Thanks for the link BruceB
This is the IMPORTANT bit from the BS:
So I think that both the IET and NICEIC guys according to the LETTER of the regulations are WRONG when relating to rotary isolators (the important words from above are "and distribution" ); if putting in a 'garage' / 'shower' or similar small unit with a main switch and at least one MCB, then it needs to be in a non-combustible enclosure.
If we consider the SPIRIT of the regulations, then see here for the reason for the introduction of non-combustible CU's: (Consumer units - IET Electrical)
Then on the basis that the same poor workmanship could occur on a a rotary isolator, double pole MCB or incoming RCD you can see why IET / NICEIC will send out the message that they wish it to be in a non-combustible enclosure
If you've never seen it, then you should seee the sparks and flames you can get when a short circuited DC cable (for Isc testing) on a small domestic installation is pulled apart - it's just like an arc welder.
HOWEVER, (and this is where the argument falls down) I would hope that MCS registered solar PV installers, the installation being of a specialist nature are particularly aware of the dangers of the above poor workmanship issues and so take particular care to ensure those errors don't occur. Unfortunately we have took often come across badly installed isolators.
This is the IMPORTANT bit from the BS:
Additional definition
3.1.104 Customer distribution board CDB
An integrated assembly, for the control and distribution of electrical energy, principally in a household or similar premise, incorporating manual means of double-pole isolation on the incoming circuit(s), with polarity observed throughout. They are designed for use exclusively with specific protective devices on the outgoing circuits, and type-tested for use when energized through the specified 100 amp fuse. NOTE Generally known in the UK as a Consumer unit.
So I think that both the IET and NICEIC guys according to the LETTER of the regulations are WRONG when relating to rotary isolators (the important words from above are "and distribution" ); if putting in a 'garage' / 'shower' or similar small unit with a main switch and at least one MCB, then it needs to be in a non-combustible enclosure.
If we consider the SPIRIT of the regulations, then see here for the reason for the introduction of non-combustible CU's: (Consumer units - IET Electrical)
Reason for the new regulation
Regulation 421.1.201 was introduced because of reports from fire investigators of a recent trend of increasing numbers of fires involving consumer units having a moulded thermoplastic enclosure
The cause of the fires investigated was almost invariably found to be resistance heating as a result of poor electrical connections due to poor workmanship or lack of maintenance. Examples of such poor workmanship are thought to include:
- failure to tighten neutral conductor connections to the same torque as line conductor connections due to a misconception that neutral conductors carry less current;
-inadvertently taking cable insulation inside the terminal at a connection, resulting in the securing screw or the clamp of the terminal not making proper contact with the conductor;
- failure to check factory installed connections for tightness where required to do so by the manufacturer; and
- tightening connections to an incorrect torque and/or with inappropriate tools.
The crucial importance of checking that all electrical connections are properly made, and of taking remedial action where necessary, should never be forgotten.
Whilst the main cause of fire within plastic consumer unit enclosures is without doubt poor workmanship, other potential causes of fire within plastic consumer unit enclosures are thought to include:
- the type of internal components, such as where terminations have only one securing screw or are of the 'cage clamp' type); and
-where increased heat transfer to the enclosure is caused by the close proximity to an internal item, such as a neutral bar or a conductor terminated at the neutral bar and protruding above it.
Intent of the new regulation
The intent of Regulation 421.1.201 is considered to be, as far as is reasonably practicable, to contain any fire within the enclosure or cabinet and to minimise the escape of flames.
Then on the basis that the same poor workmanship could occur on a a rotary isolator, double pole MCB or incoming RCD you can see why IET / NICEIC will send out the message that they wish it to be in a non-combustible enclosure
If you've never seen it, then you should seee the sparks and flames you can get when a short circuited DC cable (for Isc testing) on a small domestic installation is pulled apart - it's just like an arc welder.
HOWEVER, (and this is where the argument falls down) I would hope that MCS registered solar PV installers, the installation being of a specialist nature are particularly aware of the dangers of the above poor workmanship issues and so take particular care to ensure those errors don't occur. Unfortunately we have took often come across badly installed isolators.