I seem not to have access to the professional forums so I post this here:

I understand ohm's law and to get a current you use Volts/Resistance (V/R); so if it's Perspective Fault Current (PFC), it's V/R or Volts/Ze; and we divided by 1000 to convert to kA. Yes?

Is there a difference when calculating PFC on either earthing systems? For a TN-S, TN-C-S, TT or IT, is the same formula used?

Thanks.
 
PFC calc is the same as far as I'm aware, earthing arrangements won't make a difference as in 99% of the time PSCC will be higher than PEFC.
 
Yes, it would be the same, but more specifically L-E is the Prospective Earth Fault Current (PEFC). L-N is the Prospective Short Circuit Current (PSSC). The higher reading of the two you then record as the Prospective Fault Current (PFC).
 

Reply to Full Calculation of Perspective Fault Current - PFC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
I'm installing a new supply to a ceremoniously dumped welfare cabin. I can't see any legitimate reason not to apply section 717, welfare units are...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock