Morning guys,
I'm just after a bit of advice. I carried out an EICR on a commercial premises yesterday (no periodic since 1995). 3 phase out of the meter into Henley blocks then split between 3 distribution boards. Two single phase (one old 7 way rewireable wylex board and one single way proteus board) and one enclosure housing only a 3 phase mcb feeding an oven.
What is best practice to record in the main switch/circuit breaker on the EICR? They obviously don't share anything common apart from the 1361 cutout fuses. Any help would be appreciated!

IMG_5544.JPG
 
Well have you removed the covers for inspection purposes? if the don't have covers at all I would be more concerned with that issue, than what main switch I should be quoting in my EICR.
oh sorry, yes, the covers have been removed for the inspection, it wasn't found like that!
 
Looks a right lash up the conductors between the Hager mcb and the trunking are not suitably enclosed.
 
Looks a right lash up the conductors between the Hager mcb and the trunking are not suitably enclosed.
Yeah it's a bit of a mess, there were a lot of faults on the general standard of wiring and IP ratings. With no single point of isolation would this go in as C3?
 
If I were doing the EICR for an insurance company, who have less than intelligent conditions of addressing all C3s, then it would be no code as the switches are all in close proximity, if it were being done privately then C3 on the schedule of inspections as this would be a recommended improvement for safety. N/A on the installation details and each individual main switch identified in the schedule of test results.
 
If I were doing the EICR for an insurance company, who have less than intelligent conditions of addressing all C3s, then it would be no code as the switches are all in close proximity, if it were being done privately then C3 on the schedule of inspections as this would be a recommended improvement for safety. N/A on the installation details and each individual main switch identified in the schedule of test results.
I don't really get that what difference does it make. Whether someone ignores the C3 is not a reason for not including it.
 
I don't really get that what difference does it make. Whether someone ignores the C3 is not a reason for not including it.
If there is a minor recommendation for safety that will cost a customer significant sums to address for minimal gain I feel this is counter productive and not a professional approach. Having someone aware of an issue that could be addressed at a time something else is being changed is good, forcing someone to immediately and without fail to install a single main switch for close grouped boards is not good.
 
If there is a minor recommendation for safety that will cost a customer significant sums to address for minimal gain I feel this is counter productive and not a professional approach. Having someone aware of an issue that could be addressed at a time something else is being changed is good, forcing someone to immediately and without fail to install a single main switch for close grouped boards is not good.
appreciate your feedback
 
There was a section on the single point of isolation recently in the mag we get from napit, it's page 32 in issue #1 2017 for anybody that hasn't binned it yet.

Their view is that although yes it is good practice to have an isolator at the origin it is NOT required by BS7671 and so no code is required.
How have they explained side tracking Reg 537.1.4
 

Reply to EICR Main Switch/circuit breaker in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
882
HI , potential 2 bed 1970’s bungalow buyer here…. Our surveyor (RICS) has pointed out there is no circuit breaker to the electrics (fuse board...
Replies
16
Views
1K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
654
Hi all, Been asked to quote an EICR on a fairly large installation. Approx. 400 circuits that are a mixture of single and 3 phase. This is across...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock