Discuss Does a CU swap require a full initial verification on all circuits before it can be energised? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
16
To my understanding it would be ideal to test and inspect before energisation, but it isn't 100% necessary. If it leaves a client without power, it breaches health and safety (no power to safety services etc) or inconveniences them I'd have thought it would be reasonably practicable to turn on the juice and test ASAP.
 
To my understanding it would be ideal to test and inspect before energisation, but it isn't 100% necessary. If it leaves a client without power, it breaches health and safety (no power to safety services etc) or inconveniences them I'd have thought it would be reasonably practicable to turn on the juice and test ASAP.
You couldn't really have any confidence in that circuit/s unless you do.

In the case of a Cu change, for instance, why would you not test before energising ?
The power is only going to be going off again when it comes to testing, which will end up having no power for a longer time overall, unless you don't bother testing at all.
 
To my understanding it would be ideal to test and inspect before energisation, but it isn't 100% necessary. If it leaves a client without power, it breaches health and safety (no power to safety services etc) or inconveniences them I'd have thought it would be reasonably practicable to turn on the juice and test ASAP.

You're not really going to energise the system without doing the testing though are you. Surely the customer has been told that the power will be off during the CU change??

Yes, the testing is necessary.

In any case, you'd have to switch the power back off to do the dead tests, so what's the advantage of rushing to get the power back on before this?
 
Last edited:
How do you 'Change' a consumer unit without turning off the power ? Ok doing a little bit of dead testing might and an extra 25mins to the power being off but thats about it on an average board change. You could just switch everything on (the Bang Test) and hope for the best, but that is not the right way Imo
 
Ok,

To explain the situation... it's 4am, The electrician has been working since 8am. Beginning the testing process will be dangerous as the electrician is too tired to continue. The CU is installed properly so won't go bang an inspection of the CU shows this. If it is not energised there are severe disruptions... ambulance access, police access, security patrols are disrupted etc and the fire alarms & emergency lighting are affected to the premises.

Like I said, ideally, it would be tested but in this situation... but the regs just say reasonably practicable.
 
Ok,

To explain the situation... it's 4am, The electrician has been working since 8am. Beginning the testing process will be dangerous as the electrician is too tired to continue. The CU is installed properly so won't go bang an inspection of the CU shows this. If it is not energised there are severe disruptions... ambulance access, police access, security patrols are disrupted etc and the fire alarms & emergency lighting are affected to the premises.

Like I said, ideally, it would be tested but in this situation... but the regs just say reasonably practicable.
I should have been tested before the Cu was fitted ?
 
Ok,

To explain the situation... it's 4am, The electrician has been working since 8am. Beginning the testing process will be dangerous as the electrician is too tired to continue. The CU is installed properly so won't go bang an inspection of the CU shows this. If it is not energised there are severe disruptions... ambulance access, police access, security patrols are disrupted etc and the fire alarms & emergency lighting are affected to the premises.

Like I said, ideally, it would be tested but in this situation... but the regs just say reasonably practicable.

That's quite a specific example!

For such a critical installation then the job has been badly planned. And the bang test is certainly not appropriate.
 
Ok,

To explain the situation... it's 4am, The electrician has been working since 8am. Beginning the testing process will be dangerous as the electrician is too tired to continue. The CU is installed properly so won't go bang an inspection of the CU shows this. If it is not energised there are severe disruptions... ambulance access, police access, security patrols are disrupted etc and the fire alarms & emergency lighting are affected to the premises.

Like I said, ideally, it would be tested but in this situation... but the regs just say reasonably practicable.
Where is this DB.
 
That was my thinking, system had periodic inspections and the initial verification.

Job was planned by the bosses, timing and planning not up to the electrician.

Advice to next shift on at 8am to test critical systems given. Client happy to wait a further 4 hours. They neither tested nor re-energised. Left no power for 2 days.

When it was tested... and re-energised... no bang.

Has caused a bit of a thing at work. Just wondering which way to go.
 
That was my thinking, system had periodic inspections and the initial verification...

...Has caused a bit of a thing at work. Just wondering which way to go.

The reason given for not doing anything was there was a C3 fault. The board installed was smaller than the original so conduit no longer fitted. (Not installers choice) it was planned to be boxed in. This was predicted and reported to management. Knockouts were given grommet strip edging.

Tbh... I'd have tested it, powered it up and said get the joiner in ASAP. (I think the 2nd shift are just bullying the original electrician)
 
The C3 where conduits no longer line up with knockout holes…. Is there a gap now with basic insulation showing between the conduit and the DB?

Could have been solved with a bit of trunking?
 
Last edited:
The C3 where conduits no longer line up with knockout holes…. Is there a gap now with basic insulation showing between the conduit and the DB?

Could have been solved with a bit of trunking?
Yes we used to run some galv trunking horizontal butted up to the board and take the conduits into the trunking which means no gaps or mis-aligned old conduits in the new DB
 
To explain the situation... it's 4am, The electrician has been working since 8am.

So the Electrician has been working continuously for 20hrs and is then starting or completing a C.U change?

Powering up untested because it's inconvenient / potentially a H&S issue is not a valid reason.
It could be a bigger H&S issue if there was a fault that caused injury or worse.
Just because it had had previous inspections doesn't mean at the end of the CU swop that it doesn't have any faults, especially given how long the Electrician had been working.

There's already a serious H&S issue with the electrican working 20hrs.
 
Last edited:
The C3 where conduits no longer line up with knockout holes…. Is there a gap now with basic insulation showing between the conduit and the DB?

Could have been solved with a bit of trunking?

Agree. Conduits line up perfectly. There's about a 9-10mm gap. It's boxed in with no stress or strain & no access. Essentially the conduit is rendered null & void?
 
So the Electrician has been working continuously for 20hrs and is then starting or completing a C.U change?

Powering up untested because it's inconvenient / potentially a H&S issue is not a valid reason.
It could be a bigger H&S issue if there was a fault that caused injury or worse.
Just because it had had previous inspections doesn't mean at the end of the CU swop that it doesn't have any faults, especially given how long the Electrician had been working.

There's already a serious H&S issue with the electrican working 20hrs.

Ok... maximum security prison. Various high risk prisoners topping themselves and stabbing each other... yes planning should have been way way better... but loss of power was a real H&S risk. Refusing to test it or put it back on for 2 days over a C3 fault? The more I think about it the more I think they should have had the guys back and sorted something out.
 
I still don't get how the job ended up going the way it did. Was it badly planned? Were there too few staff doing the job?

What if it had gone wrong due to lack of time/testing?

Edit: I realise it's easy for me to criticise while I'm sat here drinking Old Peculier!
 
Last edited:
I still don't get how the job ended up going the way it did. Was it badly planned? Were there too few staff doing the job?

What if it had gone wrong due to lack of time/testing?

As far as I can tell mistakes on both sides. Electrician thought 6-8 hours to install and test. Had to put in extra metal conduit for fire alarm because board had to be moved further left to align the conduit. Board supplied had incomer on wrong side and most CPD's supplied were wrong too. True nightmare job. The bosses son organised it and was assisting (office admin/wannabe apprentice) apparently he just sat down and did next to nothing. Didn't even pass tools.
 
Terrible planning does not mean you can energise circuits without proper testing, whether that's in your house or in a prison. The location of the circuits is absolutley irrelevant, it should NEVER be energised before proper testing has taken place. Person planning job should be sacked for lack of competence and having a spark working 20 hours van only lead to tiredness and inevitably mistakes. Prisoners topping themselves won't be an issue if they are killed by something electrical due to lack of testing to confirm its safe I'm the worst case scenario.
 
I still don't get how the job ended up going the way it did. Was it badly planned? Were there too few staff doing the job?

What if it had gone wrong due to lack of time/testing?

Edit: I realise it's easy for me to criticise while I'm sat here drinking Old Peculier!
Early guzzle Daz 🍺🍺
 
Terrible planning does not mean you can energise circuits without proper testing, whether that's in your house or in a prison. The location of the circuits is absolutley irrelevant, it should NEVER be energised before proper testing has taken place. Person planning job should be sacked for lack of competence and having a spark working 20 hours van only lead to tiredness and inevitably mistakes. Prisoners topping themselves won't be an issue if they are killed by something electrical due to lack of testing to confirm its safe I'm the worst case scenario.

That's what I'm saying though. It's just a board change. There aren't really any tests that are anything to do with the wiring up of the board itself. A visual could confirm that live, neutral and earth cables were in the correct terminals or if there was damage to cables. Tork screwdriver for the secureness of the terminations, RCD test. That's about it. Even if the neutral or earth conductors weren't in exactly the right/corresponding terminals it's a busbar at the end of the day. There was a legend so CPD ratings could be verified. Sure it should be tested, I don't disagree, but I mean, what is it that we're actually testing?

Am I wrong. Am I missing something?
 
Look, you are obviously concerned youself. Otherwise you wouldn't have asked the question!
 
Look, you are obviously concerned youself. Otherwise you wouldn't have asked the question!

Lol no. Just want people's opinions. I'd have tested it, but failing that I think I would have put on one circuit at a time. Until it was all up. There's nothing definite in the regs. Just wondered what the popular consensus was... while I also have a beer.
 
Was there any thorough testing carried out beforehand though? How would you be aware of any faults that were already existing e.g broken ring conductor or high resistance connection on a circuit that an rcbo wouldn't pick up? Every single termination in the board has been remade and there is requirement by regulation for every circuit to be tested. There is no leg to stand on here, every circuit must be tested before re-energising. I'm afraid there is no short cut or other solution here, I agree with the electricians decision not to re-energise until testing has taken place, as if a situation did arise he would take the blame for it, poor planning or not
 
Was there any thorough testing carried out beforehand though? How would you be aware of any faults that were already existing e.g broken ring conductor or high resistance connection on a circuit that an rcbo wouldn't pick up? Every single termination in the board has been remade and there is requirement by regulation for every circuit to be tested. There is no leg to stand on here, every circuit must be tested before re-energising. I'm afraid there is no short cut or other solution here, I agree with the electricians decision not to re-energise until testing has taken place, as if a situation did arise he would take the blame for it, poor planning or not

Ah, right. The electrician refused to do the testing based on the C3. Said it failed outright.

Periodic inspection and testing every 12 months.

I admit it's a weird one. Just my own pondering whether the installer could have given permission to energize.
 
Surely that is referring to the design process.
132.16 states: "No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including the distributor, will be adequate for the altered circumstances
 
Ah, right. The electrician refused to do the testing based on the C3. Said it failed outright.

Periodic inspection and testing every 12 months.

I admit it's a weird one. Just my own pondering whether the installer could have given permission to energize.
But that periodic testing is only as good as the day it's tested, and the eicr does not apply once the board has been changed. Much like the mot on your car. Except changing the board is like taking every single screw and bolt out of your car, putting them back in and not getting it checked. He couldn't give permission to energise whilst still following regulation.
 
Last edited:
But that periodic testing is only as good as the day it's tested, and the eicr does not apply once the board has been changed. Much like the mot on your car. Except changing the board is like taking every single screw and bolt out of your car, putting them back in and not getting it checked. He couldn't give permission to energise whilst still following regulation.

Unless he inspected and tested. Which he could have done. But didn't. (I still find no regulation supporting your view mind.)
 
What was this C3 and was this C3 from a previous EICR.

The C3 was a 70-90mm gap between the existing conduit and the board. Planned to be sorted with boxing in later and grommets. Risk assessment done expected very low risk from the position of the board. Could not physically cause or contribute to an accident short of sticking a fork in it.
 
Unless he inspected and tested. Which he could have done. But didn't. (I still find no regulation supporting your view mind.)
You find no regulation that says you can't energise a circuit without testing being completed? I wont attempt to justify what I said, as I know i am correct. Scary to think anyone would consider energising anything without confirming its Sage
 

Reply to Does a CU swap require a full initial verification on all circuits before it can be energised? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I hear many views of people who believe that DPF's and CDPF's fitted to their vehicles are a problem and many people resort to removing them, or...
Replies
0
Views
8K
I'm a Facilities Manager and not an electrician though I do have some electrical qualifications of some years ago. I wonder if anyone would like...
Replies
4
Views
8K
W
Hello again ladies and gentleman, To those who vaguely remember who I am from my last posts maybe 24 months or so ago and those who of course...
Replies
8
Views
1K
wade88
W
G
I'm taking C&G 2377 22 next year probably around May ish My hunch is that asking some qualified electricians a few somewhat daft questions...
Replies
20
Views
5K
goodconnection
G
S
Hi everyone, I am after some advice/feedback on the British gas six weeks electrician course in Rotherham . I was told it will cost £3995 inc...
Replies
25
Views
3K
sedgy34
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock