Search for tools and product advice,

Discuss EICR - top of consumer unit is not correctly IP rated in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Hi all,

Hope your all well!

I've just had an eicr done on my coffee shop and one of the things that has come back is the above as per the attached pics, the consumer units are in a cupboard which I can out a lock on to stop access.

I am being told that all the wires have to be removed from the board to allow the fitting of trunking and that is a major job (basically the same job as changing the fuse board), is that right, as I'm hoping there must be an easier way???

Many thanks,

Martin
 

Attachments

  • IMG_20200701_180238.jpg
    65.6 KB · Views: 177
I think the problem here is the connectors floating about.(even inside a locked cupboard) They could be joined inside the consumer unit.
The IP rating would just "need improving" but nothing wrong with that as it stands. If they were putting trunking in, they will have quoted for metal consumer units as well.

James beat me to it..... just hide the cables behind a wood panel
 
We could have a non binary, gender neutral individual in here.
Lots of monkeys as well, if you look at some profile pictures.
Mine is just a painting of Baby Yoda.... on a stone.
 
Ideally the cable joint should be inside the consumer unit , apart from that it’s simply boxing the consumer units in to hide the cables...
 
What code did the inspector give on the EICR? Is the top surface readily accessible? I would suggest a C3 for the IP rating and C3 for the exposed wago connectors (Potentially C2 on closer inspection - can’t tell from pic how well they have been done or how secure the cupboard is) does the cupboard Solely for the consumer unites , have warning notice 240v and under controlled lock and key access ? If so you could argue no codes /improvement are required.
 
What is the issue with the IP rating of the CU's they look to meet the requirements of IP2X Looking at it they would pass the British Standard Finger test which is the minimum IP2X requirement so I don't see any reason to code it
The wagos do need a box or relocating within one of the CU's though and should have been coded
 
What is the issue with the IP rating of the CU's they look to meet the requirements of IP2X Looking at it they would pass the British Standard Finger test which is the minimum IP2X requirement so I don't see any reason to code it
The wagos do need a box or relocating within one of the CU's though and should have been coded
It’s ip4x on the top surface required
 
strange that it's IP4 on the top where a non-insulated driver could be inserted to possibly touch the top terminalof a MCB, but IP2 on the bottom where a screwdriver can touch a live busbar more easily.
 
strange that it's IP4 on the top where a non-insulated driver could be inserted to possibly touch the top terminalof a MCB, but IP2 on the bottom where a screwdriver can touch a live busbar more easily.

ive never fully understood why the top has a different (higher) ingress rating...
The whole board should be the same imo
 

Reply to EICR - top of consumer unit is not correctly IP rated in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Hoping someone can clarify for me. I've recently moved into a rental property, the landlord had new electric radiators installed and a new...
Replies
3
Views
587
Hi all, Been asked to quote an EICR on a fairly large installation. Approx. 400 circuits that are a mixture of single and 3 phase. This is across...
Replies
22
Views
3K
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top