Discuss how to upgrade the earthing conductor? in the Electricians' Talk area at ElectriciansForums.net

The information is not a secret,but the understanding of the system should be fundamental to any electricianL
limitations are what safety is about, Diyers should limit their work to the level of their understanding
Once they exceed that understanding,any work they carry out could be dangerous
Informing the ignorant of ways to end their existance may not be a sensible action
 
Going back to a point raised earlier gents.
Are we saying it's acceptable to leave the current earthing as is it and reterminate in a MET and link into the CU with 16mm.
Or
Apply the adiabatic equation and work out if it is acceptable according to this.
I'm with brucelee on this one. Yes the OSG is a guide, hoeever there must be reason behind stating these figures in the first place backed by knowledge and reasoning from the regs.
 
That will be a tn-s system and is the suppliers earth to met, so providing you have a ze lower than 0.8 ohms and the consumers earth from the met to the consumer unit is of an adequate size its of no concern to your pir. If on the other hand the small wire is coming straight off the sheath into the consumer unit i usually reterminate into an external met and take a 16mm into the cu it will then satisfy the cert as the consumers main earthing conductor is of the right size. you should neva mess with there incoming cable, if you take a ze reading and it doesnt satisfy you contact the supplier to upgrade hope this may help.

If I was doing a PIR and there was a 6.0mm earth from the cutout to the MET and then a 16mm to the CU,the earth size on the cert would be 6mm, not 16mm.....the 6.0mm will have to carry the same fault current as the 16mm.
 
As I've already stated, sizing of protective conductors is by either SELECTION or CALCULATION!!
If it's a new installation then selection can be applied at the design stage. This chap has attended an already existing installation and is thinking about upgrading the earth when it most likely is not necessary.

If you don't know how to do the adiabatic then say so!!!


Sent from my iPhone using Tapatalk
 
just to come in on this at a late stage on what has obviously been an interesting discussion. It should be remembered that unnecessarily upgrading earths could potentially cause problems in itself as this could lead to higher PEFCs that might exceed the breaking capacity of the protective devices so they can not clear the fault safely. It really should be checked properly and not just immediately assumed that bigger must automatically be better.
 
just to come in on this at a late stage on what has obviously been an interesting discussion. It should be remembered that unnecessarily upgrading earths could potentially cause problems in itself as this could lead to higher PEFCs that might exceed the breaking capacity of the protective devices so they can not clear the fault safely. It really should be checked properly and not just immediately assumed that bigger must automatically be better.
i may be inaccurate here, but theoretically the protective device, usually a 1361, will blow long before the fault current gets anywhere near it's rated breaking capacity of 16kA. it's a very rare occurence for a fault current to develop upstream of the circuit protective devices, although not unknown.
 
Last edited:
As I've already stated, sizing of protective conductors is by either SELECTION or CALCULATION!!
If it's a new installation then selection can be applied at the design stage. This chap has attended an already existing installation and is thinking about upgrading the earth when it most likely is not necessary.

If you don't know how to do the adiabatic then say so!!!


Sent from my iPhone using Tapatalk

Fair comment.
But selfishly let me take another view.
A few months ago I started a thread similar to this where I went to a customers house.
British gas where to install a new central heating system but refused to do it cause the main earthing conductor was 4mm straight into the MET on a TNS system.
I'm still in the process of awaiting DNO to come out so it can be changed over.
Now although the Ze was fine and PFC I questioned the inadequacy of the size that would it take the fault current. Would this mean I shouldn't be changing this too and telling British Gas to stop being so silly?
 
Fair comment.
But selfishly let me take another view.
A few months ago I started a thread similar to this where I went to a customers house.
British gas where to install a new central heating system but refused to do it cause the main earthing conductor was 4mm straight into the MET on a TNS system.
I'm still in the process of awaiting DNO to come out so it can be changed over.
Now although the Ze was fine and PFC I questioned the inadequacy of the size that would it take the fault current. Would this mean I shouldn't be changing this too and telling British Gas to stop being so silly?

It would depend completely on the calculation. I can't say yes or no without knowing more.


Sent from my iPhone using Tapatalk
 

Reply to how to upgrade the earthing conductor? in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
927
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
522
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K
I've come to a decision, I just cant do work anymore that involves mad stuff, for example today - 2 bed flat that's had fire damage, someone has...
Replies
4
Views
867
Just a bit of a muse at the moment, work won't happen for a while, though I do already have the ducting. We have (what's left of - it was rotten...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock