-97C4-4F55-938F-3DC9F1B645E0.jpeg
 
I would simplify things and place the socket RCBO in its own garage consumer unit, and the contactor on the supply to this CU.

What is the ring circuit used for? Power tools in a workshop?
 
Who has decided the Circuit needs an E.M stop and what is the reason for this decision?
Has whoever made the decision thought of the consequences of the EM stop being reset and whatever is plugged in suddenly starting up?
As it would be on 13amp sockets, anything in the future could be plugged in and subject to uncontrolled restart.

Normally anything under Em Stop control would have individual no volt release protection to stop the above happening.
 
Don't call it an Emergency Stop..... Just a Stop Button.
Next fit a Shunt Trip for the 32A RCBO.
 
Last edited:
Who has decided the Circuit needs an E.M stop and what is the reason for this decision?
Has whoever made the decision thought of the consequences of the EM stop being reset and whatever is plugged in suddenly starting up?
As it would be on 13amp sockets, anything in the future could be plugged in and subject to uncontrolled restart.

Normally anything under Em Stop control would have individual no volt release protection to stop the above happening.
It is a stop button that needs a key to disengage it again
 
It is a stop button that needs a key to disengage it again
It’s more that when it’s disengaged it turns on again anything plugged in e.g an angle grinder could unexpectedly start up. There is stuff in regs about avoiding rotating machines starting without warning.
A possible solution might be to also change the sockets to non-latching RCD sockets so restoration of power requires each socket to be individually reset.
I still don’t hugely like this though as by adding a facility to stop everything it’s introducing multiple scenarios of a button unexpectedly starting things.
 
Hi guys , I have to break a ring circuit through a contactor with an emergency stop button .. just want to double check my wiring in the diagram is correct .. haven’t done much of this sort of work so any feedback is appreciated.View attachment 108600

No, to the best of my knowledge that is non-compliant as the contactor will re-energize immediately when the stop button is reset.

There should be a minimum of a seperate reset button.

How far away from the RCBO is the contactor going to be? You'd be better off having a single 4mm conductor from the RCBO to the contactor.
If the contactor is far away from the OCPD then somebody could mistakenly add sockets to the ring before the contactor.
 
That would still need a seperate reset control.
Why ?

There's a big issue with the key reset type of E-stop in that human nature is to leave the key in it so that you don't loose it. This means the button can't be as easily operated as it should be.
If someone is silly enough to leave the key in after going to all the trouble of fitting a key to reset stop.

The same could be said for a tripped RCD or MCB do we need a separate reset for them as well ?
 

Reply to Contactor wiring, break ring circuit through a stop button in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
513
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Hi Everyone, hoping someone will be able to help me decipher the wiring for this hoist controller. the handset it came with has stopped working...
Replies
5
Views
510

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock