Discuss eicr communal areas in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

1983

-
Reaction score
34
Hi all some advice would be much appreciated please when carrying out a eicr in a communal area for landlord supply lightning and power on the report section main bonding conductors as I'm aware you hardly get a gas and water supply for communal areas would that mean I put na in the boxes? The gas and water is bonded from the main met before branching off to each flat but as I'm only testing landlords supply that has nothing to do with my report is that right. Spoken to two different guys from nic technical departments and one says to put na the other says as its bonded to the main met u note it down.
 
I'd have checked the bonding anyway and so may as well note it.
 
Thanks for the feed back guys much appreciated its a 3phase supply tncs goes to ryfield board and from there splits to each meter with submains to each flat 6 flats and one for the landlord supply I'm doing a eicr on the landlords supply only. the section on the cert that ask bout main bonding I've been told to put n/a and also to put what ever size main bond is to the incoming gas water to the building not sure which nic technical guy to listen to
 
If the services are in proximity to the Landlords supply, for example they are in the same room as the electrical distribution then yes. If there is total separation from the Landlords electrical system then I would put NA.
 

Reply to eicr communal areas in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
850
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
173

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock