Seems to be a lot of confusion, that FP cable is the be all, and end all of fire resistant cable. And is only suitable for fire alarms. So let me put some points across.
FP is often used for fire alarms, emergency lighting, PA systems, Disabled refuge, control switching, sprinkler control, UPS or in any installation upto 300v, where a designer may have reason to install.
FP comes in singes FP100, 2, 3, 4 or multi core FP200.....Has two versions Standard & Enhanced.
Although FP is quick and easy to install, it has limitations, and these limitations are crucial in any design.
Due to its making, FP200 has no internal seal. A can easily pass gas and water, by compilary down its internal structure.
So chemical plants, server rooms or areas of integrity, need to be thought out.
Pyro/Micc after being around for decades, is still the ideal way to over come design problems, such a integrity...and unlike FP, it is actual classed and enhanced cable. The fire time restraints to failure are also different between FP & pyro...FP has a fire rating of 20-30 minutes, where Pyro has outlasted some intense fires.
So as with any cable, it has its places and its usage, but only with taught and design.
This video you may find interesting, Worth watching the testing procedures.
https://www.youtube.com/watch?v=N3ZAYFSwInk
FP is often used for fire alarms, emergency lighting, PA systems, Disabled refuge, control switching, sprinkler control, UPS or in any installation upto 300v, where a designer may have reason to install.
FP comes in singes FP100, 2, 3, 4 or multi core FP200.....Has two versions Standard & Enhanced.
Although FP is quick and easy to install, it has limitations, and these limitations are crucial in any design.
Due to its making, FP200 has no internal seal. A can easily pass gas and water, by compilary down its internal structure.
So chemical plants, server rooms or areas of integrity, need to be thought out.
Pyro/Micc after being around for decades, is still the ideal way to over come design problems, such a integrity...and unlike FP, it is actual classed and enhanced cable. The fire time restraints to failure are also different between FP & pyro...FP has a fire rating of 20-30 minutes, where Pyro has outlasted some intense fires.
So as with any cable, it has its places and its usage, but only with taught and design.