Search for tools and product advice,

Discuss How many fire alarms do i need to install on a 3 bedroom house (2 floors) in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

C

charlalberts

Hi, Could someone give me advice on how many fire alarms need to be installed on a 3 bedroomed, 2 floor house? I know with loft conversions every room besides the bathrooms need alarms, but what is the requirements for a standard double storey house?

Do they also need to be mains powered, or can they be 9v battery operated?
House it to be rewired.
Thanks for looking, and thanks in advance for your comments.
 
Dont get me wrong there is nothing wrong with the 9v fire alarms! they save lives
Only problem is they dont interlink!

The fire brigade provide free of charge fire alarms to residential houses so if this is your house worth giving them a ring - they are 3v battery powered but guaranteed for 10 years.

Think of it this way - if the heat alarm goes off in the kitchen (door closed) are you going to hear it? - NO!
If it is interlinked to the upstairs alarm will you hear it - YES!

Weigh up the risks - how much is your/your families/the customer's family's life worth? - Dont cut corners when it comes to safety
 
Doesn't it all depend on the size of the property as to what system/ how many alarms need to go in? I remember wiring simple interlinked smokes in a property but then the building inspector came out to sign off the 1st fix and he said it had to be a proper system with panel because of the size of the house. I was working for a company and only just out of my time at this point so i had no clue about this requirement when i was wiring. Haven't got the regs to hand so i cant remember what the categories are.
 
Doesn't it all depend on the size of the property as to what system/ how many alarms need to go in? I remember wiring simple interlinked smokes in a property but then the building inspector came out to sign off the 1st fix and he said it had to be a proper system with panel because of the size of the house. I was working for a company and only just out of my time at this point so i had no clue about this requirement when i was wiring. Haven't got the regs to hand so i cant remember what the categories are.

How big of a property did you install this in?

Most domestic properties have a standard interlink system

Just remember with fire alarms, as long as every room that has a risk item of equipment (e.g. cooker, dryer, open fire, etc) has a smoke in it then your fine. You can go OTT with these systems but its all down to what the customer wants.

Some customers dont want panels so a standard interlink system is fine, an advantage is the locate unit, so if you have a large building - press the locate button and all alarms stop apart from the one which was activated! - they also have a reset button and a silent button as well.

again thats Aico.


Go onto Aico and request the free contractors booklet - all you need to know is in there
 
Top and bottom of the stairs to protect escape route. Avoid putting smoke alarm to close to the kitchen as it will keep going off, same with bathrooms. Smoke alarms are designed to provide early warning in case of fire so you can get out of the house not go and fight the fire, so keep this in kind when positioning them.
 
How big of a property did you install this in?

Most domestic properties have a standard interlink system

Just remember with fire alarms, as long as every room that has a risk item of equipment (e.g. cooker, dryer, open fire, etc) has a smoke in it then your fine. You can go OTT with these systems but its all down to what the customer wants.

It was a biggie, 25m Wide, 11m deep, 3 storey, 5 Bed mansion worth about 2mil. I was just really doing what my supervisor at the time told me to do because like i said i was only just out of my time. It had all the Legrand Arteor home automation in, was a joy to work on.
 
Smoke throughout on every landing and hall

Heat in the kitchen NOT ABOVE the hob as I seen before

Heat in the utility room (if they have one) for the dryer

Interlink the CO2 alarm in with the lot as well - always dread CO2 leak and you cant hear the bloody alarm because you closed the door.

The idea behind this is that your not going to mess around when the alarm goes off in the middle of the night - your going to get dressed and get out either way!

If its a bigger house I have installed a sounder upstairs for the CO2 alarm before instead of interlinking them.


I got a 4 story house to do next week - new build and debating what to put in: panel or interlink. I want the panel but landlord/owner wants the interlink, even though I can build this in the wall with a system he is alerted by text if the alarm goes off.
 
no gas and open fire doesnt get used.. its a small bungalow being converted with 3 bedrooms up. all bedroom doors are next to each other , so one smoke there in small landing, one smoke at bottom of stairs where all doors are within 3-4 meters of eachther and a heat in the kitchen.

ionisation or optical??? goig by that website i should go for optical. is a good few pages(adico)
 
no gas and open fire doesnt get used.. its a small bungalow being converted with 3 bedrooms up. all bedroom doors are next to each other , so one smoke there in small landing, one smoke at bottom of stairs where all doors are within 3-4 meters of eachther and a heat in the kitchen.

ionisation or optical??? goig by that website i should go for optical. is a good few pages(adico)


Sounds good

Its really up to you what you put in

I would use the multi or optical - the ionistion is only really good for smoldering clothes and realistically you wont have much of that.

Check this out
What works where?Aico - Fire & CO Detection & Fire Protection Specialist

This is a good guide
 
yeah was reading it, good guide for a punk like me wanting t wire the world but my heads sore trying. good guide consider it saved in favourites ty
 
Dont forget you have to do a risk assessment to determine what is the best and what locations.

Dont forget the following:
Smokers
Open fires
Utility rooms
Electric heaters (inc Eco 7)
Electric/gas cooker
use of candles


use your common sense with them - work out which are in use more than 10% of the time and count them in, the others put a low likely hood on them.

As your N/Ireland I would be happy to pop across and help with the RA as I used to teach councils and H&S officers/inspectors how to carry them out - pm me if your interested
 
If in doubt check with building control as they will be signing it off. I'd avoid putting too many in as this leads to them going off for no reason and the owners then try and disconnect them.
 
Interlink the CO2 alarm in with the lot as well - always dread CO2 leak and you cant hear the bloody alarm because you closed the door.

If its a bigger house I have installed a sounder upstairs for the CO2 alarm before instead of interlinking them.

Why would you fit Carbon Dioxide (CO2) alarms ?
 
Well, this thread is a bit of an eye opener to say the least.

Jst goes to show the lack of knowledge/confusion that exists regarding fire protection & alarms etc.

Although Approved Document B currently states that a Grade D LD3 should be installed, it also states that BS 5839-6 should be followed and this standard recommends a Grade D LD2 system.

First off they are CO (Carbon Monoxide) not CO2 (Carbon Dioxide) alarms and they SHOULD NOT be interlinked with standard smoke/heat alarms as the sound they emit when detecting CO is different to smoke/heat and YOU MUST be able to differentiate between the two i.e smoke from a fire and CO.

A new build or materially altered building would normally require a minimum of a Grade D LD2 (BS 5839-6) system which covers all circulation spaces that form part of an escape route and rooms or area's with a high fire risk. These area's cover hallways & landings, the principal habitable room and will require a smoke alarm.

Kitchens will require a heat alarm.

A fire risk assessment will determine the exact level of cover reequired but as stated BC will tell you what you need which nowadays in my experience is a Grade D LD2.
 
Lenny should be on Myth busters
Given the myths that are around

Assessing the risk and responding by siting alarms where needed,Bs5839-6 is a document that perhaps all who work in domestic should hold
 
Totally agree Des.

Relevant guidance documents should be held and referenced by EVERYONE involved with installing these or any kind of unfamiliar system.

More so with fire/smoke alrms IMO as you are trying to save someones life!!!


The guesswork evident worries me to say the least but, at least, you can always use a bloody phone app if you're not sure!!!!!!!!!!!!!!!!!
 
sorry topcat relating to this post....... dl2
Well, this thread is a bit of an eye opener to say the least.

Jst goes to show the lack of knowledge/confusion that exists regarding fire protection & alarms etc.

Although Approved Document B currently states that a Grade D LD3 should be installed, it also states that BS 5839-6 should be followed and this standard recommends a Grade D LD2 system.

First off they are CO (Carbon Monoxide) not CO2 (Carbon Dioxide) alarms and they SHOULD NOT be interlinked with standard smoke/heat alarms as the sound they emit when detecting CO is different to smoke/heat and YOU MUST be able to differentiate between the two i.e smoke from a fire and CO.

A new build or materially altered building would normally require a minimum of a Grade D LD2 (BS 5839-6) system which covers all circulation spaces that form part of an escape route and rooms or area's with a high fire risk. These area's cover hallways & landings, the principal habitable room and will require a smoke alarm.

Kitchens will require a heat alarm.

A fire risk assessment will determine the exact level of cover reequired but as stated BC will tell you what you need which nowadays in my experience is a Grade D LD2.
 
When someone uses the word "Fire Alarm" I tend to think of the typical zoned, pyro / FP200 cabled installation you would find in a industrial or commercial building. I have installed Fire Alarms in domestic properties but normally HMO.

I find calling them smoke/heat detectors when describing domestic installs much softer on the pallett :smart:
 
When someone uses the word "Fire Alarm" I tend to think of the typical zoned, pyro / FP200 cabled installation you would find in a industrial or commercial building. I have installed Fire Alarms in domestic properties but normally HMO.

I find calling them smoke/heat detectors when describing domestic installs much softer on the pallett :smart:

And much easier to install!
 
Aico pocket guide has everything that's needed in it, from new build to existing properties, of different sizes too.

Its even on a slide chart at the back. Fit as this then your system will comply with whichever standard it states. Also a page regards using the risk assessment to determine if more or less alarms are required.
 

Reply to How many fire alarms do i need to install on a 3 bedroom house (2 floors) in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi, I'm completely rewiring a 9 bed 3 storey HMO in Jan, The fire detection required is just some linked lithium detectors in the...
Replies
7
Views
755
This isn't really an electrical issue as such but I know you guys are pretty tech savvy and familiar with all the latest and greatest...
Replies
13
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
776
Hi All, I am looking to install a Quinetic double gang in line receiver switch (QURS2W) in my hallway on the ground floor to control the lights...
Replies
4
Views
1K
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
512

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock