Search the forum,

Discuss fire rated or not down lightd in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Reaction score
22
Looked at job for a builder to put down lights in soffit of a porch, single storey flat roof 2m x 2m. But void is only 80mm deep, told him he should have built it bigger but just says put them down lights in with no covers. My I dea was fireproof down lights, but not enough room. So as its outside, only one story do they need to be fireproof????
 
hi simon, if it is hasn't got a habital room above then no requirement for fire rated fittings to be installed, is there insulation in void? and what is ceiling material? presuming internal not external? confused about sofit as this is the external overhang normally.
 
Haler H2 are only 70mm high

Fire rated are only needed to maintain fire barriers. Typically, these will only be found between floors of separate properties, ie. in the ceiling of a ground floor flat. If there's no second floor flat then the downlights in the ceiling of the first floor flat need not be fire rated.

A lot of misinformation out there about when you need and don't need to maintain fire barriers.
 
Haler H2 are only 70mm high

Fire rated are only needed to maintain fire barriers. Typically, these will only be found between floors of separate properties, ie. in the ceiling of a ground floor flat. If there's no second floor flat then the downlights in the ceiling of the first floor flat need not be fire rated.

A lot of misinformation out there about when you need and don't need to maintain fire barriers.

You also require fire rated in a standard two storey house. You would need this to maintain the 30 min rating of a standard plasterboard ceiling. http://www.downlights.co.uk/files/ESC-Fire-Rated-Downlights.pdf?334762691
 
Thanks for the quick genuine response, yes external soffits but always tried to fit fire rated before as a good practice measure. And correct that there are many misconception of fire rating rules, thanks
 
You also require fire rated in a standard two storey house. You would need this to maintain the 30 min rating of a standard plasterboard ceiling. http://www.downlights.co.uk/files/ESC-Fire-Rated-Downlights.pdf?334762691

TJ, thank you very much for the link to this document ... it should be mandatory reading for all professional electricians. Furthermore, I think that it provides insight into the reasons behind that much discussed and ill-liked BS 7671 amendment 3 provision for incombustible CUs.
 
Haler H2 are only 70mm high

Fire rated are only needed to maintain fire barriers. Typically, these will only be found between floors of separate properties, ie. in the ceiling of a ground floor flat. If there's no second floor flat then the downlights in the ceiling of the first floor flat need not be fire rated.

A lot of misinformation out there about when you need and don't need to maintain fire barriers.


There is a lot of misconception and I'm still not sure about whether or not they HAVE to be fitted in the ceiling if there is a roof space above. However, I will always fit fire rated ones when there is a loft above as this is recommended by 'Electrical safety first' in Best Practise Guide Number 5 - page 8 section 7.7 - (see link given by TJ in post 8). Their reasons are that this will:

1. Safeguard escape from the premises
2. Restrict the spread of fire.
3. Reduce the risk of premature failure of the roof structure

Also, The Electrical Safety Council recommends fire rated downlights fitted in 'all' ceilings' View attachment downlight information sheet- ESC.pdf
 
Have a read of part B and you'll see that they are not required for ceilings when the only stricture above is a roof.

But I normally fit fire rated downlights everywhere because the fittings I use don't exist as a non fire rated fitting
 
Have a read of part B and you'll see that they are not required for ceilings when the only stricture above is a roof.

But I normally fit fire rated downlights everywhere because the fittings I use don't exist as a non fire rated fitting

I've looked through the index Dave and also spent 5 mins scanning through the 86 pages but I cant see any mention of downlights. I'm not saying they're not there, I'm sure they are, I just cant find it! Do you know which page refers to the downlights and there situation in a ceiling with roof above?

ps.. Have also just done a search for the word 'downlights' and 'recessed' in Part B and nothing came up? Perhaps you are referring more to do with general requirements in a roof space rather than specifically anything to do with downlights?
 
Last edited:
I've looked through the index Dave and also spent 5 mins scanning through the 86 pages but I cant see any mention of downlights. I'm not saying they're not there, I'm sure they are, I just cant find it! Do you know which page refers to the downlights and there situation in a ceiling with roof above?

That's because it doesn't mention downlights. It mentions fire ratings of ceilings in minutes, the situations in which they apply, and the need for reinstating such ratings if the ceilings are compromised.
 
That's because it doesn't mention downlights. It mentions fire ratings of ceilings in minutes, the situations in which they apply, and the need for reinstating such ratings if the ceilings are compromised.

I was beginning to think it must be something like that, thanks.

Would still be good to have the section of the document pointed out though if you feel like it? :smile5: As I'm looking and looking and cant find it!
 
Last edited:
I've looked through the index Dave and also spent 5 mins scanning through the 86 pages but I cant see any mention of downlights. I'm not saying they're not there, I'm sure they are, I just cant find it! Do you know which page refers to the downlights and there situation in a ceiling with roof above?

ps.. Have also just done a search for the word 'downlights' and 'recessed' in Part B and nothing came up? Perhaps you are referring more to do with general requirements in a roof space rather than specifically anything to do with downlights?

The same as all other standards etc you have to read, understand and apply the requirements. They couldn't possibly list every single possible penetration of a fire barrier seperately!

The following sections of part B3, among other sections, apply.

7.2 covers holes for cables etc to pass through, also can apply to downlights etc
7.4 says that holes in fire barriers for downlights etc may need to have the fire barrier maintained, you have to refer to the structural requirements in part B3 to ascertain what is and is not a required fire barrier
7.6 (and following sections) covers pipes passing through fire barriers which applies to us for extractor ducting.

4.1 covers the purpose of minimum fire resistance standards
4.2 covers the minimum fire resistance to be provided for structural elements.
4.4 excludes structures only supporting roofs (subject to exceptions) from the structural requirements
 
There is a lot of misconception and I'm still not sure about whether or not they HAVE to be fitted in the ceiling if there is a roof space above. However, I will always fit fire rated ones when there is a loft above as this is recommended by 'Electrical safety first' in Best Practise Guide Number 5 - page 8 section 7.7 - (see link given by TJ in post 8). Their reasons are that this will:

1. Safeguard escape from the premises
2. Restrict the spread of fire.
3. Reduce the risk of premature failure of the roof structure

Also, The Electrical Safety Council recommends fire rated downlights fitted in 'all' ceilings' View attachment 28008

My reply was specifically in response to the OP. If ever I fit downlights and they're not LEDs then they will be mains voltage fire rated. If however a customer didn't have the budget for LEDs and wanted cheap downlights fitted below a flat roof, I'd have no qualms fitting non fire rated lights.

My point was mainly to illustrate that you only have to fit fire rated cans in specific situations. Hence why non fire rated ones would be perfect for a tight void above.
 
I have read through the posts...and wonder if the op and others actually understand what is ment by fire rated fittings. It has nothing to do with the heat produce by the fitting (but is an issue) it is the fire retainment between floors of a building.
 
I have read through the posts...and wonder if the op and others actually understand what is ment by fire rated fittings. It has nothing to do with the heat produce by the fitting (but is an issue) it is the fire retainment between floors of a building.

I'd be willing to bet that 99% of domestic sparks don't actually know what the fire rating of a can is actually there for.

Just yesterday I was at the counter at my wholesaler and the fella to my right was ordering downlights, when the sales guy asked if he needed them to be fire rated his reply was along the lines of "err, yes, yes they do need fire rating coz they're gonna be surrounded by insulation innit"?!?!?!?

Even I couldn't let that one slide and swiftly educated him, turns out he wasn't a spark but the builder buying for the spark (so he said!), but I'd have thought as a builder he should know this like the back of his hand! Fire barrier preservation is their realm! Pft!
 
I'd be willing to bet that 99% of domestic sparks don't actually know what the fire rating of a can is actually there for.

Just yesterday I was at the counter at my wholesaler and the fella to my right was ordering downlights, when the sales guy asked if he needed them to be fire rated his reply was along the lines of "err, yes, yes they do need fire rating coz they're gonna be surrounded by insulation innit"?!?!?!?

Even I couldn't let that one slide and swiftly educated him, turns out he wasn't a spark but the builder buying for the spark (so he said!), but I'd have thought as a builder he should know this like the back of his hand! Fire barrier preservation is their realm! Pft!

I'd like to think that its a far lower figure than that, perhaps 50%, but really it should be common knowledge among domestic sparks as if they believe fire rated means it stops the fitting from catching fire thats pretty scary.

Also, even among the sparks who do realise that a fire rated downlight limits the spread of fire, i wonder how many realise what that little strip around the inside rim of the downlight is for.. i.e the intumescent strip (which breaks and falls off easily)!!
 
It's probably around the same number of electricians who don't one that there are building regulations other than part P which they have to be aware of!
 
It's probably around the same number of electricians who don't one that there are building regulations other than part P which they have to be aware of!

Huh?! Other building regs?!

I thought you got Part P qualified and that's it?! No one told me nuffin' about no other ones guv?!
 
I shouldn't worry too much, they're only silly trivial things like structural integrity, fire safety, toxic substances, ventilation. You'll never make your £50K/year if you go worrying about that sort of nonsense.
 

Reply to fire rated or not down lightd in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
979
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi all, I have been asked to install new electrics to a wooden lodge / chalet. It is a single storey very large building with a flat roof. I have...
Replies
10
Views
3K
Am hoping you can help Following an integral garage conversion, I am after a couple of fire hoods to cover some LED ceiling spotlights. The...
Replies
21
Views
2K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock