So you apply if the installation complies with BS7671 Amd 3 depending who you are doing the EICR for ?.C3 is improvement recommended/does not comply with the latest regsIf I were doing the EICR for an insurance company, who have less than intelligent conditions of addressing all C3s, then it would be no code as the switches are all in close proximity, if it were being done privately then C3 on the schedule of inspections as this would be a recommended improvement for safety. N/A on the installation details and each individual main switch identified in the schedule of test results.
C3 is for a non compliance with BS7617 that may give rise to danger and so improvement is recommended but it is not a situation of immediate danger or where a fault may cause danger.So you apply if the installation complies with BS7671 Amd 3 depending who you are doing the EICR for ?.C3 is improvement recommended/does not comply with the latest regs
Now why doesn't that surprise me?Along with your scheme technical helpline does anyone use the IET tech line?
I have done once and they had different advice from the NICEIC helpline.
I'd rather phone the IET tech line.Now why doesn't that surprise me?