It depends on the rating of the cable whether the items needs/ is suitable for 16a supply as you will be removing the protection provided by the fuse and relying on mcb o4 rcbo controlling the circuit for overload protection.
 
Bear in mind that 16A sockets are sometimes protected by 20A OCPD, possibly C20. So the cable needs to be sufficient to withstand clearing a fault on a C20.

Items with 0.75mm² flex would be adequately protected on a B16, and in continental Europe they would be connected with unfused plugs to socket outlets on 16A radials. I don't think it is adequate for a C20.

There are other cases which are definitely no-go on a B16 either, e.g. an appliance with a 0.5mm² flex that would be fused down to 3A in a 13A plug, and unfused multi-socket extensions with 1.25mm² flex where the total rated current must not exceed 13A but the plug fuse is relied upon to limit this.
 

Reply to Fitting a 16amp plug to a 13 amp in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
838
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
878
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
445
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
987
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock