Hi, I've got a practical exam for testing and inspecting later this week. I've researched the net and these forums and there is some good info just need to get some things clear in my head so I'm certain about the testing for the motor circuit. Its single phase and the circuit goes as follows:

DB > ISOLATER > DOL > REMOTE START/STOP > SIMULATED MOTOR (NEON INDICATOR)

For continuity is it correct to be thinking:
1 - link out L-E at the board and get reading at the DOL
2 - get reading from the DOL to the motor (I'll need to link L-E somewhere here too?)
3 - add the 2 readings together for my total R1 + R2 reading

For IR, I test from:
1 - DB > DOL
2 - DOL > MOTOR

The thing I'm not sure about is where to test for the IR and if any connections need removing. For DB > DOL do I remove L-N-E at the DOL and test at the DB. For DOL > MOTOR do I remove any connections supply side of the DOL and test at the MOTOR?

Any help is much appreciated, thanks.
 
dan or link out cables at dol and test full length from board to motor.

this is what people do to get a r1+r2 and zs on inverter fed motors etc.

you will get very high readings if you try to test zs through the dol
 
Last edited:
I wasn't thinking of testing through the starter just upto it, then after it and adding those values. When you say link out cables at the DOL you mean link incoming with outgoing to effectively bypass the DOL?

No point asking my tutor not sure he knows what he is doing. The college is riduculous, we haven't even been shown how to test a motor circuit. Great preperation!

Thanks for responding.
 
I wasn't thinking of testing through the starter just upto it, then after it and adding those values. When you say link out cables at the DOL you mean link incoming with outgoing to effectively bypass the DOL?

No point asking my tutor not sure he knows what he is doing. The college is riduculous, we haven't even been shown how to test a motor circuit. Great preperation!

Thanks for responding.
you test the motor the same as you do any other circuit.

we were asked to test upto the dol with r1+r2 and zs and r1+r2 from dol to motor
 
I am not sure what exam format you are involved with,but the second part of that test,could be motor control,and not installation. Also,the motor itself,may require disconnecting,depending what IR test is being performed.

I am a bit concerned,regarding your lack of confidence,in your tutor.

You really need to have that confidence,as what he is teaching you,could have serious consequences,the very least of which,is test methods...

If you post your course title,maybe we could advise where to get the best assistance,book wise,for example.
 

Reply to Continuity and IR for DOL starter in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
512
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
694
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
650
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
943
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
513

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock