Hi Everybody

Why fuse is no longer use in Final Circuit Protection. Instead, Circuit breakers are used.

So far, I know that CB is more sensitive than fuse.

Can someone depicts any reason and their respective curves.

Thanks
 
Have a look in appendix 3 of bs7671 for the time/ current curves of both fuses and mcbs.
Also fuses to bs 88 are still used for circuit protection for things like distribution circuits.
Perhaps you mean bs 3036 rewireable fuses no longer used?
 
Fuses can still be used if required, however a fuse requires replacement when it operates whereas a circuit breaker can (usually) be reset.
Therefore the maintenance costs are lower and re-energising a circuit is easier with circuit breakers so they are the preferred method.
Fuses may be used more often upstream in the circuit as they can provide discrimination and, if the cascading works, will not operate often.
 

Reply to Final Circuit Protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
803
I would like to get some information on what protection is on a multi meter when accidentally testing a live circuit while the meter is on the...
Replies
1
Views
483
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
510
I am using a 160watt-200watt multi uv tube stand alone sunbed,When the 2 power leads (plugs protected by 2x13amp fuses) plugged into a double wall...
Replies
9
Views
743
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock