Discuss Extending cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
8
Been asked to move supply for a pizza oven in a fast food outlet,it's currently wired in 16 mm but could I use 10 mm to extend via Lucy blocks or stick with 16? I have plenty of 10 but no 16 but want to do the job right.

oven is 50 a an cable will be in 50 x50 PVC trunking

Many thanks in advance
 
Changing, especially reducing, cable CSA in mid run would be very bad practice. The next sparky may replace the MCB in the CU according to the cable size he sees and this would leave the 10mm section open to overload.
 
You can buy 16mm by the meter at the wholesalers, the cost of which you pass onto the client. However if you say it is only 6m to the DB why not renew the whole run rather than putting a join in?
 
I assume someone would have mentioned it by now if there was but I'm surprised there's no reg forbidding the reducing of CSA mid cable run.
 
I reduced a lighting circuit from 2.5mm to 1.5mm the other day. 2.5mm was in there to due to voltage drop, and didn't fancy trying to terminate 2.5 into switches and pendants. Not quite the same thing, I know. Hope I don't get shot!
 
Just wondering how any electrician would even think of reducing the supplying cables CSA on a high current bit of equipment. Or come to that, putting a joint in the system when we're only talking about 6 metres to the DB!!

Has anyone even bothered to assess and/or calculate the correct size of cable for this Pizza oven??
 

Reply to Extending cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Replies
1
Views
360
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
858
(Trying again, as picture didn't post first time) Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how...
Replies
5
Views
1K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
942

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock