U need to link the neutrals together from the two twin and earth cables.
And take the feed and put it into L1, along with the black of the 3 core. And take the brown that goes to the light fitting and put it into L2 along with the grey of the 3 core. As long as at both your switches the common is brown from 3 core this should work for you.
Yes this is my guess.
 
In your first picture you only need the brown of the three core, ignoring earths in the common. The other two go in L1 and L2, one in each it doesn't matter which way round this is assuming you have a live in and then out to the light.
 
One more bit of info needed.
Go to the other switch (the one switch of the two way lighting circuit) and remove it, DO NOT REMOVE ANY WIRES GOING TO IT.
Now, make a note of what colour wires are connected to the terminals. I would expect to see BROWN on com, BLACK sleeved in Brown on L1 & GREY sleeved in Brown on L2
 
Being picky, it does look a bit untidy. Hope that neutral sticking out of the connector, doesn't touch the metal back box at some stage.

Think the grommet is in place, a metal one?
 
I will tidy it up once I got it all in the right places. It's like this as it's still trial and error.

I think I have is sorted now thanks all much appreciated!!
 
On the new switch snip off all the old ends and redo them so they don't break when you refit it.
 
I am a DIYer, fitted a few switches and sockets in the past. It's part of an extension to my house that runs on its own fuse box so all electric to this part of the house if off and tested with a tester pen. That's how I know which wire has power and that the others dont

Gonna sound r-see,but,no, you don't...:(
 

Reply to Help please! 2 Way light switch in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
472
Hi, Iā€™m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
372
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
1K
Hi, I have a single light switch, wired like this.. the 2 wires in com, with a always live wire coming to the switch, and then wire going out to...
Replies
6
Views
697
Hey everyone complete idiot herešŸ˜‚ can anyone please help me with what goes where if possible by these pics? There is one black and one grey wire...
Replies
1
Views
537

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock