Discuss CPC/Earth feed to Light Switch Back Box in the UK Electrical Forum area at ElectriciansForums.net

B

BettyBoop44

Hi
Just a bit of info required , just been checking all over the house checking for a earth feed to light fittings and switches , ( a friend informed yesterday that there friend have more or less sold there house , but an electrcal inspection has come up with no cpc to all the light switches ) .
I have found 3 light switch back boxes that do not have a earth feed to them , now the question is can I fit a plastic box inplace of the metal one that is in there and not need a earth feed to them ! .
All the light fittings have a earth feed to them ! , every circuit in the house is protected by a RCD .
cheers
BB
 
Hi
Just a bit of info required , just been checking all over the house checking for a earth feed to light fittings and switches , ( a friend informed yesterday that there friend have more or less sold there house , but an electrcal inspection has come up with no cpc to all the light switches ) .
I have found 3 light switch back boxes that do not have a earth feed to them , now the question is can I fit a plastic box inplace of the metal one that is in there and not need a earth feed to them ! .
All the light fittings have a earth feed to them ! , every circuit in the house is protected by a RCD .
cheers
BB
Has the cable at the switch had cpc cut off where the cable enters the box?
 
No just 2 core flat
So twin and earth from light to light with a twin to the switched, odd. Did the inspection produce any testing results? as it stands your friend can only use plstic switched, so no changing to fancy metallic switches.
 
I've seen this as lot as it was quite common around here for the feeds to be wired in 3/029 twin&earth with the switch drops in twin 1/044.

The solution to this is to replace the switch drop cables with T&E after testing the circuit to confirm that the CPC present is viable and compliant.
But you should also consider that this is an old installation and there may be other things which require improvement. Adding a CPC to a few plastic switches is a bit pointless if the main earthing and bonding aren't up to scratch!
 
So twin and earth from light to light with a twin to the switched, odd. .

Pretty common around here, I've fixed a few installations like this when I was doing domestics. Usually they have conduit down to the switches so it's an easy job to replace the switch drop with twin.
I think the reason it was done like this is that it was done when rewireing and the 3/029 twin didn't fit down the narrow conduits already in the wall.
 
So twin and earth from light to light with a twin to the switched, odd. Did the inspection produce any testing results? as it stands your friend can only use plstic switched, so no changing to fancy metallic switches.
Hi
Thanks for your reply , I am talking about my house not my friends friends house ! , the feed to the lights were also just 2 core flat , I fit a cpc to them a long time ago direct from the cpc bonding terminal next to the meter ,but did not think about the light switches , the kitchen and lounge light switches have a cpc they where put in when some workwas done there prob about 5 year ago .

cheers

BB
 
yes you could fit a plastic box in leui of a metal one, but remember the accessory would also have to be plastic. Are they cpc's at the light fittings?
 
If the back box and light switch are both non metallic then no CPC is required.
However care must be taken that a later owner doesn't add metal faced switches and a risk is created. We don't rely on RCD for protection as they can fail.
You could leave a note in the plastic backbox as a reminder that no CPC is present and no metal switches to be installed as a sort of gift to the next owner.
 
Hi
I really need a answer to my first post ie , can I fit a plastic back box in place of the metal one and then not need a cpc !
I assume these are flush to the wall boxes and plastic isn't ideal for this. Do the existing boxes have plastic lugs for the cover screws.
 
I assume these are flush to the wall boxes and plastic isn't ideal for this. Do the existing boxes have plastic lugs for the cover screws.

Good point. One of the common issues with light switches is the screws from the face plate being long and puncturing the wires behind. Potentially leaving a live screw head.
A plastic push in cover for each screw helps reduce that risk. Also taking care of the position of the cables as the face plate closes up and the length of the securing screws helps.
 
If the back box and light switch are both non metallic then no CPC is required.
However care must be taken that a later owner doesn't add metal faced switches and a risk is created. We don't rely on RCD for protection as they can fail.
You could leave a note in the plastic backbox as a reminder that no CPC is present and no metal switches to be installed as a sort of gift to the next owner.
Earthing may not be needed, but cpcs need to be present regardless
 
Hi
Thanks for your reply , I am talking about my house not my friends friends house ! , the feed to the lights were also just 2 core flat , I fit a cpc to them a long time ago direct from the cpc bonding terminal next to the meter ,but did not think about the light switches , the kitchen and lounge light switches have a cpc they where put in when some workwas done there prob about 5 year ago .

cheers

BB
BB your post has become confusing, what you need is a comprehensive EICR Electrical Installation Condition Report carried out by a competent Electrician, things have become difficult being drip fed information, get a Spark in to do the EICR and go from there.
 
  1. Taken from best practice guide 1 with installation containing no cpc to lights.
    This is regarding a consumer unit change but nevertheless contains some useful information I think.
    Sorry about the quality as it's copied and pasted

    Carry out a continuity test applied between the earthing terminal in the exis ng consumer unit and all Class I light fittings and metal plate accessories.

    If the resistance value is 1 Ω or less, the equipment may be considered to be earthed.
  1. 10.5.3. An insula on resistance test should be applied between the live conductors (line and neutral connected together) and the earthing terminal in the consumer unit, with that terminal connected to the means of earthing.

    The resistance should be at least 1 MΩ.

  2. 10.5.4. An insula on resistance test should be applied between line and neutral connected together
    and the exposed-conduc ve-parts of every Class I lighting and metal switch plate found to not be earthed by the con nuity tes ng described in Sec on 10.5.2.

    The resistance should be at least 1 MΩ.
10.5.5 If the circuit does not ful l the requirements
of either 10.5.3 or 10.5.4. there would be a
risk of electric shock if the circuit were to be re-energised. The customer must be advised in wri ng that this danger exists, and that the circuit must be disconnected from the supply and should not be connected into a new consumer unit.

10.6. If the customer will not agree to the risk assessment as described in Sec on 10.5. being carried out,
they should be advised that a ligh ng circuit having no protec ve conductor that has metal or Class I switches, light ngs or other accessories ed

is poten ally dangerous (and so would warrant a Code C2 classi ca on in an Electrical Installa on Condi on Report).

This will mean that the circuit cannot be connected into a new consumer unit (see Sec on 4.3 of this Guide).

10.7. It should be noted that the protec ve measure double or reinforced insula on is only applicable
to electrical installa ons or circuits therein that are under e ec ve supervision in normal use to ensure that no change is made that would impair the e ec veness of the protec ve measure (regula on 412.1.3). Domes c and similar premises falling within the scope of this Guide cannot be considered to be under e ec ve supervision.
 

Reply to CPC/Earth feed to Light Switch Back Box in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am installing some driveway lights. The customer wants to be able to switch them on from t he house, but also have a PIR at the driveway...
Replies
12
Views
658
Not the usual per-1966 sort of "no CPC in wiring issue" but plastic light switches in plastic back-boxes in trunking wired in singles. The lights...
Replies
3
Views
1K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
584
I'm installing smart modules in my light switches which means I need to replace the existing 25mm back boxes with 47mm ones. Downstairs all walls...
Replies
0
Views
325
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
637

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock