Thats correct in parallel with each otherDo you mean there is 10mm in parallel with old 6mm to both water and gas?
I would just leave it be, unless you suspect the 6mm is a much shorter route than the new 10mm and so might take the majority of fault current.
My bad?....Ahem
[pedant alert]
That is bonding, not earthing.
[\pedant alert]
Yes. Length is not the determining factor... its the resistanceCan't see the problem if they are in parallel and the 10mm one is not significantly longer than the 6mm one.