I got a Ra of 4 ohms the other day tho I used the structural steel as the electrode.
All bolted together about 10 lengths of steel into the foundations.
 
I know the kqi Schneider rcbo instructions tell you not to bundle the neutrals together but can cut to length.
They recommend if the functional earth is cut then a bootlace is fitted due to crushing of the fine strands when tightend in the terminals
Temporary supply mate, might be in a month max. Probably try blag the company to give him the cable and gear back since they won't use it :D did on the last tempory supply we did haha
 
Boss does the testing, I took a Zs at the board after I finished. That's what I was referencing

Does your boss not include you in the testing process? Did you see him set up temporary electrodes and test the earth rod at any point in time?

Your Zs measurement almost certainly did not include the earth rod. You will have been testing via the cpc straight back to the star point via the N-E link at the generator

With a generator fed installation the earth electrode is the earth reference of your TNS system. In comparison to a normal installation the generator is equivalent to the substation transformer.
 

Reply to Full rcbo boards???? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just wondering if any of you know which RCBOs might fit this old GET board? Cheers in advance!
Replies
4
Views
893
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
763
Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
941
Hi all, just a quick one to ask about an issue I'm having with my EV charger. I'll give a little background first but ultimately I want to know if...
Replies
11
Views
2K
Evening all. I did an EICR recently and then changed a consumer unit. As part of the EICR process I take off around 25% of all accessories to...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock