Discuss Garage Consumer Units in the UK Electrical Forum area at ElectriciansForums.net

Are you going to incorporate surge protection into it?
Prob not. It's my own garage. Washing machine, dryer etc, lights etc. But yea know were you coming from prob fact I don't fit one will regret it later Murphy's Law. Actually was looking to see if maybe room in the main consumer. Unit for Type 2 but there is not. If I was getting on I would prefer to protect whole house. Maybe see if it can be done as stand alone enclosure at main consumer unit.. Cheers Jonny
 
You will need RCD protection somewhere is virtually every case. If it is fed via SWA cable so no need for protection on the distribution cable then it makes sense to have just a MCB at the house CU and then RCD and any other MCBs at the garage.

However, if you can't be sure of the sub-main installation then having RCD/RCBO at house and then just MCB at the garage is a better choice.

Two 30mA RCD in series without selectivity is poor design, not enough to worry about on an EICR beyond C3, but not something you should aim to do unless you have a very good reason.

Having said that, having MCB in series or RCBO+MCB will have negligible fault selectivity, even if they are OK on overload due to a 1.6:1 or greater difference in rated current. Again, not good design, but usually an acceptable trade-off if the final circuits in the garage are not critical as done in practically every case.
 
You will need RCD protection somewhere is virtually every case. If it is fed via SWA cable so no need for protection on the distribution cable then it makes sense to have just a MCB at the house CU and then RCD and any other MCBs at the garage.

However, if you can't be sure of the sub-main installation then having RCD/RCBO at house and then just MCB at the garage is a better choice.

Two 30mA RCD in series without selectivity is poor design, not enough to worry about on an EICR beyond C3, but not something you should aim to do unless you have a very good reason.

Having said that, having MCB in series or RCBO+MCB will have negligible fault selectivity, even if they are OK on overload due to a 1.6:1 or greater difference in rated current. Again, not good design, but usually an acceptable trade-off if the final circuits in the garage are not critical as done in practically every case.
Thanks great advice and that's my plan. So MCBs in parallel not a good idea either?? That warrant a C3? Don't want to design code breaking into the circuit. Cheers Jonny
 
You have an HNC in electrical engineering so the design of this should be straight forward.
I was used wiring and designing high end avionic equipment and power supply in trainee fighter aircraft a past life so slightly different area of expertise. I do have an NVQ3. I come on here to get advice as I know I don't know everything. Before anyone says leave it to professionals - And I am updating my skill base having completed C&G 18th Edition and CG Initial Verification and Periodic Testing. I do concede I get stuck and use this forum to bounce ideas with the helpful people on here of which there are plenty. Thanks Jonny.
 
You will need RCD protection somewhere is virtually every case. If it is fed via SWA cable so no need for protection on the distribution cable then it makes sense to have just a MCB at the house CU and then RCD and any other MCBs at the garage.

However, if you can't be sure of the sub-main installation then having RCD/RCBO at house and then just MCB at the garage is a better choice.

Two 30mA RCD in series without selectivity is poor design, not enough to worry about on an EICR beyond C3, but not something you should aim to do unless you have a very good reason.

Having said that, having MCB in series or RCBO+MCB will have negligible fault selectivity, even if they are OK on overload due to a 1.6:1 or greater difference in rated current. Again, not good design, but usually an acceptable trade-off if the final circuits in the garage are not critical as done in practically every case.
And thankyou that was great advice. J
 

Reply to Garage Consumer Units in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
865
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
407
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock