Discuss Ground Fault Detection Interrupter (GFDI) in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

I

Ibis Designs

Some inverters are provided with GFDI and some are not. Is this a regulatory thing dependent upon the country of use intended for the product?
 
transformerless inverters need it, galvanically isolated inverters don't because they're protected by virtue of the DC being galvanically isolated from earth.
 
Hi Gavin

Do you have an example of such an inverter? I always thought that a GFDI must have a permanently grounded pole (Pos or neg) on the DC, where is Riso monitoring (like in SMA centrals) use a Bender relay, using PE as a reference point.

Thanks

Meeb
 
galv isoltated inverters would be stuff like the old SMA sunnyboy SB series, but also NEDAP's power Router hybrid battery inverter is galv isolated.
 

Reply to Ground Fault Detection Interrupter (GFDI) in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
663
Hi All, I understand the requirement for PEN fault detection on EV chargers for TN-C-S installs (or to place an earth rod). However, when I was...
Replies
3
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
936
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
280

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock