Discuss Do you need an earth rod for an outbuilding? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

All due respect josh, this is one if not the most talked about subject and the answer is definitely in previous posts. All good information. Search the forum with the search button and then use the similar threads underneath the page as you scroll down.
See you in a couple of weeks! (that's how many there are)
You will find the answer but people will also pipe up. Cheers, Rob
 
Search for Exporting PME on this forum and it gives you the various alternatives for supply to garage. TT system is one option and to me makes the most sense but there are other ways.
 
Of course the top hit if you search "Exporting PME" will be this Topic :)
 
Josh, there is an excellent article, that was published in the IET's Wiring Matters magazine that covers this, and other, issues relating to outbuildings power.
electrical installations outdoors: a supply to a detached outbuilding

Note; it was written a few years ago (16th edition) but the principles are the same.
 
Don't forget Josh there often isn't a right answer. The regulations often don't prescribe exact methods. They detail what you must do and what you mustn't do. But it also states that you can use alternative solutions as long as they provide equivalent or better safety to the suggested solutions.
As long as you aren't breaching a regulation (or doing so without a supported method to demonstrate your approach is safer, better etc) then the finer detail is just about choice and preference.
The best you can do is gather all the views. Check the regs yourself and come to your own solution. It won't be the solution everyone would chose but as long as its compliant and safe you are ok.
 
Well essentially normally DNO's dont like extending PME to garages, outhouses. That is why A TT system is used. For instance if you asked your DNO would they guarantee their PME in your garage at say 20m away see what they say. Might be a good starting point for how you are gonna go about it?
 
But surely some large houses will have runs greater than 20 mtrs? I know of some houses fed from one single phase supply with very long runs internally.
And for a garage using heavy SWA with its earth (larger than T&E CPC) surely you'd have as good if not better than a large house would have.
 
Fed from a spur on an existing ring in the house with a 2.5mm 3 core swa running to the shed (about 10m away from the house). Im going to put a small consumer unit inside the shed with an rcd in with a 6a mcb for a few light & a 16a mcb to feed 2 double sockets.

The house is tnc-s.

Josh
 
Fed from a spur on an existing ring in the house with a 2.5mm 3 core swa running to the shed (about 10m away from the house). Im going to put a small consumer unit inside the shed with an rcd in with a 6a mcb for a few light & a 16a mcb to feed 2 double sockets.

The house is tnc-s.

Josh
 
Fed from a spur on an existing ring inside the house with a 2.5mm 3core swa running to the shed (10m from the house). A small garage consumer unit in the shed with an rcd, a 6a mcb for 3 lights & a 16a mcb to feed 2 double sockets.

The house is tnc-s

Josh
 
Fed from a spur on an existing ring inside the house with a 2.5mm 3core swa running to the shed (10m from the house). A small garage consumer unit in the shed with an rcd, a 6a mcb for 3 lights & a 16a mcb to feed 2 double sockets.

The house is tnc-s

Josh
 

Reply to Do you need an earth rod for an outbuilding? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
315
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi, Posted here as I'm not an electrician, not because it relates to anything I'm considering "Doing Myself". My late parent's house is supplied...
Replies
5
Views
298
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
610

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock