Hi all

Got a PME with 6mm gas & water
Looking into the board there is 10mm gas & water it's been upgraded to 10mm.

The 6mm from the PME is still in place with the 10mm. Board was upgraded to an RCBO board. What would you do?

I have a pic

Cheers
 
Do you mean there is 10mm in parallel with old 6mm to both water and gas?

I would just leave it be, unless you suspect the 6mm is a much shorter route than the new 10mm and so might take the majority of fault current.
 
Do you mean there is 10mm in parallel with old 6mm to both water and gas?

I would just leave it be, unless you suspect the 6mm is a much shorter route than the new 10mm and so might take the majority of fault current.
Thats correct in parallel with each other
 

Attachments

  • 20210906_145300.jpg
    200.8 KB · Views: 24
Can't see the problem if they are in parallel and the 10mm one is not significantly longer than the 6mm one.
 

Reply to Earthing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
610
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
245
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
536
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
582

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock