Discuss Contactor wiring, break ring circuit through a stop button in the UK Electrical Forum area at ElectriciansForums.net

Because, to the best of my knowledge it is one of the minimum requirements for emergency stops of any type, this isngiverned by legislation and not bs7671. I'm far from an expert on the relevant legislation though so yes I may be wrong.
If someone is silly enough to leave the key in after going to all the trouble of fitting a key to reset stop.

But you can't design a safety system based on whether it would be silly for someone to do something, these systems need to be designed failsafe and if one possible failure is a key being left in an e-stop then it should be designed out of the system.

The same could be said for a tripped RCD or MCB do we need a separate reset for them as well ?

The same cannot be said for those things, they are completely different and governed by completely different rules!

An MCB or RCD will automatically trip again if the fault still exists, an E-stop will not automatically press itself if reset in error.

If the E-stop fails to latch in the off position for any reason then having it electrically latched and requiring a second deliberate action to reset it will prevent a dangerous situation.
 
Hi guys , I have to break a ring circuit through a contactor with an emergency stop button .. just want to double check my wiring in the diagram is correct .. haven’t done much of this sort of work so any feedback is appreciated.View attachment 108600
I should add, The scenario for this wiring is in a classroom situation , for the instructor to kill the power when leaving the room. There won’t be any power tools used in this scenario so there shouldn’t be any reason for issues with anything starting up when engaging the stop button again .
Having said this , will the wiring be ok ?
 
Because, to the best of my knowledge it is one of the minimum requirements for emergency stops of any type, this isngiverned by legislation and not bs7671. I'm far from an expert on the relevant legislation though so yes I may be wrong.

Emergency switching: 537.4​

Emergency switching should be provided for any part of an installation where it is necessary to isolate the supply quickly to remove unexpected danger.

In installations with rotating machinery, this is usually done by using ‘stop’ buttons. Care should be taken to ensure that the stop buttons are…

  • Near to the machine / equipment
  • Should not be capable of being reset remotely, unless with a key switch.
  • If remote resetting is possible, then the activated stop button must remain activated at the point of the danger until being reset once the danger is removed.
  • In areas where there are untrained people, the stop buttons should lock when operated.

There is a difference between an emergency stop, generally used on moving machinery, and emergency switching off to turn off a few sockets, which is what the OP is intending.


An MCB or RCD will automatically trip again if the fault still exists, an E-stop will not automatically press itself if reset in error.
That's only if a fault is still present, it could be that the fault is intermittent, such as a partially cut cable.

If the E-stop fails to latch in the off position for any reason then having it electrically latched and requiring a second deliberate action to reset it will prevent a dangerous situation.

Emergency stop is an emergency operation intended to stop a process, system, machine, or a movement that has become hazardous.


Emergency switch off triggers an operation of switching off the supply of electrical energy and aims to reduce risk of an electric shock or other hazard.
 
I should add, The scenario for this wiring is in a classroom situation , for the instructor to kill the power when leaving the room. There won’t be any power tools used in this scenario so there shouldn’t be any reason for issues with anything starting up when engaging the stop button again .
Having said this , will the wiring be ok ?
So it’s not an emergency stop?

Just an isolator?
Simple on/off switch to control the contactor would be fine.

The instructor will be the “trained” individual and will know that all machines are off or unplugged before turning on the circuit.
 
I should add, The scenario for this wiring is in a classroom situation , for the instructor to kill the power when leaving the room. There won’t be any power tools used in this scenario so there shouldn’t be any reason for issues with anything starting up when engaging the stop button again .
Having said this , will the wiring be ok ?
The wiring is fine.
You probably don't need to disconnect the Neutral, depending on the earthing system.
In fact, you don't even need a contactor.
 
The instructor will be the “trained” individual and will know that all machines are off or unplugged before turning on the circuit.
We don't know what the instructor is trained in, he may be only good at sticking soles on shoes. :)
 
They have asked for the stop button that needs key to renegage
The contactor would be a N/O with a N/C stop switch.
You don't need a 4 pole contactor, a double would be fine or as said even a single depending on the earthing system.
 
I should add, The scenario for this wiring is in a classroom situation , for the instructor to kill the power when leaving the room. There won’t be any power tools used in this scenario so there shouldn’t be any reason for issues with anything starting up when engaging the stop button again .
Having said this , will the wiring be ok ?

So not an emergency stop at all then!

You just need a normal switch operating a contactor
 

Reply to Contactor wiring, break ring circuit through a stop button in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
498
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Hi Everyone, hoping someone will be able to help me decipher the wiring for this hoist controller. the handset it came with has stopped working...
Replies
5
Views
510

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock